Topic: 3 phase Screw Compressor on an Add-A-Phase.

User: 11bgrunt, Location: TEXAS

Asked on: Saturday, January 11, 2025 at 8:47 pm EST
Answered on: Thursday, March 6, 2025 at 7:11 am EST

Question: Customer has a shop on the same single phase, 50kVA POCO transformer as his house.The shop does tire repair with an autoclave. This requires a large cu. ft. of compressed air to 85psi.An Ingersoll Rand SSR-EP25SE 25HP Rotary Screw Air Compressor served by an Add-A-Phase, provides part of the air requirement.The POCO three phase line extension was quoted $40K+. A rotary phase converter would also be expensive.The LRA on the screw is 540A @ 3P, 240V.I believe this starting current is the root of all his power quality complaints over the last five years.I thought the automatic unloader might be an issue and asked him to start @ 0psi. He reported this was not going to work for his operation.There are a lot of different things that could be done, but all are expensive.Can a soft start be used on this compressor, that is served by the Add-A-Phase? If the Add-A-Phase was not functioning correctly, what would the symptoms be?The POCO is willing to increase the transformer to a 75kVA.

You've hit on the likely culprit of your customer's power quality problems: the massive inrush current of the 25HP rotary screw compressor during startup, especially when operating on a single-phase to three-phase converter (Add-A-Phase). Let's break down the situation and address your questions.

Understanding the Problem High Inrush Current

The LRA (Locked Rotor Amps) of 540A at 240V on a 3-phase motor is
huge. This initial surge is what's likely causing voltage dips and other power quality issues. The Add-A-Phase converter has to work very hard to supply this initial surge, and the utility transformer and wiring are likely undersized for that sudden load.

Single-Phase Limitation

A 50kVA single-phase transformer is already being heavily burdened by the house and shop combined. The compressor's intermittent, high-demand nature makes it even worse. The Add-A-Phase further complicates things as it has limitations in providing balanced 3-phase power, especially during transient events like motor starting.

Automatic Unloader Issue

Your suspicion about the unloader is valid. If the compressor is starting against pressure, the motor has to work even harder, increasing the inrush current.


Power Quality Complaints

These are a direct result of the voltage dips caused by the compressor starting. Sensitive electronic equipment can malfunction or be damaged by these dips.

Can a Soft Start be Used on a Compressor Served by an Add-A-Phase?


Yes, a soft starter can be used with a rotary phase converter (like the Add-A-Phase), and it's likely the best solution without a full 3-phase upgrade. However, there are some considerations: Compatibility

The soft starter must be compatible with rotary phase converters. Some soft starters are designed to work better with them than others. Look for models specifically recommended for use with phase converters.


Sizing

The soft starter must be correctly sized for the motor's horsepower and voltage, and the Add-A-Phase must have sufficient capacity to handle the reduced starting current.

Add-A-Phase Capacity

Ensure the Add-A-Phase unit is robust enough to handle the reduced, but still significant, starting current of the soft-started motor. Review the Add-A-Phase specifications and consult with the manufacturer.


Bypass Contactor

Most soft starters include a bypass contactor that engages after the motor reaches a certain speed. This allows the motor to run directly on the line voltage, improving efficiency. Verify that the bypass contactor is rated for the full running current of the motor.

Installation

Have a qualified electrician install the soft starter. Proper wiring and configuration are critical.

Why a Soft Starter is Beneficial



Reduced Inrush Current

Soft starters gradually increase the voltage applied to the motor during startup, significantly reducing the inrush current. This will lessen the strain on the Add-A-Phase and the POCO transformer.

Smoother Starts

Reduced mechanical stress on the compressor components due to gentler acceleration.


Improved Power Quality

Less voltage dip during startup, improving the performance and lifespan of other electrical equipment.

Symptoms of a Malfunctioning Add-A-Phase



Voltage Imbalance

Uneven voltage on the three phases. Use a voltmeter to check the voltage between each pair of phases. Significant differences (more than a few volts) could indicate a problem.


Overheating

The Add-A-Phase unit gets excessively hot during operation.

Humming or Buzzing

Unusual or loud noises coming from the unit.


Motor Stalling

The compressor motor fails to start or stalls during operation, especially under load.

Flickering Lights

A more pronounced flicker when the compressor starts, even more so than usual.


Low Generated Phase Voltage

The generated phase may have a noticeably lower voltage compared to the other two.

Failure to Start

The Add-A-Phase may simply fail to power the compressor.

Possible Solutions and Considerations
1. Soft Starter (Highly Recommended)

This is the most cost-effective solution to investigate first. Research compatible models and get a quote from a qualified electrician. Consider the sizing requirements carefully.2.

Increase Transformer Size (POCO Offer)

While upgrading to a 75kVA transformer from the POCO will provide some improvement, it might not completely solve the problem
without also using a soft starter. The inrush current will still be present, just less impactful on the larger transformer. Get a detailed explanation from the POCO on how much improvement they expect and if it's guaranteed.3.

True Three-Phase Service

The $40K+ cost is substantial, but it's the ultimate solution for eliminating power quality issues and providing a stable power supply. Explore financing options or government incentives.4.

Rotary Phase Converter (RPC)

A properly sized RPC will typically provide better performance than a static phase converter like the Add-A-Phase, but may not be much cheaper than installing a soft starter. You will need to weigh the cost and consider future needs.5.

Load Management

If possible, try to minimize other electrical loads when the compressor is starting. Turn off lights, HVAC, and other non-essential equipment.6.

Accumulator Tank

Increase the size of the accumulator tank. This will allow for less frequent compressor starts.7.

Check Compressor Operation



Unloader Valve

Verify the unloader valve is functioning correctly. It should be relieving pressure when the compressor stops, allowing for easier restarts. A faulty unloader valve can cause the motor to work harder during startup.*

Air Leaks

Check the entire compressed air system for leaks. Leaks cause the compressor to run more frequently, increasing the load on the electrical system.8.

Monitoring

Consider installing a power quality monitor to track voltage, current, and other parameters. This will help you identify the root cause of the problems and verify the effectiveness of any solutions.

Recommendation


Start with a thorough investigation of the Add-A-Phase unit. Check the voltage balance and look for any signs of damage or overheating.Get quotes for a suitable soft starter, including installation. Discuss the options with the electrician, emphasizing the Add-A-Phase converter's limitations.If the soft starter doesn't completely resolve the issue, then consider the POCO transformer upgrade.Weigh the long-term costs and benefits of the true three-phase service against the other solutions. While expensive upfront, it might be the most cost-effective option in the long run.

Crucially, document everything and get guarantees from vendors where possible. Good luck! Flag for review