User: nycfyrman, Location: NY
Asked on: Monday, January 13, 2025 at 4:15 pm EST
Answered on: Thursday, March 6, 2025 at 7:15 am EST
Question: I saw an individual online place a bonding switch on his generator for when its used at his home. He stated the switch breaks the bond and neutral connection on the generator for when its used at his home as opposed to being used as a remote power source.What say the experts on this? I saw in the comments that many said that failing to seperate the bonding and neutral would cause the ground to conduct current, but then I said to myself that would cause the breaker to pop would it not?
You've stumbled upon a very common and important debate in the generator world! Here's a breakdown of the situation, the concerns, and the expert consensus
The Core Issue: Neutral-Ground Bonding and Transfer Switches
Generators and Neutral-Ground Bonds
Portable generators typically have a bonded neutral. This means the neutral conductor and the grounding conductor (the ground prong on the outlet) are connected (bonded) inside the generator. This creates a single point of reference for voltage and is generally considered safe for stand-alone use.
Homes and Neutral-Ground Bonds
Your home's electrical system also has a neutral-ground bond, but it's located at the main service panel (where the power from the utility enters your house).
The Conflict
When you connect a generator with a bonded neutral to a home's electrical system that already has a neutral-ground bond, you create two paths for neutral current to return to the source (the generator). This is a parallel neutral situation.
Why is a Parallel Neutral a Problem? Stray Voltage/Current
Some of the neutral current may flow through the grounding conductor (the safety ground). The grounding conductor is not designed to carry normal current. This can lead to:
Increased risk of electric shock
If someone comes into contact with a grounded metal object (like a water pipe or appliance chassis) while the ground is carrying current, they could receive a shock.
Nuisance tripping of ground fault circuit interrupters (GFCIs)
GFCIs are designed to detect small imbalances in current between the hot and neutral wires. Current flowing through the ground wire can trigger these breakers even if there isn't a true fault.
Inaccurate voltage readings
Measurements may be skewed due to the complex current flow paths.
Overheating of Ground Wires
While the home's breaker might trip if the total current exceeds its rating, the ground wires may not be properly sized to carry the returning neutral current. The ground wires could then overheat.
The Solution: Switching the Bond (and Using a Transfer Switch Properly)
This is why people install a switch to disconnect the neutral-ground bond in their generator when using it with their home's electrical system via a transfer switch. How the Switch Works
The switch physically breaks the connection between the neutral conductor and the generator frame (which is connected to the ground prong).
When to Use the Switch
Bonded (switch OFF)
When the generator is used as a stand-alone power source (powering tools in the yard, for example), the bond should be ON.
Unbonded (switch ON)
When the generator is connected to the home's electrical system via a transfer switch, the bond should be OFF.
Important Note
This applies specifically when using a transfer switch. The transfer switch isolates your home's electrical system from the utility grid. This isolation is essential. If you are using a "suicide cord" connected to a standard wall outlet (which is HIGHLY DANGEROUS and illegal) the neutral ground bond could still be a problem.
Transfer Switches are Crucial
A properly installed transfer switch is the key to safely using a generator with your home. There are two main types: Manual Transfer Switch
You manually switch circuits from utility power to generator power.
Automatic Transfer Switch (ATS)
The transfer happens automatically when the power goes out.
The "Experts" and Code Considerations Electricians and Electrical Codes
Most qualified electricians will recommend (and many codes require) breaking the neutral-ground bond in the generator when used with a properly installed transfer switch. The National Electrical Code (NEC) addresses this, although the specifics can be complex and depend on the application.
Generator Manufacturers
Some generator manufacturers are now producing generators with a built-in switch to easily toggle the neutral-ground bond for different use cases.
Why the Breaker Might Not Always Trip
You're right to think about the breaker. However, the problem is not necessarily an overload that would trip the breaker. The issue is that current is flowing through the wrong path* (the ground wire), and the ground wire may not be sized for that current. Also, the amount of current flowing through the ground wire might not be enough to trip the breaker, but still be dangerous.
Bottom Line1. Never backfeed your house by plugging a generator into a wall outlet ("suicide cord"). This is extremely dangerous and illegal.2. If you plan to connect a generator to your home's electrical system, use a properly installed transfer switch.3. With a transfer switch, consider breaking the neutral-ground bond in the generator. Consult with a qualified electrician to determine the best and safest approach for your specific setup. They can assess your home's electrical system, the generator, and local codes to ensure everything is done correctly.4. If you have a generator with a switch, understand when to use it. Stand-alone = Bonded, Transfer Switch = Unbonded.5. When in doubt, consult with a qualified electrician. This is not a DIY project if you lack the knowledge and experience.Safety is paramount when dealing with electricity. Don't take shortcuts or assume you know enough. Call a professional. Flag for review