Topic: Sizing MCB for Panelboard

User: CopperYeti, Location: Florida

Asked on: Thursday, January 16, 2025 at 3:34 pm EST
Answered on: Thursday, March 6, 2025 at 7:26 am EST

Question: Hi All,I have some questions about sizing a Panelboard MCB based upon the total connected kVA load. Panelboard is a 208/120v, 3Phase.If I have a Panelboard with a total connected load of 78.3 kVA: 78300/208√3 = 217 Amps. How would you size this panelboard?- Connected load amps (217 A) and add a 10% or 25% spare capacity margin?- Size based on next C/B size up from 217 -> 225A MCB?- Add a Spare Capacity margin and then go to the next C/B size up? 217 * 1.25 (25% Spare Capacity) = 272 Amps -> 300 Amp MCB?- Should you ever size a Panelboard MCB based off of the 80% circuit breaker load rule?If there are any more tips about sizing MCBs for Panelboards, it is greatly appreciated. I'm a younger design engineer trying to build good design practices.Thanks in advance!

Okay, let's break down panelboard main circuit breaker (MCB) sizing based on your connected load. You've got the basic calculations correct, but the reasoning behind the choices is key.

Understanding the Considerations Connected Load

This is the
maximum possible current your connected equipment could draw if everything ran at its nameplate rating simultaneously. This almost never happens in real life, which is why diversity/demand factors are crucial (see below).

Continuous vs. Non-Continuous Loads

This is a key concept from the NEC. A continuous load is one that is expected to operate at its maximum current for 3 hours or more at a time. Loads that run for shorter durations are considered non-continuous. This affects the 80% rule.

Demand/Diversity Factors

These are multipliers you apply to your connected load to account for the fact that not everything will be running at its maximum simultaneously. This is where experience and knowledge of the
specific application come in. For example, a residential panelboard might have a lower demand factor than a commercial kitchen panelboard. You need to determine appropriate demand/diversity factors before calculating your load.

Spare Capacity

This is a buffer for future expansion. It's good practice, but the amount depends on your client's needs and budget.

80% Rule (125% Rule)

This is the most misundersood thing about sizing breakers. NEC 210.20(A) and 215.3 state overcurrent protection (circuit breaker or fuses) are sized at
no less than 125% of the continuous loads plus 100% of the non-continuous loads.

Standard Breaker Sizes

Circuit breakers come in standard ampacities. You can't just pick any arbitrary size.

Panelboard Busbar Rating

The panelboard itself has a maximum current rating for its busbars (the internal conductors that distribute power). You
must ensure your calculated load and the breaker you select do not exceed the panelboard's busbar rating.

Feeder Conductor Ampacity

The wires feeding the panelboard must also be sized to handle the calculated load and must be protected by the main breaker.

Step-by-Step Sizing Process
1. Determine Connected Load (You've Done This): In your example, 78.3 kVA gives you 217 amps at 208V, 3-phase. This is the starting point.2. Apply Demand/Diversity Factors

This is the most important step and requires specific knowledge of the application. Let's assume, for the sake of example, that you've analyzed your load and determined a demand factor of 70% is appropriate. Demand Load: 217 amps 0.70 = 151.9 amps.
3.


Determine Continuous and Non-Continuous Loads

Let's say after demand factor, 150A is 120A (continuous load) and 31.9A (non-continuous load).
4.


Apply the 125% Rule (80% Rule)
(Continuous Load 1.25) + Non-Continuous Load = Breaker Amperage (120A 1.25) + 31.9A = 181.9 Amps5. Add Spare Capacity (Optional)

This is a judgment call. If you anticipate future loads, add a percentage here. Let's assume you want 20% spare capacity. 181.9 Amps 1.20 = 218.3 Amps6.

Select Next Standard Breaker Size

Find the next standard breaker size above your calculated value. Common standard sizes are 15, 20, 30, 40, 50, 60, 70, 80, 90, 100, 110, 125, 150, 175, 200, 225, 250, 300, 350, 400, etc. In this case, the next size up from 218.3 amps is a

225 Amp
breaker.7. Verify Panelboard Busbar Rating

Make
absolutely sure that the 225 amp breaker does not exceed the panelboard's busbar rating. You'll need to look at the panelboard's specifications. If the busbar rating is less than 225 amps, you'll need to select a panelboard with a higher busbar rating.8.

Size Feeder Conductors

Size the wires feeding the panelboard to be rated for at least 181.9 amps (your load calculation
before adding spare capacity) and to be protected by the 225 amp breaker (NEC 240.4(B) allows you to use the next standard breaker size if your conductor ampacity doesn't perfectly match a standard breaker size if certain conditions are met).

Addressing Your Specific Questions
Connected load amps (217 A) and add a 10% or 25% spare capacity margin?

No. Using the connected load directly without demand factors will almost always result in an oversized and expensive system. Spare capacity is added after applying demand factors and the 80% rule.

Size based on next C/B size up from 217 -> 225A MCB?

No, unless you have a 100% demand factor and there are no continuous loads.


Add a Spare Capacity margin and then go to the next C/B size up? 217 1.25 (25% Spare Capacity) = 272 Amps -> 300 Amp MCB?

Again, no. Spare capacity is added
after applying demand factors and the 80% rule. Also, using 217A is incorrect.

Should you ever size a Panelboard MCB based off of the 80% circuit breaker load rule?
YES! The 80% rule is the 125% rule in the NEC. The overcurrent protection (circuit breaker or fuses) are sized at no less than 125% of the continuous loads plus 100% of the non-continuous loads.

Tips for Young Design Engineers Always document your assumptions. Clearly state the demand factors you used and the reasoning behind them. This is critical for future reference, troubleshooting, and potential changes. Understand the specific application. Don't just guess at demand factors. Talk to experienced engineers, research industry standards, and understand how the equipment will actually be used. Consult the NEC and other relevant standards. Don't rely solely on memory. The code is your guide. Use load calculation software. Software can help with the math, track loads, and ensure you're considering all relevant factors. Review your work. Have a senior engineer review your calculations and designs, especially when you're starting out. Don't be afraid to ask questions. It's better to ask a "stupid" question and learn than to make a costly mistake.

In Summary

The key to properly sizing a panelboard MCB is to:1. Accurately determine the actual expected load by using appropriate demand/diversity factors.2. Apply the 125% rule on continuous and non-continuous loads.
3. Add spare capacity based on anticipated future needs.4. Select the next standard breaker size above your calculated value.5. Verify that the breaker and calculated load do not exceed the panelboard's busbar rating.
6. Size feeder conductors to match.By following these steps, you'll be well on your way to creating safe, reliable, and cost-effective electrical designs. Good luck! Flag for review