Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: ungrounded delta primary ?

User: Fred B, Location: Upstate, NY

Asked on: Tuesday, January 28, 2025 at 12:12 pm EST
Answered on: Thursday, March 6, 2025 at 7:54 am EST

Question: I know some of you deal more with the higher voltage systems so thought I'd ask here as my experience has been limited to up to 480 and under 600A.We seem to have a lot of ungrounded primary in our more rural areas around here. What safety systems are at work for the primaries when you get a short to ground on the system like a tree or say a car accident that breaks off the pole? A lot of the one line, no neutral, lines feeding down for several miles sometimes to one or more transformer(s) that then derives it own neutral for a 120/240. Will the fuse break blow with such a high resistance ground potential?Any additional considerations or caution needed with this type of system vs a wye system such as potentially being "worse" with only a high resistance earth only grounding, that might be different when dealing with the 120/240?

You're asking some great questions about ungrounded (also called "isolated" or "delta" primary) distribution systems. They do present different challenges and safety considerations compared to grounded (wye) systems. Here's a breakdown of the safety mechanisms, considerations, and differences

Safety Mechanisms for Ungrounded Primary Systems
Fuse Cutouts

Yes, fuse cutouts are still the primary overcurrent protection. However, their effectiveness during a ground fault depends heavily on the
ground fault current. This is where things get tricky.

High Resistance Ground Fault

On an ungrounded system, when a fault occurs (e.g., a tree limb touches a phase conductor), a fault current path is established through the capacitance to ground of the other two phases, through the fault itself, and back to the system. This capacitance is inherent in the cables, insulators, and other equipment. The fault current, often called "capacitive charging current," is

limited
by this capacitance. This current can be relatively low even at high voltages. Will the Fuse Blow? This is the critical question. If the fault current is less than the minimum melting current of the fuse, the fuse will not blow. This can create a dangerous situation where a line is energized with respect to ground, but not enough current is flowing to trip the protection. Capacitance to Ground

As mentioned above, capacitance to ground from each phase is a critical factor. The longer the lines and the more equipment on the line, the higher the capacitance. This capacitance acts as a path for fault current to flow back to the source.

Ground Detectors

To address the problem of low fault current, many utilities use ground detectors on ungrounded systems. These devices continuously monitor the voltage between each phase and ground.


How they work

In a balanced, unfaulted ungrounded system, the voltage from each phase to ground will be approximately equal. When a ground fault occurs, the voltage of the faulted phase drops significantly towards zero, while the voltage of the other two phases increases to line-to-line voltage. The ground detector senses these voltage imbalances.

Alarm or Trip?
Ground detectors can be set up to simply alarm (alerting the utility to investigate) or to trip a breaker, taking the entire line out of service. Often, they are initially set to alarm, giving crews time to locate and isolate the fault before a complete outage. Surge Arresters

These protect equipment from voltage surges caused by lightning or switching. They are typically connected between each phase and ground.

Additional Considerations and Cautions
"Creeping Faults"

An ungrounded system can tolerate a
single ground fault without an immediate outage. This is sometimes touted as an advantage – service continues. However, it's a

dangerous myth
. The second ground fault, on a different phase, creates a phase-to-phase fault, which will cause a very high fault current and will blow fuses or trip breakers. The danger is that the first fault might be a slow, developing problem (e.g., a tree branch gradually wearing away insulation). This "creeping fault" can exist for days or weeks, putting stress on the system and increasing the risk of a second, catastrophic fault. Transient Overvoltages

During ground faults, even with low fault currents, significant transient overvoltages can occur on the unfaulted phases. This is due to the shift in neutral potential. Surge arresters play a crucial role in mitigating these overvoltages.


Locating Ground Faults

Finding the location of a ground fault on an ungrounded system can be challenging. The low fault current makes it difficult to trace the fault using conventional methods. Utilities often use specialized equipment that injects a signal onto the line and then traces the signal to the fault location.

Induced Voltage

When a ground fault is present the line to neutral voltage can shift. So on the un-faulted lines they will see the Phase to Phase voltage. This can create a dangerous situation if the line is accidentally contacted as it may not be recognized as a high voltage fault.


Safety Procedures



Treat all lines as energized.
This is always good practice, but especially critical on ungrounded systems where a fault might exist without immediately causing an outage. When working on or near lines, use appropriate grounding techniques. Grounding helps to ensure that any potential difference between the line and ground is minimized, reducing the risk of electric shock. Be aware of the potential for transient overvoltages during switching operations or when a ground fault occurs. Transformer Neutral Grounding

You mentioned transformers deriving their own neutral for 120/240V service. This is standard practice. The important point is that this neutral is grounded at the transformer. This provides a low-impedance path for ground fault current on the secondary side, ensuring that overcurrent protection devices (breakers or fuses) will trip quickly in the event of a ground fault.

Ungrounded vs. Wye (Grounded) Systems: A Comparison
| Feature | Ungrounded (Delta) | Grounded (Wye)

---------------- | ---------------------------------- | -------------------------------------------------
Ground Fault Current | Typically low, limited by capacitance | Can be high, depending on grounding impedance
Outage | Can tolerate a single fault without outage | Single fault typically causes immediate outage
Ground Detection | Required to detect faults | Easier to detect faults due to higher fault current
Overvoltage | Can experience transient overvoltages | Generally lower overvoltages
Complexity | More complex fault location | Simpler fault location || Safety | Requires careful monitoring | Generally considered safer for initial faults |Is Ungrounded "Worse"?

It's not inherently "worse," but it presents different challenges. The tolerance of a single fault can be seen as an advantage in maintaining service. However, the risk of a second fault and the potential for undetected faults make it crucial to have robust ground detection and maintenance programs. In addition, because the fault currents on the primary are lower it can be easier for the fault to migrate to the secondary or even to the local ground, meaning that if your equipment is grounded to the same ground as the secondary grounding, that you can see voltage on your equipment.

In Summary

Ungrounded primary distribution systems rely on a combination of fuse cutouts, ground detectors, and surge arresters to protect against faults. They require careful monitoring and maintenance to prevent undetected faults and to mitigate the risks associated with transient overvoltages. While they can offer some advantages in terms of service continuity, the potential for undetected faults and the complexity of fault location make them a less forgiving system than grounded wye systems. A clear understanding of their behavior and safety procedures is essential for anyone working on or near these systems. Flag for review

Previous Question Next Question