Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Temporary Connect: Generators

User: Prototype1, Location: Kansas City

Asked on: Thursday, January 23, 2025 at 2:37 pm EST
Answered on: Thursday, March 6, 2025 at 7:43 am EST

Question: I am working on a quick disconnect generator project and creating a cost estimate. We have seven generators in storage, consisting of three 300 kW, two 400 kW, and two 500 kW units.I have obtained a list of buildings from the user, which includes over 30 buildings. My task is to determine which generator can power each building. To do this, I have researched the Main Distribution Panel (MDP) size for each building and performed calculations to determine the required generator size.For example, Building 40 has an MDP size of 208Y/120 3P 4W 1000A. Using the formula:I x E x 1.731000I calculated that the required generator size is 287.87 kW. Since we have a 300 kW generator available, I know it can handle the load.To bring the 300 kW generator to the building and connect it to the Main Distribution Panel, what line items do I need to include in my estimate? The goal is to power the critical circuits with the generator.We already have the 300 kW generator on standby, and the MDP is already installed in the building. This will be a temporary generator setup, which will be used for 3 to 4 days when the building experiences an outage. After that, the generator will be returned to storage and made available for use in other buildings.Currently, my estimate includes a manual transfer switch and a safety switch. I am also considering sizing the wire and conduit, as well as Camlock connectors. However, I lack experience in this area and am unsure what other equipment I may need.

Okay, let's break down the line items you need for your temporary generator connection estimate, focusing on providing power to critical circuits for 3-4 days, and considering the generator is already in storage and the MDP is in place. You're on the right track with the items you've identified.Here's a comprehensive list, categorized for clarity, with explanations and considerations

I. Equipment & Materials:
Manual Transfer Switch (MTS)

Absolutely essential. This allows you to safely switch the building's load between the utility power and the generator.
Sizing: This is critical. The MTS

must
be rated for the building's MDP voltage and amperage (in your example, 208Y/120 3P 4W 1000A). Don't undersize! It’s better to go slightly larger. Type: Consider an MTS specifically designed for generator connection. These often have features like generator exercising capabilities. Enclosure: NEMA 3R (weatherproof) if the MTS will be located outdoors or in a potentially damp environment. NEMA 1 (indoor) if it's definitively inside. Optional Features: Some MTS models have built-in metering to monitor generator output. Safety Switch/Disconnect Switch

Yes, needed on the generator side of the MTS for safe isolation of the generator. Sizing: Must be rated equal to or greater than the breaker size on the generator and voltage to match your system. Type: Heavy-duty disconnect switch. Enclosure: Same NEMA considerations as the MTS.

Wiring & Conduit

Crucial for safe and efficient power transfer. Wire Type: Use appropriately rated copper conductors (e.g., THHN/THWN) for the voltage, amperage, and environment. Calculate the required wire size based on the generator's output breaker amperage, the distance between the generator and MTS (voltage drop is a factor), and relevant electrical codes (NEC in the US). Err on the side of caution. Oversized wire is always better than undersized wire. Conduit Type: Rigid metal conduit (RMC) is a robust choice, especially outdoors or in areas prone to damage. Electrical metallic tubing (EMT) is acceptable indoors in dry locations. Flexible metal conduit (FMC) can be used for short runs to allow for vibration and movement. Grounding Wire: Don't forget a properly sized grounding conductor running with the power conductors. This is vital for safety. Conduit Fittings: Include couplings, connectors, straps, and supports for the conduit.

Camlock Connectors

These are a very good choice for temporary generator connections.
Amperage Rating: Ensure the Camlocks are rated for the generator's output amperage. Color Coding: Use standard color coding (Black, Red, Blue for phases, White for neutral, Green for ground) for easy and safe connections. Make sure they are properly labeled to avoid any confusion during connection. Protective Caps: Include caps for the Camlocks when not in use to prevent dirt and corrosion.

Generator Connection Cable

Type: Use a flexible, heavy-duty cable designed for generator connections. SOOW or similar is common. Length: Accurately measure the distance between the generator's desired location and the MTS location, plus extra length for flexibility and routing. Err on the longer side. Termination: Terminate the cable with Camlock connectors.

Grounding Rod and Clamp

If the generator's grounding isn't adequate (check the manufacturer's specifications), you may need to drive a grounding rod and connect it to the generator's grounding lug. This is especially important if the generator is placed on a non-conductive surface.


Fuel

Diesel, propane, or natural gas, depending on the generator type. Estimate the fuel consumption based on the generator's load and the duration of the outage (3-4 days). Consider a fuel tank if on-site fuel storage is limited.

Load Bank (Optional, but Recommended for Commissioning)

A load bank is a device that simulates an electrical load, allowing you to test the generator's performance under various conditions. It's a good way to verify that the generator is working correctly and can handle the building's load
before a real outage.

II. Labor



Site Assessment

Time to visit each building, inspect the MDP location, identify the best generator placement, and plan the cable routing. This step is crucial to avoid surprises during the actual installation.

Transfer Switch Installation

Mounting, wiring, and connecting the MTS. This is often the most time-consuming part.


Wiring and Conduit Installation

Running the conduit, pulling the wire, and making connections.

Generator Placement & Connection

Positioning the generator, connecting the Camlocks, and grounding.


Testing & Commissioning

Verifying the system is working correctly, checking voltages and phase rotation, and testing the transfer switch. This includes using the load bank if you have one.

Training (Optional)

Briefly train building staff on how to operate the transfer switch and basic generator troubleshooting.


Decommissioning & Removal

Disconnecting the generator, removing the cabling, and returning the generator to storage.

III. Permitting & Inspection



Permit Fees

Check with your local building department to determine if a permit is required for the temporary generator connection. This is very likely if you are modifying any existing electrical infrastructure.


Inspection Fees

If a permit is required, there will likely be an inspection fee.

IV. Transportation & Logistics



Generator Transportation

Cost to transport the generator from storage to the building and back. Consider the type of vehicle needed (flatbed truck, trailer).


Equipment Transportation

Cost to transport the MTS, wiring, conduit, and other materials.

Fuel Delivery

If needed, cost to deliver fuel to the generator.

V. Contingency



Contingency (5-10%)

Always include a contingency to cover unexpected costs, such as additional materials, labor overruns, or unforeseen site conditions.

VI. Safety Equipment



PPE (Personal Protective Equipment)

Hard hats, safety glasses, gloves, arc flash protection (if required), etc.


Safety Cones/Barricades

To protect the work area.

Lockout/Tagout Equipment

For safely isolating power during the installation.


Fire Extinguisher

A properly rated fire extinguisher should be readily available.

Key Considerations & Tips



Code Compliance

Ensure all work complies with the National Electrical Code (NEC) and any local electrical codes. Consult with a qualified electrician if you're unsure.


Load Calculation

While you've calculated the kW requirements, remember that the generator also needs to handle the inrush current of motors and other inductive loads. Factor this into your generator sizing and breaker selection. Consider using a soft starter or VFDs for large motors to reduce inrush current.

Automatic Transfer Switch (ATS)

While you specified a manual transfer switch, consider the benefits of an ATS for critical applications. An ATS will automatically switch the load to the generator when utility power fails, and back to utility power when it is restored.


Noise

Consider the noise level of the generator and its impact on the surrounding environment. Use noise barriers or place the generator in a location where it will not disturb neighbors.

Exhaust

Ensure the generator's exhaust is properly vented away from buildings and people. Carbon monoxide poisoning is a serious risk.


Weather Protection

Protect the generator from the elements, especially rain and snow. Use a generator enclosure or canopy if necessary.

Fuel Management

Implement a system for tracking fuel consumption and ensuring an adequate supply.


Security:
Secure the generator to prevent theft or vandalism.By thoroughly addressing these line items and considerations, you'll create a more accurate and reliable cost estimate for your temporary generator connection project. Remember to get multiple quotes for equipment and labor to ensure you're getting the best value. Always prioritize safety and compliance with electrical codes. Flag for review

Previous Question Next Question