User: Eliaso, Location: Albuquerque NM
Asked on: Thursday, January 23, 2025 at 8:53 am EST
Answered on: Thursday, March 6, 2025 at 7:41 am EST
Question: I’ve been doing quite a few Resi standby generators. Most I’ve used a service rated 200 amp ATS installed right after the utility meter. Recently a inspector questioned the size of the generator that services the ATS. It’s a 26kw with a 110 amp breaker. So I ran #3 copper from the ATS to the Gen. He’s trying to say that generator need to provide 200 amps since is feeding a 200a ATS. I’m trying to find an article that explains if this 26kw is acceptable. I’m in Albuquerque NM. Thanks for the help.
Okay, I understand your situation. Here's a breakdown of the code considerations and how to address the inspector's concerns, along with relevant NEC references and strategies for communication
Understanding the Inspector's Concern
The inspector's concern stems from the common assumption that the generator should be able to supply the full rated amperage of the transfer switch. In his mind, a 200A transfer switch implies a 200A source is required. However, this isn't necessarily true, especially in residential standby applications.
Key NEC Articles and Considerations NEC 702.4(B) Size of Alternating-Current Generator Set. "(B) Sizing of Alternating-Current Generator Sets. Alternating-current generator set(s) shall be of sufficient capacity to supply the loads to be transferred, plus the transfer equipment." This is the core article. The generator must be sized to handle the load being transferred, plus the transfer equipment itself. It doesn't say it must be sized to the full rating of the transfer switch. NEC 220.10 General. "(A) Ampere Rating. Feeders and branch circuits shall have sufficient ampacity to carry the calculated loads, and shall not be smaller than the rating of the overcurrent protective device protecting the circuit." This article, while more general, emphasizes that conductors and overcurrent protection are based on the calculated load, not the equipment's maximum possible draw. NEC 220.82 Optional Calculation—Dwelling Unit. This is the article you would use to properly size the generator in a dwelling unit. This article allows a more realistic load calculation that takes into account the diversity of loads in a typical dwelling. It provides specific methods for calculating heating, cooling, cooking, and general appliance loads. Using this method often results in a significantly lower calculated load than simply adding up the nameplate ratings of all appliances. NEC 702.5 Transfer Equipment. "(A) General. Transfer equipment, including automatic transfer switches, shall be suitable for the intended use and be so designed and installed that there shall be no accidental interconnection of the normal and alternate sources of supply." This emphasizes suitability but doesn't mandate a specific amperage match. NEC 702.6 Overcurrent Protection Requires proper overcurrent protection for the generator output conductors. Your 110A breaker on the 26kW generator is likely appropriate, but double-check the generator's documentation.
Why Your 26kW Generator is Likely Acceptable1. Load Calculation is Key
You need to perform a load calculation based on NEC Article 220.82 (Optional Calculation) to determine the actual load that the generator will be supplying. This calculation will likely be far less than 200 amps. Residential load diversity is significant.2.
Generator Output
A 26kW generator, operating at 240 volts, can supply approximately 108 amps (26,000 / 240 = 108.3). Your 110A breaker is protecting the generator from overload, as it should. The #3 copper conductors are rated to carry 110 amps.
3.
ATS Function
The 200A ATS is simply a switching device. It's rated to handle up to 200 amps, but it doesn't require a 200-amp source. It just needs to be appropriately sized for the service it is connected to.
How to Respond to the Inspector1. Politely Explain Your Rationale
Don't be confrontational. Start by saying you understand his concern, but that the NEC allows for generator sizing based on calculated load, not the ATS rating.2.
Provide the Load Calculation
This is the most important step. Show the inspector your load calculation using NEC 220.82. If the calculated load is significantly less than the generator's output capacity, it will be hard for him to argue.
3.
Cite NEC Articles
Reference NEC 702.4(B), 220.10, and 220.
82. Have your code book handy to show him the exact wording.4.
Generator Specifications
Provide the generator's specifications, showing its output amperage and the recommended overcurrent protection size. This will demonstrate that you've sized the conductors and breaker appropriately for the generator's capabilities.5.
Highlight Load Management Features (If Applicable)
Many modern generators have load management features that prioritize essential circuits and shed non-essential loads during periods of high demand. If your generator has these features, explain how they contribute to ensuring that the generator doesn't become overloaded.6.
Be Prepared to Negotiate
If the inspector is still hesitant, be prepared to discuss alternative solutions, such as a smaller ATS (although this may not be cost-effective) or further refinement of the load calculation.
Example Load Calculation (Simplified)
Let's say, after performing a 220.82 load calculation, you determine the total calculated load is 80 amps. Your 26kW generator (capable of ~108 amps) is more than adequate.
Important Note
Always consult with your local Authority Having Jurisdiction (AHJ) before installation to discuss their specific requirements and interpretations of the code. This can prevent misunderstandings and delays during inspection.
In Summary:
The inspector's concern is understandable, but misguided. A properly sized generator, based on a calculated load according to NEC 220.82 and protected by appropriate overcurrent protection, is perfectly acceptable, even if it's feeding a 200A transfer switch. Focus on providing a clear and well-documented load calculation to justify your design. Good luck! Flag for review