Question: I'm kind of confused on the terminology of what is a grounding electrode conductor is and where it becomes an EGC, bonding jumper or if its all a GEC.For example, If I go from my ground rod and run up a column setting a ground terminal bus bar on each floor, then go from my GTB to ground a pipe on the roof, would every conductor connecting each of these points be referred to as a grounding electrode conductor. Or does the wire become a bonding jumper or EGC when I go from the GTB to the pipe?In my head, the grounding electrode conductor is the connections between building steel and the ground rod and all my connections for equipment, pipes, floor pedestals, ETC tied back into the GTB would be bonding jumpers or EGCs. Any help clarifying this would be greatly appreciated.

You're right to be confused! The terminology can be tricky, but let's break it down with your example

Definitions and Clarifications (Based on NEC - National Electrical Code, which is the standard in the US):
Grounding Electrode (GE)

The actual object that makes contact with the earth. In your example, the ground rod. Could also be a building steel foundation, a buried plate, etc.


Grounding Electrode Conductor (GEC)

The conductor that connects the system grounded conductor (neutral in most cases) OR the equipment grounding system to the grounding electrode.

The key is it connects to the EARTH.
This is crucial. Equipment Grounding Conductor (EGC)

A conductor that connects the non-current-carrying metal parts of equipment (enclosures, appliances, etc.) back to the service equipment (typically the main panel) where the neutral and ground are bonded. Its purpose is to provide a low-impedance path for fault current to return to the source, allowing the overcurrent protective device (circuit breaker or fuse) to trip and clear the fault quickly.


Bonding Jumper

A reliable conductor to ensure the required electrical conductivity between metal parts required to be electrically connected. Bonding jumpers are used to bond: Metal enclosures around conductors (like conduit). Metal water piping systems. Other metal parts that could become energized. Sections of grounding electrode conductors (to ensure continuity).

Applying the Definitions to Your Example


Ground Rod to Column/GTB on First Floor

This conductor is your

Grounding Electrode Conductor (GEC)
. It's connecting the grounding electrode (ground rod) to your equipment grounding system (represented by the GTB).2. GTB on First Floor to GTB on Upper Floors

This conductor is also a

Grounding Electrode Conductor (GEC)
. Think of it as an extension of the original GEC, effectively creating a distributed grounding system throughout the building. While it's tempting to call it a bonding jumper, its primary purpose is to extend the grounding electrode system upward, making it a GEC.3. GTB on any Floor to Pipe on Roof

This conductor is a

Bonding Jumper
. It connects the GTB (which is part of the equipment grounding system) to a metallic object (the pipe) to ensure it is at the same electrical potential as the rest of the grounding system. This prevents voltage differences that could create a shock hazard or cause corrosion.4. GTB on any Floor to Equipment/Pedestals/Enclosures

These conductors are

Equipment Grounding Conductors (EGCs)
. They provide a path for fault current from the equipment back to the grounding system, allowing for safe operation and tripping of circuit breakers in the event of a fault.

Here's a summarized table

| Connection | Type of Conductor | Purpose

----------------------------------------- | ------------------------------ | ----------------------------------------------------------------------------------------------------------------------------
Ground Rod to First Floor GTB | Grounding Electrode Conductor (GEC) | Connects the grounding electrode (earth) to the building's grounding system.
GTB (Floor 1) to GTB (Floor 2, etc.) | Grounding Electrode Conductor (GEC) | Extends the grounding electrode system throughout the building. Ensures a low impedance path to ground on each floor.
GTB to Metal Pipe on Roof | Bonding Jumper | Bonds the metal pipe to the grounding system to eliminate potential differences. || GTB to Equipment/Pedestals/Enclosures | Equipment Grounding Conductor (EGC) | Provides a low-impedance path for fault current to return to the source, facilitating quick tripping of overcurrent devices. |


Key Takeaways



Think about the
purpose of the conductor.
Is it connecting to the earth (directly or indirectly)? Then it's likely a GEC. Is it connecting metal parts to the grounding system to equalize potential? Then it's a Bonding Jumper. Is it providing a fault current path from equipment back to the source? Then it's an EGC. The GTB acts as a central point. All EGCs from equipment and bonding jumpers connect to the GTB, which is then connected to the grounding electrode system via the GEC. Local Codes

Always consult your local electrical codes. Some jurisdictions may have specific requirements or interpretations that differ slightly from the NEC.


Consult a Qualified Electrician:
If you're working on a complex electrical system, always consult with a licensed and qualified electrician. They can ensure that the grounding and bonding system is properly installed and meets all applicable codes.Understanding these definitions and applying them to your specific situation will help you correctly identify and use the appropriate grounding and bonding conductors, ensuring a safe and effective electrical system. Good luck! Flag for review