Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Disable generator auto-start when emergency disconnect

User: ChasM, Location: North Texas

Asked on: Wednesday, January 22, 2025 at 10:16 pm EST
Answered on: Thursday, March 6, 2025 at 7:39 am EST

Question: I understand that NEC 230.85 now requires an emergency disconnect switch (EDS) to be installed on the outside of a house so emergency responders can remove all electrical power from the building. The house is supplied with a 120/240V, 200A split phase electrical service (L1, L2, and N).However, this requirement becomes somewhat of an enigma when there is a generator with an automatic transfer switch (ATS) at the house with an auto-start capability when utility power is lost. In this situation the generator would immediately try to autostart when the emergency responder opens the emergency disconnect switch, thus energizing the house electrical systems. Not a good situations!I would like to configure an approach where the emergency responder action does not cause thr generator to autostart. I see several possibilities and would like some feedback back on my preferred solution.1. Add a second emergency disconnect switch for the generator next to the unity servcoe switch - Not a good situation since the emergency responder must open two switches to remove all power from thr house.2. Connect the EDS between the house electrical panel and the house output from the ATS - Not a good solution since the ATS and the generator remain have full electrical power with thr house circuits isolated.3. Preferred approach - Make use of the Generac remote start feature by running the two remote start control wires through the third pole/blade of the EDS. In normal operation, when the EDS is normally closed the generator will automatically startup and power thr house when utility power is lost. When the EDS is opened by an emergency responder, the generator autostart function is disabled preventing the generator from starting and all power is removed from the house by a single emergency responder action. This appears to be the correct solution however does the 2020 NEC allow control wiring to be rooted through one of the poles of a three pole EDS.I would appreciate any comments on my house requirement so the emergency responder is protected in the best manner possible.

You've outlined the core problem and some potential solutions accurately. The critical issue is ensuring that disconnecting the utility power doesn't inadvertently energize the house via the generator. Let's break down your proposed solutions and address the NEC compliance aspects.

Understanding the Problem

Your understanding is correct. The NEC 230.85 requirement is designed to provide a single point of disconnect for emergency responders. The presence of an automatic standby generator significantly complicates this, as a simple disconnect could trigger the generator and re-energize the system.

Analysis of Proposed Solutions1. Two Disconnects

This is generally discouraged and likely

not compliant
with the intent of NEC 230.85. The goal is a single, easily identifiable disconnect. Requiring emergency responders to locate and operate two separate switches increases the risk of error, delay, and potential hazard. It introduces confusion and undermines the purpose of the emergency disconnect.
2. Disconnect Between Panel and ATS

This approach is

not a viable solution
. It isolates the house panel from both utility and generator, but leaves the ATS and generator energized. This doesn't eliminate the hazard because the generator could still be manually started or malfunction, potentially backfeeding the system. It also does not meet the requirement of disconnecting ALL power sources to the building.3. Using EDS to Interrupt Remote Start

This is the most promising approach, but needs careful examination for NEC compliance. Here's a detailed breakdown:

Concept

You are proposing to use the EDS to break the control circuit that initiates the automatic generator start. By doing so, even if the utility power is lost (simulated by opening the EDS), the generator won't start. This is a good way to eliminate the hazard.


NEC Concerns



230.85 (Emergency Disconnects)

While not explicitly prohibiting this approach, the focus of this section is on disconnecting conductors that carry power to the building. Your concern about interrupting the control wiring is reasonable, as is the approach you propose. The spirit of the code is to eliminate all sources of power, and disabling the automatic start achieves that.


300.3 (Conductors of Different Systems)

A key area of concern is running low-voltage control wires (the generator remote start wires) within the same raceway, cable, or enclosure as the 120/240V service conductors. This can be permissible, but only under strict conditions:

300.3(C)(1)

Wiring Methods. If the control wiring and power conductors are installed in a raceway, that raceway must be approved for the voltage of the highest voltage circuit within the raceway, in this case 240 volts. This means using the correct type of conduit and fittings. If the control wiring and power conductors are installed in a cable, that cable must be approved for the voltage of the highest voltage circuit within the cable, in this case 240 volts.

300.3(C)(2)

Equipment Wiring. Wiring internal to factory assembled equipment is not governed by the same constraints as field installed wiring. This exception would not be applicable in your scenario.

Article 700 (Emergency Systems)

If your generator is part of a legally required emergency system (e.g., for fire pumps or life safety systems), additional requirements apply. It's unlikely in a typical residential setting.


Generac Installation Manual

You MUST consult the Generac installation manual for their specific recommendations and requirements for remote start connections. They may have specific instructions or warnings about using external disconnects on the control circuit.

Implementation



Use the correct blade of the EDS

You would need a 3-pole EDS. Two poles would be for the normal L1 and L2. The third pole should be dedicated solely to switching the generator remote start control circuit. The neutral (N) wire would NOT be routed through the EDS.

Wiring Method

The remote start control wires MUST be rated for the same voltage as the L1 and L2 cables (240 volts).


Enclosure

The generator remote start control wires could be routed through a separate conduit/fitting through the EDS enclosure.

Signage

A clear label should be placed next to the EDS stating: "EMERGENCY DISCONNECT - DISCONNECTING THIS SWITCH WILL PREVENT AUTOMATIC GENERATOR START."

Recommendations and Considerations
1. Consult with a Licensed Electrical Engineer or Master Electrician

This is not a DIY project. The NEC is complex, and the potential for serious injury or death is real. A qualified professional can assess the situation, ensure code compliance, and provide a safe and reliable installation. They can also review local amendments to the NEC that might affect your installation.2.

Contact Your Local Authority Having Jurisdiction (AHJ)

The AHJ (usually the city or county electrical inspector) has the final say on code interpretation and enforcement. It's prudent to discuss your proposed solution with them
before starting any work. They may have specific requirements or preferences.3.

Consider Alternative Solutions (if possible)



Generator Control Module with Emergency Stop Input

Some generator control modules have a dedicated emergency stop input that can be wired to the EDS. When this input is activated, the generator will shut down and prevent starting. This may be a cleaner solution than interrupting the remote start circuit.4.

NEC Requirements for Service Disconnects

Remember that your EDS must meet all the requirements for service disconnects as outlined in Article 230 of the NEC, including:

Readily Accessible

It must be easily accessible to emergency responders.


Suitable for Service Equipment

It must be rated for use as service equipment.

Externally Operable

It must be operable from the outside of the house without opening the enclosure.


Clearly Marked

It must be clearly and permanently marked as an emergency disconnect.

In summary,
while using the third pole of the EDS to interrupt the generator remote start circuit is potentially viable, it requires careful planning, proper wiring methods, and approval from your local AHJ. Consult with a qualified electrical professional to ensure a safe and code-compliant installation. Ignoring the NEC and potentially creating a dangerous situation is not an option. Flag for review

Previous Question Next Question