Question: For above rental generator to serve the building while building’s main utility xfmr is replaced, no need to feed the generator’s block heater and batteries from a different source of power, correct? Once the generator runs, it will power those loads itself?
You are correct. You typically do not need a separate power source for the block heater and battery charger once the generator is running. Here's why: Integrated Charging System
Most rental generators designed for backup power applications have an integrated charging system. This system, powered by the generator's engine, takes over the function of maintaining the battery charge and providing power to the block heater once the generator is running.
Automatic Transfer Switch (ATS)
The automatic transfer switch (ATS) is the key component that switches the building's electrical load from the utility transformer to the generator. When the ATS senses a power outage (utility transformer replacement in this case), it starts the generator and, once the generator is up to speed and voltage, transfers the building's load. Crucially, the generator's charging system and block heater are already powered by the generator itself at that point.
Block Heater Purpose
The block heater is primarily for cold weather starting. It helps keep the engine warm so it can start reliably. Once the engine is running, the engine's normal operation generates heat.
Battery Charger Purpose
The battery charger maintains the battery's charge while the generator is off, ensuring it has enough power to start when needed.
Rental Generator Configuration
Rental generators are typically configured to be self-sufficient once they are running. They are designed for easy connection and operation. Providing a separate power source for the block heater and battery charger would add complexity and is usually unnecessary.
Important Considerations
Verify with Rental Company
Double-check with the rental company to confirm that the generator's charging system and block heater are designed to operate from the generator's output. This is standard practice, but it's always best to verify.
Fuel Supply
Remember that the generator needs a reliable fuel supply (diesel or natural gas) to run continuously during the utility transformer replacement. Plan for adequate fuel delivery and storage.
Exhaust Venting
Proper exhaust venting is critical to prevent carbon monoxide buildup.
ATS Operation
Ensure the automatic transfer switch (ATS) is properly configured and functioning correctly to switch between the utility transformer and the generator.
Load Management
Check the generator's capacity and the building's electrical load to avoid overloading the generator.*
Safety
follow all electrical safety precautions.
In summary, you are correct. For a standard rental generator used to back up a building during a utility transformer replacement, you do not typically need a separate power source for the block heater and battery charger once the generator is running. The generator's integrated charging system will take over these functions. Flag for review