Question: I have a service disconnect located on the house exterior. At that point there are 2 driven ground rods from the disconnect.At the opposite end of the house ( 160’ there is a 1” Cu underground water line coming into the basement.With that Cu water line being present does it need to be connected to the GE system?Thanks
Yes, the copper water line needs to be connected to the grounding electrode system (GES). Here's why: NEC (National Electrical Code) Requirement
The NEC (specifically, section 250.52(A)(1)) generally requires a metal underground water pipe to be used as a grounding electrode if it's in direct contact with the earth for 10 feet or more, and is electrically continuous. In your case, with a 1" copper water line buried underground for a distance of 160 feet, it easily meets this requirement.
Supplementary Grounding Electrode
If the grounding electrode conductor (GEC) to the water pipe isn't continuous or the connection to the water pipe is questionable, it is still required to supplement it with another grounding electrode, such as your ground rods.
Bonding to the GES
Since you have the ground rods established at the service disconnect, you'll need to run a grounding electrode conductor (GEC) from the service disconnect to the copper water pipe. This ties the water pipe into the overall grounding electrode system.
Purpose of Grounding
The purpose of grounding is to provide a low-impedance path for fault current to return to the source (the transformer). This helps to quickly trip a breaker or blow a fuse during a fault, minimizing the risk of electric shock and fire.
Size of GEC
The size of the GEC to the water pipe is determined by the size of your service entrance conductors as described in the 2020 NEC Table 250.66.
Bonding Jumper Around the Water Meter
When connecting to a metallic water piping system, the NEC also requires a bonding jumper to be installed around any insulated joints or equipment that may interrupt the electrical continuity of the system. Typically, this would be the water meter. This bonding jumper should be sized per NEC Table 250.102(C)(1), based on the size of the GEC to the water pipe.
Corrosion Concerns
The connection to the water pipe must be made within 5 feet from its point of entrance to the building per NEC.
Aluminum Considerations
Aluminum and copper are dissimilar metals that can cause corrosion when they come into direct contact with one another. Therefore, it is essential to use the proper listed connector when bonding the GEC to the copper water line.
How to Connect
Determine the GEC Size
Consult NEC Table 250.66 based on the size of your service entrance conductors to determine the correct size of the grounding electrode conductor (GEC).
2.
GEC Installation
Run the GEC from the service disconnect to the copper water pipe. The GEC can be copper or aluminum. It must be protected if it's subject to physical damage.3.
Approved Connector
Use a listed connector that is suitable for direct burial and for connecting the GEC material (copper or aluminum) to the copper water pipe. The connector should be corrosion-resistant.4.
Bonding Jumper
Install a bonding jumper around the water meter, as close to the water meter as practical. Size this jumper according to NEC Table 250.102(C)(1).
5.
Point of Connection
Connect to the water pipe within 5 feet of where the water pipe enters the building.
Important Considerations
Local Codes
Always check with your local electrical inspector or building department for any specific requirements or interpretations of the NEC that may apply in your area.
Qualified Electrician
This type of work is best performed by a qualified and licensed electrician to ensure compliance with all applicable codes and safety regulations. Incorrect grounding can create a dangerous situation.