Topic: Undesirable DC current solutions?

User: TwoBlocked, Location: Bradford County, PA

Asked on: Sunday, January 19, 2025 at 7:06 am EST
Answered on: Thursday, March 6, 2025 at 7:30 am EST

Question: We've been experiencing problems with the ABB XIO controllers. My thinking is that there is undesirable DC current in the negative busses due to the chassis and all the negative terminals on the I/O cards being bonded to together through the DIN rail. The power terminals on the controller do not have a separate ground, just a positive and a negative, with the negative internally bonded to the chassis.I see this as the same as the AC definition of undesirable current when the Equipment Grounding Conductor and the Neutral are bonded together at the field devices. Negative DC current anywhere in the system can flow through the grounded negative busses in the controller and the I/O cards.The problem that is being experienced is the analog input cards lose their "calibration" sometimes for no apparent reason, and sometimes related to a DC breaker opening. When "calibrating" an AI point on these, using the programming software, 4mA and then 20mA is sourced to the card and the chosen Engineering Units are assigned to these values. I would call it scaling, not calibration... So what happens is that instead of the program using the calibrated/scaled units, unexpectedly, other values are used. Of course everything goes whacko, we get called in, and "re-calibrate."The local ABB Guru was consulted and he said the problem is with the inductive kick back from solenoids, both those operating valves and those operating relays. His solution is to install 6 amp diodes (Six Amps !!!) across all the wet and all the dry contacts of circuits controlling the solenoids. This includes the open collector outputs on the DI/DO cards going to din mounted wafer relays. (Really ???) I was told this was a dirty little secret that ABB knows about but won't publish. (Hmmm, Colonel Mustard, in the drawing room, with the candlestick?)OK, I haven't personally talked to the Guru about this (a great, very knowledgeable guy) but plan to tomorrow. The solution is what was explained to me by someone else. (Yeah, one of the Fine Fellows involved in the single phase motor VFD fiasco...) I am very familiar with protecting contacts on control devices (especially wet ones) that feed inductive loads with various types of "snubbers." Doing so won't "hurt" anything, although it introduces another potential point of failure. But it will still send the inductive kick back current from the solenoid to the chassis ground where it can still flow through the negative buss of the controller and I/O cards, which I believe is the real problem.My thought is to electrically isolate the controller and I/O cards from the backplane, thereby producing a system with an isolated ground; the negative to the controller would be the only ground connection. I often see this in quality installations. Will also need to ensure that the negative return from field devices go to the specific I/O terminal point, and not to a convenient negative terminal somewhere else.So I am asking you fine folks for two things:1. Are my thought processes on the right track?2. Can you point out me to some good documentation about installing controllers with isolated grounding? I've looked for stuff, but it all seems to be either about grounding just one end of instrumentation shielding or about receptacles with isolated grounding. I want something independent to show those that make these decisions.It's already on this week's schedule for the techs to go out and start installing 6A diodes all over the place. If this is a bad idea, like I am convinced it is, I want to "head it off at the pass." (Yeah, I like westerns. )

You've got a good, systematic approach to this problem, and your concerns are valid. Let's break down your thoughts and address your questions.1. Are my thought processes on the right track?

Yes, absolutely. Your concerns about circulating DC currents in the negative bus and the potential for them to disrupt sensitive analog input calibration are legitimate and well-reasoned. Let's unpack why: DC Current in Negative Bus

You're correctly identifying the potential for circulating currents. If the negative terminals of your DC power supply, I/O cards, and the chassis are all bonded together, it creates a parallel path for DC current. Any slight voltage differences (created by solenoids, power supply imperfections, or other noise sources) can drive current through this unintended path. This current
can impact the performance of sensitive analog circuits, especially if they share that same reference point.

Analogy to AC Grounding

Your analogy to AC grounding issues is apt. Bonding the neutral and ground at multiple points in an AC system creates unwanted current flow in the equipment grounding conductor. The DC equivalent is unwanted current flow in the shared negative bus.

"Calibration" Issue

The fact that the analog input cards lose their "calibration" (really scaling) is a red flag. While inductive kickback
could contribute, it shouldn't be the primary cause of a scaling drift, especially if the drift is correlated with DC breaker tripping. The correlation with breaker tripping strongly suggests a system-wide grounding/noise issue.

ABB Guru's Solution

The diode solution is... questionable. While inductive kickback suppression is important, slapping 6A diodes across every contact seems like a shotgun approach. More importantly, as you point out, it doesn't address the underlying grounding issue. The energy from the inductive kick is still being dumped into the grounding system.

2. Can you point me to some good documentation about installing controllers with isolated grounding?


Finding definitive "isolated grounding" documentation for industrial DC control systems can be tricky because it's often embedded within broader EMC and system design guidelines. However, here's a breakdown of what you should look for and where to find it, along with some principles to guide your research

Key Concepts to Search For:
Single-Point Grounding

This is the fundamental principle. The idea is to establish
one and only one point in your system where the DC negative and chassis ground are connected.

Star Grounding

A variant of single-point grounding where all ground returns converge on a central grounding point.

EMC (Electromagnetic Compatibility) and EMI (Electromagnetic Interference) Mitigation

Isolating grounds is a key technique for reducing noise and improving EMC performance.


Instrumentation Grounding

While your application isn't just instrumentation, the principles of grounding for sensitive measurement devices apply.

Floating Grounds

Understand what a floating ground is (an ungrounded system) and why it's generally not recommended for safety reasons. You want
isolated grounding, not floating.

Ground Loops

Learn about ground loops (circulating currents in grounding paths) and how to prevent them.

Where to Look for Documentation



Industrial Automation Guides (General)

Search for "industrial control system grounding best practices" or "EMC guidelines for industrial automation." Look for white papers and application notes from major automation vendors (Siemens, Rockwell Automation, Schneider Electric) - even if they don't directly address ABB, the principles are often transferable.

EMC and Electrical Safety Standards



IEC 61000 series

This is the international standard for EMC. It's broad, but it contains sections relevant to grounding and noise reduction. It's a very detailed and technical series of standards and probably more in depth than what you're looking for to hand over to people.


IEEE 1100 (Emerald Book)

Recommended Practice for Powering and Grounding Electronic Equipment. This focuses on AC systems, but it's an excellent resource for understanding general grounding principles.

Specific Component Manufacturers

Check the documentation for your DC power supplies, PLCs, and I/O cards. They may have recommendations on grounding.

ABB Documentation (More Specific)

Search the ABB website for technical documents related to noise immunity, EMC, and grounding for their XIO controllers. They may have something hidden away in a less obvious section.

Practical Steps and Justification

Here's how you can justify your proposed approach:1.

Demonstrate the Problem

Use a multimeter to measure the DC current flowing in the DIN rail or the negative bus of the controller. This provides concrete evidence of the circulating current. Document these measurements.2.

Explain the Theory



Ground Loops

Explain how the multiple grounding points create parallel paths for current flow and how this can introduce noise into the analog signals. Draw a diagram showing the current flow.


Impact on Analog Accuracy

Explain how small voltage fluctuations on the ground reference can directly impact the accuracy of analog-to-digital conversion in the I/O cards.

Single-Point Grounding as a Solution

Describe how a single-point grounding system eliminates the parallel paths and reduces the potential for noise injection.3.

Propose the Solution



Isolate the Controller and I/O Cards

You're suggesting electrically isolating the controller and I/O cards from the DIN rail. This means using non-conductive mounting hardware (if feasible) or insulating washers to prevent direct electrical contact. Before doing this, carefully consider safety implications (see note below).

Dedicated Negative Returns

Ensuring that the negative return from field devices goes directly to the I/O terminal is critical. This prevents current from flowing through the DIN rail.


Single-Point Ground Connection

Establish a single, dedicated grounding point for the DC negative. This should be a robust connection to the system ground.

Shielding

While not directly related to the negative bus issue, ensure proper grounding of instrumentation cable shields (typically grounded at one end, preferably the source).4.

Present the Benefits



Improved Analog Accuracy

More stable and reliable analog readings.

Reduced Noise

Lower noise floor, improving the overall performance of the control system.


Increased System Stability

Less susceptibility to ground-related problems.

Longer Component Life

Reduced stress on components due to circulating currents.

Important Safety Considerations



Safety Grounding

Never compromise safety grounding. The chassis of the controller MUST be properly grounded for safety reasons (protection against electric shock). Your goal is to isolate the DC negative bus from the chassis ground to prevent circulating currents, not to create a floating ground.

Isolation Testing

Before and after making any changes, perform insulation resistance tests to ensure that there are no unintended shorts to ground.


Consult an Electrical Engineer

If you're unsure about any aspect of grounding or electrical safety, consult a qualified electrical engineer. This is especially critical when dealing with potentially hazardous voltages or environments.

Why the Guru's solution might be misguided (but with a grain of salt)

While I'm skeptical of the "6A diode everywhere" approach, it's possible the guru is seeing a specific manifestation of inductive kickback that's causing problems. However, it's far more likely that the grounding issue is the root cause, and the inductive kickback is simply exacerbating the problem. Diodes across inductive loads are good practice in general and help to protect the switching devices controlling the loads (like relay contacts or transistors). Usually, the diodes are much smaller (e.g., 1N4001, 1N4007, etc).

Action Plan


Measure the DC Current

Start by documenting the DC current flow in the grounding paths.2.

Discuss with the Guru

Talk to the ABB guru directly. Ask him to explain why he believes the 6A diode solution is necessary and what specific symptoms he's observed. Ask how this ties into the negative buss issue.3.

Present Your Findings

Present your findings and your proposed solution to the decision-makers. Emphasize the theoretical basis for your approach and the potential benefits.4.

Implement a Pilot Project

If possible, implement your solution on a small, isolated section of the system. This allows you to test the effectiveness of your approach without disrupting the entire system.5.

Monitor and Document:
Carefully monitor the system after implementing your solution. Document any changes in analog accuracy, noise levels, and system stability.By taking a systematic approach and backing up your recommendations with data and sound engineering principles, you'll be much more likely to get buy-in for your proposed solution. Good luck "heading it off at the pass!" You've got a solid plan. Just remember to emphasize safety and consult with experts if needed.Remember to always prioritize safety. If you're not comfortable with any of these steps, consult a qualified electrician or electrical engineer. Flag for review