User: Dark Sparky, Location: USA
Asked on: Tuesday, January 28, 2025 at 1:24 am EST
Answered on: Thursday, March 6, 2025 at 7:53 am EST
Question: In an old manufacturing plant we are repurposing the 1000A feed (circuit) out of old 480V switchgear. We need to take the 1000 amp feed from the switchgear and use it for distribution from electrical panels.1000 amp panels have a prohibitively long lead time - so instead we will use two 600 amp panels. What is then best arrangement to bring the 1000 amp feed to the panels and then split the load between the two panels?For instance, a 600 amp panel with 1000 amp feed-through lugs to fed the second 600 A panel, both with main 600A breakers? A wiring trough using the tap rule and splitting the 1000A feed between the two panels, each with main breakers? The main goal is to bring the full 1000 amp capacity to the panels, and split this capacity between the two panels.Thanks in advance.
Okay, let's break down the best options for splitting your 1000A feed into two 600A panels, considering code compliance, practical considerations, and your goal of maximizing available capacity.
Understanding the Key Considerations
NEC (National Electrical Code)
This is the primary guiding document for electrical installations. You MUST adhere to NEC requirements.
Overcurrent Protection
Each conductor must be protected against overcurrent. This means breakers or fuses sized appropriately for the conductor's ampacity.
Load Calculations
You need to know the actual expected load on these panels. Oversizing everything is costly and doesn't necessarily improve safety if it leads to inadequate overload detection.
Ampacity of Conductors
The wire you use must be rated to carry the current it will be subjected to.
Accessibility and Serviceability
The solution should be easy to maintain and troubleshoot.
Options and Analysis
Here's a detailed look at the options you mentioned and some alternatives, along with pros/cons and code considerations:
1. 600A Panel with 1000A Feed-Through Lugs (with 600A Main Breakers)
Description
You bring the 1000A feeder into the first 600A panel. The panel has large lugs specifically rated to pass through 1000A. From these lugs, you run conductors to the second 600A panel. Each panel has a 600A main breaker.
Pros
Simple wiring. Potentially less expensive than other options.
Cons
Limited Capacity in First Panel
The first panel's 600A main breaker is the bottleneck. Even though the lugs are rated for 1000A, you can only draw a maximum of 600A out of that panel before the breaker trips. The 400 amps are available for the second panel.
Feed Through Lugs
The 1000A feed through lugs must be rated for two sets of conductors, one set of 1000A conductors in, and one set of 600A conductors out to the second panel.
Code Compliance Concerns
While technically compliant if executed correctly (proper wire sizing, overcurrent protection), it's not ideal because it doesn't fully utilize the available 1000A.
NEC Considerations
110.3(B) - Installation and Use
Equipment must be installed according to its listing and labeling. Make sure the feed-through lugs are specifically listed for 1000A pass-through and the intended conductor sizes.
240.4 - Protection of Conductors
The 600A breaker protects the 600A-rated conductors leaving the first panel to the second panel. The 1000A cable is protected in the main switchgear.
Verdict
Not the best option due to the limited capacity in the first panel.
2. Wiring Trough/Junction Box with Tap Rule (with 600A Main Breakers)
Description
You bring the 1000A feeder into a large wiring trough (or appropriately sized junction box). You then use the NEC tap rules to tap off conductors to each of the 600A panels. Each panel has a 600A main breaker.
Pros
Can potentially utilize more of the 1000A capacity.
Cons
Tap Rule Complexity
The tap rules in NEC are very specific and require careful calculation and execution. You must meet all the conditions of the chosen tap rule.
Space Requirements
The wiring trough/junction box must be large enough to accommodate the conductors, bending radii, and terminations.
Potential for Confusion/Error
More complex wiring increases the chance of errors.
Labor Intensive
Terminating multiple conductors within the trough can be time-consuming.
NEC Considerations
240.21 - Location in Circuit
This is where the tap rules reside. You'll need to carefully review this section. Commonly used tap rules are 240.21(B)(1) (10-foot tap rule) and 240.21(B)(2) (25-foot tap rule).
314 - Junction Boxes, Pull Boxes, and Conduit Bodies
This article governs the sizing and installation of the junction box. It must be appropriately sized and accessible.
110.14 - Electrical Connections
All connections must be torqued to the manufacturer's specifications.
Verdict
Feasible if you can meet all the requirements of a tap rule. Be prepared for a detailed calculation and potentially a more complex installation.
3. (Recommended) Distribution Block/Power Distribution Block (PDB) with 600A Main Breakers
Description
This is the best option. You bring the 1000A feeder into a Listed and Labeled Distribution Block or Power Distribution Block. From the PDB, you run conductors to each of the 600A panels. Each panel has a 600A main breaker.
Pros
Simplest and Safest
Provides a clean, organized, and code-compliant way to split the feeder.
Listed and Labeled
The PDB is specifically designed and tested for this application, ensuring safety and reliability.
Easy to Install
Typically, PDBs have clear instructions and require less complex wiring than the tap rule method.
Flexibility
Allows for future modifications if needed.
Maintains Capacity
The full 1000A is available to the combined load of the two panels, up to the limit of each panel's 600A breaker.
Cons
Cost
PDBs have an upfront cost.
Space
Requires space to mount the PDB, though they are typically relatively compact.
NEC Considerations
110.3(B) - Installation and Use
Install the PDB according to its listing and labeling.
110.14 - Electrical Connections
Torque connections to the PDB's specifications.
408 - Switchboards and Panelboards
While not technically a panelboard, the PDB functions as a distribution point and should be installed in a manner consistent with good practices for switchboards/panelboards.
Verdict
This is the recommended option. It's the safest, most reliable, and easiest to install, and it provides the best utilization of your 1000A capacity.
Example using Option 3
Select a PDB
Choose a PDB rated for at least 1000A input and with sufficient output lugs to feed two 600A panels. Make sure the PDB's lugs can accommodate the conductor sizes you plan to use.2.
Mount the PDB
Install the PDB in a suitable enclosure or on a backboard near the two panels. Ensure adequate working space.3.
Run the 1000A Feeder
Run your 1000A-rated conductors from the switchgear to the PDB input lugs. Terminate them per the PDB manufacturer's instructions, including proper torque.4.
Run Conductors to Panels
Run appropriately sized conductors (at least 600A ampacity) from the PDB output lugs to each of the 600A panels.5.
Terminate Conductors
Terminate the conductors at the PDB and the panel main breakers, again following torque specifications.6.
Labeling
Clearly label all conductors and the PDB.
Important Considerations Before Proceeding
Load Calculation
Perform a thorough load calculation for each panel to ensure that the 600A main breakers are appropriately sized. You don't want nuisance tripping.
Conductor Sizing
Consult the NEC Article 310 for conductor ampacity. Consider derating factors for ambient temperature and the number of conductors in a raceway. It's generally a good idea to use larger conductors than the minimum required for better voltage drop performance.
Overcurrent Protection
Verify that the overcurrent protection in the switchgear feeding the 1000A feeder is sized appropriately for the conductors and downstream equipment.
Grounding
Ensure proper grounding of all equipment, including the PDB and panels, according to NEC Article 250.
Permitting and Inspection
Contact your local electrical inspector to determine permit requirements and schedule an inspection.
Qualified Electrician
This work must be performed by a qualified and licensed electrician.
*In summary, using a Power Distribution Block is the most practical and code-compliant solution for splitting your 1000A feed into two 600A panels. It provides the best balance of safety, ease of installation, and utilization of your available capacity. Flag for review