Question: I have a hydraulic elevator fed from 200a main, to fused disconnect w/150A fuses. 480v, 60 hp motor. Elevator company recently replaced the rails in shaft due to "warping". Since placing elevator back in service, it will run fine for 3-4 days and then randomly trip main breaker. Breaker was replaced but still it trips. Motor is the original 17 year old motor. Electrical contractor says "power is good". Elevator tech say it "must be power". And so it goes.... Thoughts?
This is a classic head-scratcher situation where you're caught in the middle and need to methodically troubleshoot. Here's a breakdown of thoughts, potential causes, and a plan of attack
Understanding the Problem:
Intermittent Tripping
The key here is that it's not constant. This points away from a simple overload (which would trip reliably) and more towards something that develops or changes over time.
"Power is good" and "Must be power" are unhelpful
These are common refrains when no one wants to take responsibility. You need data, not opinions.
Timing
The 3-4 day interval is significant. It suggests a heat buildup, degradation of insulation, or a slow change in a component's performance.
Recent Work
The rail replacement is important to consider, though potentially not directly related to the electrical issue. Could the vibration/movement involved in the rail work have disturbed something else?
Possible Causes (In order of likelihood)
Motor Issues
Winding Insulation Degradation
Over time, motor windings can deteriorate. Heat, vibration, and contamination cause the insulation to break down. This can lead to shorts between windings or to ground. This is the MOST LIKELY scenario given the motor's age, the intermittent tripping, and the high current draw of a motor.
Loose Connections Within the Motor
Vibration could have loosened internal connections.
Bearing Issues
Bad bearings put extra load on the motor and cause it to draw more current. You'd likely hear or feel this, but it can develop gradually.
Contamination
Check the motor for dirt, dust, oil, or other contaminants that could be affecting insulation.2.
Hydraulic System Problems
Hydraulic Pump Issues
If the hydraulic pump is becoming less efficient (due to wear), the motor will have to work harder and draw more current.
Hydraulic Oil Condition
Dirty or degraded oil can increase friction and load on the pump.
Valve Problems
Stuck or slow-acting valves in the hydraulic system can cause pressure spikes and overloads on the motor.3.
Electrical System Issues
Loose Connections
Even though the electrical contractor says the power is good, specifically request that they check every connection in the elevator circuit: Main breaker terminals, disconnect terminals, contactor terminals, motor terminals, etc. Look for signs of oxidation, burning, or looseness. Use a torque wrench to ensure proper tightening. Loose connections cause resistance, heat, and voltage drop, which can stress the motor.
Contactor Problems
The contactor (the relay that switches the motor on and off) could have worn contacts or a weak coil. Arcing or chattering can cause current spikes.
Ground Fault
A small ground fault might not trip the breaker immediately but could weaken the breaker or add heat, eventually leading to a trip.
Voltage Imbalance
A significant voltage imbalance on the 480V supply can cause the motor to draw excessive current. Have the electrical contractor measure the voltage on all three phases while the elevator is running under load.
Harmonics
Harmonics in the power system (caused by other equipment) can sometimes overload breakers. Less likely, but worth considering if other equipment has been recently added to the building.4.
Elevator Control System Issues
Faulty Control Logic
In rare cases, the elevator's control system could be malfunctioning and commanding the motor to run in a way that causes an overload.5.
The Breaker Itself (Again)
Defective Breaker
Although the breaker was replaced, there is still a small chance that you got another defective one. It's rare, but it happens.
Incorrect Breaker Type
Is the replacement breaker exactly the same type and rating as the original? It must be a motor-rated breaker.
Nuisance Tripping
If the breaker is old, it could be susceptible to nuisance tripping due to heat or vibration.
Troubleshooting Plan
Gather Data
Motor Nameplate Information
Get the motor's full nameplate details (HP, voltage, full load amps (FLA), service factor, etc.).
Breaker Details
Record the breaker's manufacturer, model number, and trip curve.
Fuse Details
Verify the disconnect fuses are correct amperage for the motor/application.
Operating Conditions
Document when the breaker trips: During up travel, down travel, starting, stopping, or at a specific floor.2.
Motor Testing (Essential)
Insulation Resistance Test (Megger Test)
This is critical. Use a megohmmeter to measure the insulation resistance between each motor winding and ground, and between windings. Low resistance readings indicate insulation breakdown. This must be done with the motor disconnected from the power supply. Record the temperature and humidity at the time of the test. A significant drop in insulation resistance over time is a clear indicator of a problem.
Motor Current Readings
Use a clamp-on ammeter to measure the current on each phase of the motor while the elevator is running under load (both up and down). Compare these readings to the motor's FLA rating. Also check for current imbalance between the phases.
Motor Voltage Readings
Measure the voltage on each phase at the motor terminals while the elevator is running under load. Look for voltage imbalance.
Motor Temperature
Use an infrared thermometer to check the motor's surface temperature. An unusually hot motor is a sign of problems.
Visual Inspection
Carefully inspect the motor for signs of overheating, damage, or contamination. Check the motor's cooling fan to make sure it's working properly.3.
Hydraulic System Check
Hydraulic Pressure
Have the elevator tech check the hydraulic pressure during operation.
Hydraulic Oil
Have the oil checked for contamination.
Listen for Noises
Listen for unusual noises from the pump or valves.4.
Electrical System Inspection (Again, Be Specific)
Tighten Connections
Have the electrical contractor methodically tighten every connection in the elevator circuit.
Contactor Inspection
Inspect the contactor contacts for signs of wear or arcing. Consider replacing the contactor if it's old or shows signs of damage.
Voltage Balance
Measure the voltage on each phase at the main panel, the disconnect, and the motor terminals, while the elevator is running under load.
Ground Fault Testing
Use a ground fault locator to check for small ground faults in the system.5.
Monitoring
Current Monitoring
Install a recording ammeter to monitor the motor current over several days. This can help you identify patterns or spikes in the current that might be causing the breaker to trip.
Temperature Monitoring
If you suspect overheating, use a temperature logger to monitor the motor temperature over time.
Communication is Key
Get Everyone On The Same Page
Schedule a meeting with the electrical contractor and the elevator technician to discuss the problem and coordinate troubleshooting efforts.
Document Everything
Keep detailed records of all tests, measurements, and repairs.
Don't Assume
Verify everything.
Important Considerations
Safety First
Working with electricity and elevators is dangerous. Only qualified personnel should perform testing and repairs.*
Code Compliance
Ensure that all work is performed in accordance with local electrical codes and elevator safety regulations.
In Summary:
The most likely culprit is a failing motor. The intermittent tripping, combined with the motor's age, points strongly in that direction. The insulation resistance test is the most important test to perform. If the motor checks out, then you need to systematically investigate the other potential causes, focusing on loose connections, hydraulic system problems, and the electrical supply. Good luck! Flag for review