Question: I've recently started to get involved with some transmission scale renewable energy projects and it seems like the design around the 34.5kv system is limited based on what is commercially available for circuit breaker ratings and potentially disconnects.IEEE C37.04-2018 Table 12 "Preferred Ratings for class S2 (outdoor) circuit breakers" shows the highest rating for a 38kv class breaker as 3000A. The highest rating that I can find for this type of breaker is by Siemens via their SDV7 breaker which appears to have a high limit rating of 2500A at 40kA.IEEE C37.04-2018 Table 8 "Preferred Ratings for class S1 (indoor) circuit breakers shows the highest rating for a 38kv class breaker as 4000A. The highest rating that I can find for this type of breaker is by Eaton which is a 3000A force air cooled breaker, otherwise it's 2500A as well.Does anyone know of any other vendors that offer any higher ratings?The reason why I've been digging into these ratings in the first place is I'm trying to figure out what a realistic limit on transformer sizes should be with a 34.5kv secondary but this all rides on my next question: Is there a limit on how many circuit breakers can be on a 34.5kv bus if there is no low side breaker on a main power transformer? Some folks that I've asked at work keep referencing a 6 breaker rule if there is no main breaker on the 34.5kv bus on the low side of the transformer but I don't believe that rule applies since a generating facility would not apply under Article 230 as a Service. The breaker on the high side of the transformer would be limited to 300% per 450.3(A) so I think we are covered from that regard as I would consider the collector substation to be a supervised location.One thing that could be an issue is that the highest fault current rating that seems to be available at 34.5kv level equipment is 40kA so if the system strength is high at the transmission side from being near generation sources, that might end up being the limiting factor for the transformer size and 34.5kv system size.So if the fault current is not an issue then we could use a 4000A+ switch on the secondary of the transformer, (Southern States WAG-A Switch) and then have physical bus on the with 1200A breakers serving the collector circuits this seems like it would be the ideal setup for a collector substation.I'm interested to see if anyone has a comments on this arrangement or sees any fatal flaws. Thanks all!
Okay, this is a great breakdown of the challenges in designing 34.5kV collector substations for renewable energy projects. You've correctly identified several key constraints and are thinking about the right issues. Let's address your questions and points in detail
1. Circuit Breaker Availability:
Your Research is Accurate
You're right. Commercially available, readily-off-the-shelf circuit breakers in the 38kV class (applicable to 34.5kV systems) generally top out around 2500-3000A continuous current rating. The Eaton forced-air-cooled option is a good find, though its cost and complexity (forced air) make it less desirable in many applications.
Beyond the Standard
While 4000A breakers do exist, you'll likely find they are not common, require significantly longer lead times, and will involve custom or specialized orders. You'll need to contact the manufacturers directly to inquire about availability and lead times. Siemens, Eaton, ABB, and GE are the main players. Be specific about your application (renewable generation collector substation) when inquiring, as this may influence their recommendations.
Consider Paralleling
While less desirable than a single larger breaker, paralleling breakers could be considered in extreme cases. This introduces significant complexity in terms of coordination, protection, and maintenance. It's typically avoided unless absolutely necessary.
Alternative Protection
While you are focused on circuit breaker ratings, consider other protective devices like fuses. A properly coordinated fuse could provide backup or even primary protection in certain scenarios, potentially allowing for a smaller breaker. However, fuses have their own limitations (e.g., single-phasing concerns, replacement requirements).
2. The "6 Breaker Rule" Myth (or Misunderstanding)
You're Correct - Article 230 Doesn't Apply
The 6-breaker rule originates from the NEC, specifically related to service entrances. It's designed to limit the number of service disconnects at a residential or commercial building service. A generating facility is NOT a service under Article 230. The NEC doesn't apply to transmission and generation facilities in the same way.
The Real Rule
The "rule" at utility scale is that there is no rule dictating how many breakers you can have. The proper coordination and fault duty analysis is the only thing dictating the number of devices you can have.
3. Transformer Sizing and Fault Current
Fault Current is a Critical Constraint
This is the most crucial point you raise. The 40kA fault current rating of available 34.5kV equipment is almost certainly going to be a limiting factor. High system strength at the point of interconnection (POI) means the utility grid can contribute a lot of fault current.
Performing a Comprehensive Fault Study is Essential
You must perform a detailed fault study, including contributions from the utility grid, your generation sources, and any local loads. This study needs to be done at both minimum and maximum generation output scenarios to capture the full range of fault currents. Don't rely on "rules of thumb." Use professional power system modeling software (e.g., ETAP, SKM PowerTools, EasyPower).
Fault Current Mitigation
If your fault current exceeds 40kA, you have several options, all of which add cost and complexity:
Fault Current Limiters (FCLs)
These are specialized devices designed to limit fault current. They are expensive and can impact system impedance during normal operation, so careful planning is needed.
Reactors
Adding reactors in series with the transformer secondary (or even the feeder circuits) will increase impedance and reduce fault current. Again, this affects voltage regulation and requires careful analysis.
Split Bus
Divide the 34.5kV bus into multiple sections, each fed by a smaller transformer. This reduces fault current on each section, but increases the overall equipment count and complexity.
Transformer Impedance
Specify higher impedance transformers. This reduces fault current but also increases voltage drop under load. A delicate balance is needed.
Upgrading Equipment
The most expensive solution - find equipment that is rated higher than 40kA, which can be very difficult in the 34.5kV class.
Transformer Size
Your maximum transformer size is directly tied to the allowable fault current. You need to calculate the fault current contribution from the transformer itself during a secondary-side fault.
4. Southern States WAG-A Switch
Good Option
A 4000A+ switch with fault-closing capabilities (like the WAG-A) is a good idea for a collector substation. It provides a means of isolating and re-energizing the bus without having to rely solely on circuit breakers. It's also helpful for maintenance.
Coordination
You need to carefully coordinate the switch's fault-closing rating with the interrupting rating of the downstream breakers. The switch can only close into a fault that the breakers can clear.
5. Collector Substation Arrangement
General Concept is Sound
Your general idea of a large switch on the transformer secondary feeding a bus with multiple 1200A breakers is a typical and reasonable approach.
Consider Redundancy
Depending on the critical nature of the generation, consider some level of redundancy. For example, could you have a second transformer and bus section to maintain some level of output if one transformer fails?
Protection and Control
This is where careful engineering is essential. You need to design a robust protection and control system that includes:
Transformer Protection
Differential protection (87T), overcurrent (50/51), overvoltage (59), undervoltage (27), etc.
Bus Protection
Bus differential protection (87B) is highly recommended for a substation of this size.
Feeder Protection
Overcurrent (50/51), ground fault (50G/51G), directional overcurrent (67) are typical for the outgoing feeder circuits.
Coordination
All protective devices must be properly coordinated to ensure selective tripping. The closest device to the fault should trip first, minimizing disruption to the rest of the system.
Arc Flash
Performing an arc flash hazard analysis is mandatory. The incident energy levels at 34.5kV can be extremely high. You'll need to implement measures to mitigate the risk (e.g., remote racking of breakers, arc flash relays).
Fatal Flaws and Considerations
Oversimplification
Assuming you can just put in a 4000A+ switch and 1200A breakers without detailed fault current and coordination studies.
Ignoring Fault Current Contribution from Wind/Solar
You must include the fault current contribution from the inverters in your wind or solar farm.
Voltage Drop
With long feeder cables to the wind turbines or solar inverters, voltage drop can be a significant issue. Carefully analyze voltage drop under various loading conditions.
Harmonics
Renewable energy inverters can inject harmonics into the system. Consider harmonic filtering if necessary.
Grounding
Proper grounding of the 34.5kV system is essential for safety and protection. Consider the grounding method (e.g., solid, resistance, reactance).
Utility Interconnection Requirements
The utility you are interconnecting with will have very specific requirements for protection, control, metering, and communications. You must adhere to their standards.
Cost
The cost of equipment, engineering, and construction for a 34.5kV collector substation can be substantial. Careful cost estimation is crucial.
In Summary
You're on the right track. The key takeaways are:1.
Fault Current
This will likely be your biggest constraint. Perform a thorough fault study.2.
Coordination
Careful coordination of all protective devices is essential.3.
Utility Interconnection
Understand and meet the utility's requirements.4.
Detailed Engineering
Don't cut corners on engineering. A well-designed and properly protected collector substation is critical for the reliable and safe operation of your renewable energy project.5.
Consider Consulting: If you lack experience in transmission-scale substation design, strongly consider engaging a qualified consulting engineer with expertise in this area. It can save you significant time, money, and potential headaches in the long run.Good luck with your project! Flag for review