Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 2 HR Rating

User: Alwayslearningelec, Location: NJ

Asked on: Friday, January 31, 2025 at 2:42 pm EST
Answered on: Thursday, March 6, 2025 at 8:05 am EST

Question: Are these the most common ways to give a circuit a 2 hour fire rating?1. MI cable2. Vitalink 2 hr MC cable3. EMT with RHH 2 hour rated wire?If the circuit is within a 2 hour rated room is it then considered 2 hour rated and you don't need any of the above? What about when it leaves the room? Would not make much sense to splice over and change to a 2 hour rated wiring method

Okay, let's break down fire-rated circuit options and the implications of fire-rated rooms.

Common Methods for 2-Hour Fire-Rated Circuits

Your list is a good start and contains common options. Here's a more comprehensive view, with some nuances:1.

Mineral Insulated (MI) Cable

This is inherently fire-resistant and often meets 2-hour (or even higher) fire ratings without additional measures. It's very robust.2.

Specially Listed Fire-Resistive MC Cable

"Vitalink" is a brand name (there are others). These MC cables are specifically designed and tested to maintain circuit integrity for a specified time (2 hours, in this case) under fire conditions. They typically have special insulation and construction. Often they are listed with a UL number starting with FHIT.3.

EMT with RHH/XHHW/THHN Wire (with Fire-Resistive Protection)

EMT conduit can be part of a fire-rated assembly, but it's not inherently fire-rated on its own. You need to install it with special fire-resistant wire listed for the application, and it may also require additional external fireproofing or encasement. It is important to check the specifics of the tested assembly for a given fire rating to ensure that all requirements of the rated system are met.

Important Considerations Regarding EMT



Tested Assembly is Key

The fire rating isn't just about the individual components (EMT and wire). It's about the
entire assembly as tested and listed by a recognized testing laboratory (e.g., UL). The specific details of the installation, including the type of fittings used, support spacing, and any required fireproofing materials, must match the tested assembly.

Fireproofing Materials

Often, EMT systems require being encased in a fire-resistive material (like spray-applied fireproofing or a specific type of wrap) to achieve a 2-hour rating.

What About Circuits Within a 2-Hour Rated Room?


This is where it gets tricky and depends on the specific codes and the purpose of the fire-rated circuit. Here's the general principle: Purpose of Fire Rating

The main reason for creating a fire-rated circuit is to ensure power is available for
critical systems during a fire. This includes things like: Fire pumps Fire alarm systems Emergency lighting Smoke evacuation systems Elevators used for fire evacuation

Inside the Room (Potentially Not Required)

If the wiring is
contained entirely within a room with a 2-hour (or higher) fire-resistance rating, and the circuit is not serving one of the critical systems mentioned above, you might not need the fire-rated wiring methods. The room itself provides the fire protection. However, always check with the local authority having jurisdiction (AHJ) and the applicable building codes.

Leaving the Room (Definitely Required)

As soon as the circuit leaves the fire-rated room, it must maintain its fire-resistance rating until it reaches its intended load. This is the most common and critical application of fire-rated wiring. The fire-rated room protects what's inside the room. The fire-rated circuit protects the functionality of critical systems.

Splicing and Transitions

You're right – splicing and transitioning between wiring methods are crucial considerations:

Avoid Splicing Within a Fire-Rated Run if Possible

Ideally, design the circuit to minimize or eliminate splices within the fire-rated portion.


Approved Splice Methods

If a splice is unavoidable within a fire-rated run, use only splicing methods and materials (e.g., listed fire-resistive splice kits) that are part of a UL-tested fire-rated assembly for the specific wiring method being used. Standard wire nuts are not sufficient.

Transition Boxes/Devices

The transition from a fire-rated wiring method to a non-fire-rated wiring method must be done in a listed transition box or device that maintains the fire resistance rating.

Example Scenario

Let's say you have a fire pump that needs to run during a fire. The electrical panel for the fire pump is located outside the room. Then, the electrical circuit powering the fire pump
must be fire-rated from the electrical panel to the pump.

Key Takeaways



Consult Codes and AHJ

The specific requirements for fire-rated circuits are driven by the National Electrical Code (NEC), local building codes, and the interpretation of the local AHJ. Always check with them.

Understand the System

Don't just think about the wire or the conduit. Think about the entire fire-rated
system.

UL Listings

Look for UL listings (or listings from other recognized testing laboratories) that specifically identify the fire-resistance rating and the conditions under which it was tested.*

Documentation:
Keep thorough documentation of the fire-rated wiring methods used, including UL listings, product data sheets, and installation instructions. This is crucial for inspections and future maintenance. Flag for review

Previous Question Next Question