Question: How often would you have to actually remove the circuit back to the power source? By code could abandon it? Guess for bidding purposes one should price to remove? The panel is about 80' away and it's a dedicated circuit. Maybe could even use existing circuit for new wash bar GFI.

Okay, let's break down the considerations for removing or abandoning a dedicated circuit during a renovation or electrical upgrade. This involves code compliance, safety, and best practices, all of which impact your bidding strategy.

Code Requirements and Considerations NEC (National Electrical Code)

The NEC is the primary governing document for electrical installations in the US. While it doesn't explicitly
require removal in many cases, it heavily influences whether abandonment is acceptable. Here's the key:

Unused Conductors (300.15(G))

The NEC generally requires unused conductor runs to be terminated appropriately at both ends. This is where things get interesting. Leaving unterminated wires can create potential hazards and is against code.

Abandoned Cables (725.3(B) regarding Class 2 and Class 3 circuits and Article 800 regarding communications circuits) & (Article 820, 830, and 840 regarding coaxial, network-powered broadband communications, and premises-powered broadband communications circuits)

These articles outline requirements for specific types of cables that are abandoned. While not directly applicable to a general-purpose 120V or 240V circuit, they reflect the general spirit of ensuring unused wiring isn't left as a hazard.


Local Codes and AHJ (Authority Having Jurisdiction)

Crucially, local codes can be stricter than the NEC. An electrical inspector (the AHJ) has the final say. They might have specific rules or preferences regarding abandoned wiring.

Always check with the local building department or inspector before making a decision.
When is Abandonment Acceptable (Potentially)?

If you choose not to remove the wiring, proper and safe abandonment is crucial:1. Disconnect at the Source (Panel)

Absolutely must disconnect the breaker or fuse that feeds the circuit. Cap the wires in the panel with wire connectors or electrical tape.2.

Disconnect at the Load End (Outlet/Appliance)

Remove the outlet or appliance. Cap the wires individually with appropriate wire connectors (wire nuts or Wago connectors).3.

Accessibility

If the wiring is concealed within walls or ceilings, abandonment becomes more complicated. If you cannot access the wires at both ends without significant demolition, then you might have no other choice than to abandon the wires in place.

Arguments for Removal (The Safer/Best Practice)



Eliminates Future Confusion

Someone in the future (including you!) might mistakenly think the circuit is active and try to use it, creating a hazard.


Prevents Accidental Energizing

Even with precautions, there's a small chance of accidental re-energization.

Cleaner and More Professional

Removal leaves a cleaner installation and reduces the likelihood of issues arising during future inspections or work.


Prevents Pests

Abandoned wires can, in some cases, provide a pathway for rodents or insects.

Using the Existing Circuit for a New Wash Bar GFCI
Code Compliance

This is
potentially possible, but highly dependent on several factors:

Circuit Capacity

Is the existing circuit large enough (amperage) to handle the added load of the wash bar/GFCI receptacle plus any other devices already on the circuit? GFCI circuits in bathrooms often have specific load limits. Calculate the total load.

GFCI Protection

Is the circuit already GFCI-protected? If not, you'll need to install a GFCI breaker at the panel
or a GFCI receptacle as the first outlet on the circuit, protecting downstream outlets.

Dedicated Circuit Definition

By definition a dedicated circuit is used to power a single specific appliance. You would need to verify if you're able to add the wash bar outlet by code.

Wire Condition

Inspect the existing wiring. Is it in good condition? Is the insulation brittle or cracked? If there's any doubt, replace the wiring.


Practicality

Is the existing wiring in the right location for the new wash bar outlet? Can you easily run it to the desired location without excessive patching or demolition?

Bidding Considerations
1. Include Options

Present the customer with two options in your bid:

Option 1: Remove and Replace.
This is the safest and most compliant. Price it accordingly. Factor in the cost of new wiring (80' run), labor, and disposal of the old wiring. Option 2: Abandon in Place (Subject to AHJ Approval). Clearly state that this option is contingent on the local electrical inspector approving the abandonment method. Price this lower than the removal option, but still include labor for proper disconnection and capping of wires at both ends. Make sure to state you are not responsible for any failed inspections based on this installation method.2. Clarify Assumptions

State in your bid what you are assuming about the existing wiring (condition, capacity, etc.). If assumptions are wrong, the price may change.3.

GFCI Upgrade

If you are considering using the existing circuit for a new GFCI outlet, include a line item for "GFCI Protection Upgrade" (breaker or receptacle), and clearly explain what's involved.4.

Contingency

Add a small contingency to your bid to cover unforeseen issues (e.g., difficult wiring runs, unexpected damage during removal).5.

Permitting

Include the cost of an electrical permit in your bid. This is essential to ensure compliance and a proper inspection.

Example Bid Snippet



Option 1: Dedicated Circuit Removal and New Circuit Installation

Disconnect and remove existing dedicated circuit (80' run) back to panel. Install new 12 AWG THHN wiring (80' run) from panel to new wash bar location. Install new 20 amp circuit breaker in panel. Install new GFCI receptacle at wash bar location. Electrical permit and inspection fees included. Total: \$XXX.XX

Option 2: Dedicated Circuit Abandonment and New GFCI Installation (Subject to AHJ Approval)

Disconnect and safely cap existing dedicated circuit at panel and at load end. Install new GFCI receptacle at wash bar location, utilizing existing circuit (subject to capacity verification). Electrical permit and inspection fees included. Total: \$YYY.YY Note: This option is contingent upon approval from the local electrical inspector. If abandonment is not approved, Option 1 will be required.
In summary:
While abandoning might* be technically possible in some cases, removal is generally the safer, cleaner, and more professional approach. Always get local AHJ guidance and provide your client with options that clearly outline the pros and cons of each. Good luck with your bid! Flag for review