User: brother, Location: "I have learned, in whatsoever STATE I am, therewi
Asked on: Wednesday, January 29, 2025 at 8:28 am EST
Answered on: Thursday, March 6, 2025 at 7:58 am EST
Question: We are in an old building that had things that were done by others that were 'somewhat' questionable to say the least. lol There was a debate about the motor sizing of the branch circuit conductors calculatin from the small vfd they are thinking of bypassing, (its feed by 15amp fused disconnect that is fed by a 20amp breaker).Voltage present is 208volts 3 phase.I didn't have my code book at the time, but my 'handsome/ugly book' says a 3phase 208volt 5hp 16.7 FULL load current is what we should use plus 125%. So technically 16.7x125%= 20.875 is the calculation I get and Since they plan to bypass everything (which again I dont recommend, as the vfd had overload protections adjustable). . .Others ae saying since its just a 14 amp nameplate on motor they can use #14 for the 208v even though they said sometmes the motor start up would blow the 15amp fuses. . I tried to explain Full load current (the nec chart) vs full load amps (nameplate amps) is different in sizing the branch circuit.The overload protection are sized at the nameplate amps (ie. the 15amp fuses) or setting on the vfd possibly? can go up to about max 125% possibly 140%? (need my NEC to sure of the 140%) if trip setting is still too low. 115% of name plate is what appears to be set at 115%x 14=. 16.1 if we do 125%x 14=17.5 140%x14= 19.6 But if they bypass everyting which I dont recommend, I think they might can use the 20amp breake even though that is above the 140% , but I have always rounded down for overload protection, and round UP for groundfault/short circuit protection and it appears since everything else is bypassed the 20amp breaker will function as both the overload and ground/fault short circuit protection. Did I make a mistake on this calculation? can you technically use the 20amp breaker (no fuses) even though its 19.6amps max calculation? Also, I couln't remember what the 010A means beside the 'usuable at 208v 14. I assume the 14 was the running amps of the motor itself at 208v.When I get a chance I can double check my NEC code book 2023Here is the nameplate
Okay, let's break down this motor circuit situation, focusing on code compliance and safe practices. You're right to be concerned, and your instincts are good. Bypassing the VFD introduces significant risks.
Key Considerations and Code References (2023 NEC unless otherwise specified)
Motor Full-Load Current (FLC) vs. Nameplate Amps
This is critical. You are correct. For branch circuit conductor sizing, you
must use the values in Table 430.250 of the NEC (Three-Phase AC Motors). The nameplate FLA is only used for overload protection. For a 5 HP, 208V, 3-phase motor, Table 430.250 lists 16.7 amps. The motor's nameplate FLA of 14 amps is for overload protection and sometimes for applying short circuit and ground fault protection. The "010A" might be a model number or an internal designation for the motor, rather than a specific current rating required to calculate amperage.2. Branch Circuit Conductor Sizing (NEC 430.22)
Minimum conductor ampacity: 125% of the Table 430.250 FLC. 16.7 amps 1.25 = 20.875 amps. You are correct. Given the code, you need conductors rated for at least 20.875 amps.
#14 AWG is almost certainly not sufficient. #14 AWG is typically only rated for 15 amps (see Table 310.16). Using #14 would be a code violation and a fire hazard. You'll need to consult Table 310.16 to determine the correct conductor size, considering insulation type and ambient temperature. Generally, #12 AWG copper is a good starting point for 20A circuits. Double-check the ampacity of #12 AWG with the insulation type (THHN, THWN, etc.) and installation conditions.3. Overload Protection (NEC 430.32)
This is where the nameplate FLA is important. Overload protection is designed to protect the motor from running at currents higher than its nameplate rating for extended periods.
Without the VFD
Overload protection is now the 20 amp breaker. This means it will trip slower than a fuse of 14 Amps or slightly above. Maximum Overload Protection Size: For motors with a service factor of 1.15 or more, or a temperature rise of 40°C or less, the overload protection can be set at a maximum of 125% of the nameplate FLA (NEC 430.32(A)(1)). For all other motors, the overload protection can be set at a maximum of 115% of the nameplate FLA (NEC 430.32(A)(1)). Based on your description, this likely applies to your motor, but you would need the exact nameplate to confirm.
Applying 115% 14 amps 1.15 = 16.1 amps. The 20 amp breaker exceeds this. Since they are bypassing the VFD which had the overload protection, the 20 amp breaker will also be working as the overload protection and the 20amp breaker would be beyond the allowed percentages according to NEC 430.32(A)(1). The best solution would be to install fuses to protect from overload with the appropiate size.
4. Short-Circuit and Ground-Fault Protection (NEC 430.52)
This protects the circuit from faults, not overloads. The 20 amp breaker provides this protection. The maximum rating or setting of the breaker depends on the motor type (Table 430.52). For a standard motor, the maximum is typically 250% of the motor FLC (Table 430.250). 250% of 16.7 amps = 41.75 amps. The 20 amp breaker is less than this, so it's acceptable for short-circuit/ground-fault protection. However, if you increase the breaker to a larger size for overload protection, you must be aware of the increase in risk of a ground fault or short circuit.5.
Fused Disconnect (NEC 430.109(A))
You mentioned a 15 amp fused disconnect. Since they are bypassing the VFD, that fused disconnect is in the circuit so you will still need to comply with the overload rules. It is currently feed a 20amp breaker. So the 15amp fuses are blowing. Based on NEC 430.32 and a nameplate of 14 Amps, your overload fuses should not exceed 16.1 Amps. If you change the fuses to comply, there would likely be nuisance tripping. It might be best to bypass both the vfd and fused disconnect and replace the 20 amp breaker with fuses. That way you can install the proper fuses, and they will be properly protected.
Your Concerns & Calculations
You are absolutely right to question using #14 wire. It's almost certainly too small and dangerous. Bypassing the VFD is generally a bad idea due to loss of protection and control. Your calculations are generally correct. You understand the difference between FLC and FLA.
Recommendations
Do NOT bypass the VFD if possible. Repair or replace it. The VFD provides valuable overload protection, adjustable speed control, and often energy savings.2. If the VFD must be bypassed
Replace the #14 wire with properly sized conductors. Use Table 310.16 to determine the correct ampacity based on insulation type, installation method, and ambient temperature. #12 AWG copper is a good starting point for a 20 amp circuit. Provide proper overload protection. Since the VFD is gone, you'll need a separate overload relay or properly sized fuses. A correctly sized thermal overload relay is the ideal solution. Keep the 20 amp breaker for short-circuit/ground-fault protection. This is likely acceptable. Verify the disconnect switch's rating. Ensure it's rated for the motor horsepower and voltage. If not, replace it.3. Consult with a qualified electrician. This is not a situation to DIY without expert help. An electrician can properly assess the situation and ensure a safe and code-compliant installation.4. Document Everything! Keep a clear record of the changes made, the reasoning behind them, and the code sections followed.
Why is this important? Safety
Undersized conductors and inadequate overload protection can lead to overheating, insulation breakdown, fires, and motor damage.
Code Compliance
Failure to comply with the NEC can result in fines, insurance issues, and liability.
Motor Life: Proper protection extends the life of the motor.I hope this helps! Don't hesitate to ask if you have more questions. Flag for review