Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Medical Installations

User: medinajuli, Location: Florida

Asked on: Tuesday, January 14, 2025 at 6:37 pm EST
Answered on: Thursday, March 6, 2025 at 7:20 am EST

Question: Hello fellas:I have an existing installation, and I want to adapt it for a medical office. The NEC in section 517.13 requires me to install an additional conductor for the isolated ground. Can this conductor be added in the same wiring route, or do I have to change all the wiring that goes to each receptacle?Many thanks!!JM

Okay, let's break down the requirements of NEC 517.13 regarding isolated grounds in healthcare facilities and how it applies to your situation.

Understanding 517.13 and Isolated Grounds

NEC 517.13(A) typically requires that receptacles and fixed electrical equipment in patient care areas of a healthcare facility have a redundant grounding system. This usually involves: Equipment Grounding Conductor (EGC)

The normal EGC run with the circuit conductors (e.g., green wire in conduit).


Supplemental Grounding (Isolated Ground)

This is where 517.13 comes into play. It often requires an additional insulated equipment grounding conductor, known as an isolated ground (IG) conductor. This conductor is insulated from the raceway and enclosure and terminates at a single point within the power distribution system (typically the panelboard or a separately derived system).

Can You Add an Isolated Ground Conductor to an Existing Wiring Route?
Yes, you can add an isolated ground conductor to the existing wiring route, as long as you follow specific requirements.

Here's a breakdown: General Rule

NEC 517.13(A) typically dictates that the isolated ground wire must be run with the other circuit conductors. This means it must be contained within the same raceway, cable, or wiring method as the hot, neutral, and equipment grounding conductor.


Retrofitting

Retrofitting is where you want to pay extra attention. It is not uncommon to pull an additional wire to meet code in existing installations.

Integrity of the Grounding System

The goal is to provide a low-impedance path back to the source. So the new isolated ground conductor should be sized according to NEC 250.122. It should also have a green insulation with a yellow stripe (or be otherwise permanently identified as an isolated ground conductor per 250.119).


Termination

The isolated ground conductor must be terminated properly. It can only connect to the isolated ground terminal on the receptacle and at the designated single point in the power distribution system (usually the panelboard).

Important Considerations and Precautions
1. Local Amendments and Interpretations

Healthcare facility electrical codes can be very strict and may have local amendments or interpretations. Always consult with the local authority having jurisdiction (AHJ) and/or a qualified electrical engineer experienced in healthcare facility electrical systems. Get their specific guidance on the acceptability of adding an isolated ground conductor in your particular situation.2.

Existing Wiring Condition

Carefully inspect the existing wiring and raceway. Make sure there's enough space to add the isolated ground conductor without damaging the existing conductors. If the raceway is already full, you cannot simply cram another conductor in there. It may violate fill requirements and create a safety hazard.3.

Continuity of the EGC

Verify that the existing equipment grounding conductor (EGC) is properly sized and continuous throughout the circuit. The isolated ground is supplemental to the EGC, not a replacement.4.

Receptacle Type

Use receptacles specifically designed for isolated grounds. These are usually orange in color and marked with a triangle.5.

Planning and Documentation

Document all modifications and testing performed. This will be important for future inspections and maintenance.6.

Testing

After installation, perform thorough testing to verify the integrity of the grounding system, including voltage drop tests and impedance measurements.7.

Qualified Personnel

Only qualified and licensed electricians with experience in healthcare facility electrical systems should perform this work.

In Summary


Adding an isolated ground conductor to an existing wiring route is generally acceptable as long as the conductor is run with the circuit conductors, is properly sized and identified, and the existing wiring and raceway are in good condition. However, always check with the local AHJ to verify compliance with local codes and requirements. Improperly installed isolated grounds can create hazards and not provide the intended benefits. Flag for review