User: ElectricalMaintenance, Location: Ontario, Canada
Asked on: Tuesday, January 28, 2025 at 5:22 pm EST
Answered on: Thursday, March 6, 2025 at 7:56 am EST
Question: Hello. I am wondering if there are any cable types, other than SOOW/cabtyre, that are allowed as power drops for connecting portable equipment in factories? I can't find it in the code book.Thanks for your help!
You're right, the NEC doesn't explicitly list every permissible cable type for power drops to portable equipment in factories. Instead, it focuses on the performance characteristics the cable must have and then provides examples of suitable cable types. You won't find a section that says "ONLY SOOW and cabtyre!"Here's the breakdown of what to consider and where to look in the NEC (National Electrical Code)
Key Considerations:
Flexibility
The cable needs to be flexible enough to handle repeated bending and movement.
Durability
It must be resistant to the specific environmental conditions of the factory, including abrasion, chemicals, oil, moisture, and physical damage.
Voltage Rating
The cable's voltage rating must be appropriate for the system voltage.
Ampacity
The cable must be sized to carry the load without overheating.
Grounding
An equipment grounding conductor must be present.
Suitability
The cable must be "identified for the use." This is the critical point!
Listed
The cable should be listed by a recognized testing laboratory (UL, ETL, CSA, etc.). This helps ensure it meets the required standards.
Relevant NEC Articles and Sections (2023 NEC, but similar concepts exist in older editions)
Article 400 - Flexible Cords and Cables
This is the primary article covering flexible cables.
400.1 - Scope
Defines what Article 400 covers (flexible cords and cables).
400.4 - Uses Permitted
This is KEY! It describes where flexible cords and cables can be used. Pay close attention to this. Generally, it allows for connection of portable equipment.
400.7 - Uses Not Permitted
Equally important! This describes where they cannot be used (e.g., as a substitute for fixed wiring, where run through holes in walls, ceilings or floors).
400.10 - Ampacity of Flexible Cords and Cables
Covers the ampacity requirements. You must size the cable correctly.
400.12 - Overcurrent Protection
Ensure the overcurrent protection is proper for the cord's ampacity.
Table 400.4
This table lists many types of flexible cords and cables and their permitted uses. This is where you will find SOOW and other options. This is a good starting point.
Article 500-506 - Hazardous (Classified) Locations
If the factory has hazardous (classified) locations (e.g., areas with flammable gases or dust), you must use cables and wiring methods specifically approved for those locations. SOOW may or may not be suitable, depending on the classification.
300.11 - Securing and Supporting
Flexible cables still need to be supported correctly.
310 - Conductors for General Wiring
While this article mostly covers building wiring, it's important for understanding conductor ampacity and insulation types.
Acceptable Cable Types (Besides SOOW/Cabtyre)
Table 400.4 is your friend. You need to look at the types of cables listed and see which meet the environmental and mechanical needs of your factory. Here are some possibilities, but carefully evaluate their suitability:
SJOOW
Similar to SOOW but with a lower voltage rating (typically 300V vs. 600V). Suitable for lighter-duty applications.
STOOW
Similar to SOOW but with a thermoplastic elastomer (TPE) jacket. Can offer good oil and chemical resistance.
SEOOW
Similar to SOOW, but with a thermoplastic elastomer (TPE) insulation as well as a TPE jacket.
Type W Portable Power Cable
Heavier duty, often used for welding machines and similar high-current applications.
Other Types in Table 400.4
Carefully review the descriptions in Table 400.4 to see if any other types are suitable for your application.
Important Steps
Identify the Environment
Carefully assess the factory environment. What chemicals are present? Is there oil? What about abrasion potential? What's the temperature range? Is it wet or dry? Is it a hazardous location?2.
Determine the Load
Calculate the ampacity required for the equipment being powered.3.
Consult Table 400.4
Review the cable types in Table 400.4 and consider which ones might be appropriate based on the environment and ampacity.
4.
Check the Cable's Listing
Ensure the cable is listed by a recognized testing laboratory (UL, ETL, CSA). This will be marked on the cable itself.5.
Verify Suitability with the AHJ
When in doubt, consult with your local Authority Having Jurisdiction (AHJ) (electrical inspector). They have the final say on what's acceptable in your area.6.
Read the Cable's Specifications
Get the manufacturer's specifications for the cable you're considering. This will provide detailed information about its voltage rating, temperature rating, oil resistance, chemical resistance, and other important characteristics.
Example Scenario
Let's say you need a power drop for a portable grinder in a relatively clean, dry factory environment with minimal oil exposure. SJOOW might be an acceptable option because it has good flexibility and is less expensive than SOOW. However, if there's significant oil exposure, you'd want to opt for something more robust, like SOOW or STOOW.
In summary: The NEC doesn't restrict you to only SOOW. It focuses on the performance requirements. You can use any cable type that is listed, suitable for the application, and complies with all applicable NEC requirements. Thoroughly evaluate the environment, load, and cable specifications, and consult with the AHJ when in doubt. Table 400.4 of the NEC is your primary resource. Flag for review