Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Unbalanced delta secondary voltages causing issues with ground fault relay

User: acolella, Location: NE (9.06 miles @5.9 Degrees from Winged Horses)

Asked on: Monday, January 13, 2025 at 10:23 pm EST
Answered on: Thursday, March 6, 2025 at 7:17 am EST

Question: I have two delta-delta transformers that have very unbalanced line to ground voltages on the secondary at no load. These are 480V-600V transformers.AB: 614V A-Gnd: 560V 0 ampsBC: 610V B-Gnd: 505V 0 ampsAC: 610V C-Gnd: 104V 0 ampsI understand that line to ground to voltages can be unusual on a delta system, especially at no load. The issue I am having is that these unbalanced voltages are causing my ground fault relays to indicate a fault. I have verified that there are no actual ground faults.I have the ground fault relays connected to shunt trip breakers. The idea is that if one of the legs goes to ground, the ground fault relay detects that and trips the breaker feeding the transformer primary. These relays are indicating a fault due to the voltage unbalance and trip the breaker as soon as the transformer is energized. If I disable the shunt trip and load up the transformer, the phase to ground voltages become much more balanced. The relay then no longer indicates a fault.AB: 604V A-Gnd: 334V 490.9 ampsBC: 602V B-Gnd: 362V 492.1 ampsAC: 601V C-Gnd: 347V 489.2 ampsHas anybody ever encountered this before? If so, what are some solutions? These particular ground fault relays are Littelfuse EL3100. Maybe I need a different type of relay for this application or maybe I need to build something. One of my coworkers suggested the idea of perhaps getting a small delta-wye transformer, connecting the primary of that to the 600V source and connecting the secondary to the ground fault relay. The idea being that the wye secondary should be pretty balanced and then if there is a fault on one of the primary legs, the secondary voltage should go unbalanced enough to make the relays fault.I appreciate any replies!Thanks!

You've accurately diagnosed the problem: circulating currents in the delta secondary, even at no load, are causing unbalanced line-to-ground voltages which, in turn, are tripping your sensitive ground fault relays. Delta systems are notorious for this, especially when you're dealing with slightly mismatched transformer windings or capacitance to ground.Here's a breakdown of possible causes and solutions

Understanding the Problem Deeper:
Capacitive Coupling to Ground

This is usually the biggest culprit. Every conductor (including transformer windings) has a small capacitance to ground. In a delta system, these capacitances form a network. Any imbalance in these capacitances, especially if the transformer core isn't perfectly grounded, leads to voltage differences between each phase and ground.


Transformer Imperfections

Minor differences in winding impedance (reactance and resistance) between phases, core asymmetries, and even manufacturing tolerances can contribute to unbalanced circulating currents.

Harmonics

Even if the source voltage
appears clean, harmonics (especially 3rd and its multiples) can circulate strongly in a delta, causing voltage distortions.

Relay Sensitivity

Some ground fault relays are designed to be very sensitive to even small imbalances, aiming to detect high-resistance faults. This is good for safety but can lead to nuisance tripping in your scenario.

Potential Solutions (Prioritized)


Grounding Resistors (Most Recommended)

This is the most robust and common solution for delta systems prone to this problem. You effectively create a "corner-grounded" or "high-resistance grounded" system without actually grounding one of the corners. Here's how:

Zig-Zag Grounding Transformer

This is the
ideal solution. A zig-zag transformer has a specialized winding configuration that provides a low-impedance path for zero-sequence (ground fault) currents while presenting a high impedance to normal balanced currents. It essentially creates a neutral point. When a ground fault occurs, the zig-zag transformer allows current to flow, which the ground fault relay can then detect.

Advantages

Superior fault current control, effective for high-resistance faults.

Disadvantages

Higher initial cost, physical space requirements.


Neutral Grounding Resistor (NGR)

If a zig-zag transformer is too expensive or space-constrained, you can use a single resistor connected between an artificial neutral (created by a wye-delta transformer) and ground, or simply across one of the phases to ground. The artificial neutral can be created by three equal value impedance or resistor voltage divider connected in Wye from each phase.

Advantages

More affordable than zig-zag transformer, limits ground fault current to a known value.


Disadvantages

Still requires some sort of neutral creation, might not detect very high-resistance faults as effectively as a zig-zag transformer.

Sizing the Resistor

The resistor value is chosen to limit the ground fault current to a safe and manageable level. You'll need to coordinate the resistor value with your ground fault relay settings.2.

Relay Adjustments (Carefully Considered)

Before changing relays entirely, try these (with extreme caution and understanding):


Increase Trip Threshold

The Littelfuse EL3100 might have adjustable settings for the trip current and time delay. Carefully increase the trip current threshold just enough to avoid nuisance tripping at no load. Do not disable the ground fault protection entirely! You are trading off some sensitivity for reliability. Document this adjustment thoroughly.

Increase Time Delay

A short time delay (e.g., 0.1-0.2 seconds) might allow the unbalanced voltages to settle down after energization before the relay trips. Again, be careful; you are slowing down the response to a
real fault.

Important Warning

Altering relay settings
must be done by qualified personnel with a thorough understanding of ground fault protection principles and the system's safety requirements. Improper settings can compromise safety.3.

Relay Replacement



Solid-State Differential Relay

These relays compare the currents entering and leaving the transformer. If there's a significant difference (indicating a fault), they trip the breaker. They are more sophisticated but less prone to nuisance tripping from capacitive imbalances. However, they can be more expensive.

Ground Fault Relay with Adjustable Filters

Some relays have built-in filters to attenuate harmonic frequencies or other noise that might be contributing to the imbalance.4.

Investigate and Reduce Capacitive Coupling



Shielded Cables

If you have long cable runs on the secondary side, consider using shielded cables. The shield should be properly grounded at one end to drain away stray currents.

Physical Separation

Keep secondary conductors physically separated from grounded structures as much as possible.


Transformer Core Grounding

Verify that the transformer core is properly grounded to the station ground. A poor or intermittent core ground can exacerbate capacitive imbalances.5.

Your Coworker's Suggestion (Delta-Wye Transformer)

This is not recommended as a primary solution. While it could theoretically work, it's essentially a workaround and doesn't address the underlying problem of unbalanced currents in the delta. It also adds another transformer to the system, increasing cost and complexity. The small delta-wye transformer would essentially be acting as a voltage transformer with the ground fault relays on the secondary. This would work, but is not ideal.

Steps to Take


Thoroughly Inspect

Visually inspect the transformers, wiring, and grounding connections. Look for loose connections, damaged insulation, or anything that could be contributing to leakage currents.2.

Measure Capacitance to Ground

Use a capacitance meter to measure the capacitance to ground of each phase on the secondary side. Significant differences between phases can indicate a problem.3.

Analyze Harmonics

Use a power quality analyzer to measure the harmonic content of the voltage and current on the secondary side. High harmonic levels can be a contributing factor.4.

Consult a Power Systems Engineer

Before making any significant changes to the system, consult with a qualified power systems engineer. They can perform a detailed analysis of your system and recommend the best solution.5.

Implement a Grounding Strategy

A well-designed grounding system is crucial for safety and reliability in any electrical system. The zig-zag grounding transformer is usually the preferred method, but a neutral grounding resistor may be acceptable for some applications.

Key Considerations



Safety

Ground fault protection is essential for safety. Never compromise safety by disabling or improperly adjusting ground fault relays.

Coordination

If you have multiple levels of ground fault protection, ensure that the relays are properly coordinated to avoid cascading trips.


Documentation:
Thoroughly document any changes made to the system, including relay settings, grounding configurations, and test results.By systematically investigating the problem and implementing the appropriate solutions, you should be able to eliminate the nuisance tripping and ensure reliable ground fault protection for your transformers. Start with investigating the capacitive coupling and then consult with a power systems engineer about implementing a grounding resistor strategy. Flag for review

Previous Question Next Question