Question: Does 110.34(A) apply to VFD's? I always thought it was just for switches, CB's, switchgear and switchboards?

You're right to question the application of 110.34(A) to VFDs. Let's break it down: 110.34(A) is about Working Space

This section of the NEC deals with the
required working space around electrical equipment. Specifically, it provides the dimensions of the clear space needed in front of energized equipment that is likely to require examination, adjustment, servicing, or maintenance while energized.

The Scope of 110.34(A)

While the language isn't always perfectly clear, the intent of 110.34(A) is geared toward equipment that personnel would frequently need to access while energized, such as: Switchboards Switchgear Panelboards Motor Control Centers (MCCs) Large disconnect switches Circuit breakers

VFDs and 110.34(A)

This is where it gets nuanced. 110.34(A)
can apply to VFDs, but it depends on the specific installation and maintenance requirements. Here's how to think about it:

If the VFD requires regular maintenance or troubleshooting while energized, 110.34(A) likely applies.
Examples of such activities include: Voltage or current measurements. Checking status indicator lights. Adjusting parameters. Replacing small components (like fuses). If the VFD is installed in a way that requires opening the enclosure and working on energized parts for normal maintenance, 110.34(A) definitely applies. If the VFD is a "set it and forget it" type of installation, where the VFD is commissioned, the parameters are set, and no further access is expected until the unit fails, then 110.34(A) might not be strictly enforced. However, even in this case, it's prudent to provide reasonable working space for future troubleshooting or replacement. Consider the Size and Voltage

The larger the VFD and the higher the voltage, the more critical 110.34(A) becomes. Larger VFDs are often more complex and have higher voltage components, increasing the likelihood of needing to work on them while energized.

In summary

While 110.34(A) isn't explicitly called out for VFDs, the
need for working space as defined by 110.34(A) can exist. It's best practice to err on the side of caution and provide adequate working space around VFDs, especially larger units. Consider the types of maintenance that might be required and whether those tasks would involve working on energized parts.

Important Considerations



Manufacturer's Instructions

Always consult the VFD manufacturer's installation and maintenance instructions. They may specify required clearances or working spaces.

Local AHJ (Authority Having Jurisdiction)

The AHJ has the final say in interpreting and enforcing the NEC. Check with your local inspector for their interpretation and requirements.


Safety

Regardless of whether 110.34(A) is strictly enforced, prioritize safety. Working on energized equipment should only be done by qualified personnel with appropriate PPE and following safe work practices.

In conclusion, while 110.34(A) is not automatically applicable to all VFD installations, it's crucial to assess the potential need for working on the VFD while energized and provide adequate working space accordingly, keeping safety and manufacturer's recommendations in mind.