Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: The use of residential optional load calculations

User: bluesprinter, Location: kensington maryland. us

Asked on: Thursday, January 23, 2025 at 4:34 pm EST
Answered on: Thursday, March 6, 2025 at 7:44 am EST

Question: When is it acceptable to use the residential optional load calculation from the nec. 220.82I'm adding a evse (vehicle charger) to a existing 200 amp service with the existing typical loads including a heat pump hvac system.The county permit reviewer for the county is requesting documentation of the load calculation.when I perform the calculation using the optional methods it comes out to 155 amps on a service rated at 200 ampsI submitted a calculation using 40% derating the furnace of @. 15000kw and he responded backHeating needs to be at 100%, If heat is supplemented then you need to add 65% of the supplemental heating load unless both don’t work at the same time.what would be your thoughts and responses that he's not recognizing the option calculationWhen I took ibew code class As a student We were told that you use the standard for new properties and the optional for additional loads to existing buildings and homesbut we still must apply 80% of the main overcurrent device rating.should the load of a evse or other be added after the allowed adjustments in either method of calculation ?We have i've seen adjustments for led lighting loads vs the 3va per sq footThanks

Okay, let's break down this situation with the NEC's optional load calculation in 220.82 and how it applies to your EVSE addition.

Understanding NEC 220.82 (Optional Calculation - Dwelling Unit)

NEC 220.82 allows for a simplified calculation of the service load for a dwelling unit. It's often used (and perfectly acceptable) for existing dwellings when adding significant loads, especially when the existing service might be close to its capacity using the standard method.

Key Aspects of 220.82



Applicability

The wording of 220.82 doesn't explicitly limit its use to
only additions to existing dwellings. It says "dwelling unit." So, it's applicable to any dwelling unit. While you are correct about using the Standard method for new properties, the optional method is still a viable code compliant solution.

Conditions for Use

While it's allowed for dwellings, it becomes more appealing when adding a significant load to an existing service that might be close to its rating.

Not always lower
Sometimes the optional calculation results in a lower service load than the standard calculation, but not always.

Your Situation and the Inspector's Concerns

The core of your issue seems to be the inspector's interpretation of the heating load calculation under 220.82(C)(5).Here's what 220.82(C)(5) actually says (paraphrased):
Electric Space Heating

Calculate the larger of: 100% of the nameplate rating of the electric space-heating loads. 65% of the nameplate rating of the air-conditioning and heat pump compressor equipment.

Non-Coincident Loads

If the heating system and air-conditioning system will not operate simultaneously, you can omit the smaller of the two loads calculated above.


Supplemental Heating

You need to account for supplemental heating as the inspector described.

Analysis of Your Situation and Possible Responses


Heat Pump vs. Resistance Heat

You mentioned a "heat pump HVAC system." A heat pump is an electric space-heating load. However, it's crucial to understand the following:

Heat Pump Only

If your HVAC system is
only a heat pump and doesn't have electric resistance supplemental heat, then you should use the 65% rule on the heat pump's compressor rating as per 220.82(C)(5). The heating load is the heat pump's compressor, not the resistance heat strips (if any). This is a common misunderstanding.

Heat Pump with Supplemental Resistance Heat

If your heat pump does have supplemental electric resistance heat, then you need to calculate both the 65% of the compressor and the 100% of the resistance heat. If they're not designed to operate simultaneously (which they often are), you can omit the smaller of the two values.2.

Documentation and Clarity



Provide Detailed HVAC Information

Give the inspector the
exact nameplate information from the heat pump unit(s), including both the compressor's RLA (Rated Load Amperes) and the kW rating of any supplemental electric resistance heat.

Explain Your Calculation Clearly

Lay out your calculation step-by-step, referencing the specific subsections of NEC 220.82 you are using.

Highlight the "Not Simultaneously" Clause

If the supplemental heat is
only for auxiliary heating, you can omit the smaller load.3.

Possible Response to the Inspector

"The load calculation was performed using the optional calculation method outlined in NEC 220.82. The HVAC system is a heat pump with a compressor RLA of [RLA amps] and [kW] of supplemental electric resistance heat.
Heat pump compressor load = [RLA amps] 240V 0.65 = [amps] Supplemental electric resistance heat load = [kW] 1000 / 240V = [amps]Because the supplemental electric resistance heat is intended for auxiliary heating and does not operate simultaneously with the heat pump compressor in normal heating mode, I am omitting the smaller of the two loads per NEC 220.82(C)(5). [If this is not true, you cannot omit the smaller load.]Therefore, the heating load used in the optional calculation is [larger of the two values].The total calculated load using NEC 220.82 is [total amps], which is below 80% of the 200-amp service rating."4.

EVSE Load Calculation (After 220.82 Adjustments)



EVSE Continuous Load

EVSE loads are considered continuous loads. You
must multiply the EVSE's output amperage by 125% (or divide by 0.8) to get the load you add to the service calculation.

Where to Add It

You add the adjusted (125%) EVSE load after you've completed the adjustments and reductions allowed by either the standard or optional calculation methods.5.

LED Lighting Adjustment



LED Lighting is Key

You can account for LED lighting by using the actual wattage of the fixtures (or a reasonable estimate) instead of the NEC's 3 VA/sq ft general lighting load. This is essentially using more accurate information to replace a broad general assumption, and is generally acceptable and a common practice that saves panel space.6.

The 80% Rule (Service Size)



Understanding 215.2(A)(1)
- The 80% rule is a general guideline, particularly when dealing with branch circuits and feeders. It is not a strict rule for determining if an existing service is adequate based on the NEC 220 load calculations.

In Summary

You're correct that 220.82 is a valid option. The key is to understand the nuances of the heating load calculation, particularly when dealing with heat pumps and supplemental heat. Provide detailed documentation and a clear explanation of your calculations. Add the 125% of the EVSE load after completing the optional calculation adjustments. Don't be afraid to politely and professionally challenge the inspector's interpretation if you believe it's incorrect, with clear code references and detailed information.

Important Notes:
This advice is based on the NEC as of the last update to my knowledge. Always refer to the current edition adopted by your jurisdiction. This is general guidance. A qualified electrical engineer or inspector can provide specific advice based on your particular installation.* Always strive for clear communication and documentation with the inspector. Flag for review

Previous Question Next Question