Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: High fault current(> 200 kA) from utility

User: MI_Engineer, Location: Michigan

Asked on: Wednesday, February 5, 2025 at 3:11 pm EST
Answered on: Thursday, March 6, 2025 at 8:18 am EST

Question: Hello all,I received the following from the electric utility. The system consists of multiple 250 kVA to 500 kVA transformer banks tied together with 208 V, 3ph secondaries."The % X/R ratio for the power line is 2.87. {Electric Utility's} contribution to a fault at the customer’s service point is 58,173 Amps at 208V or 19.65MVA three phase symmetrical. The ultimate fault could be as high as 80MVA in the future."While I don't get the exact same results 19,650 kVA / (208 * sqrt(3) = 54,583 kA, it is similar to what was received in the letter.At 80 MVA it would be 222.22 kA = 80,000 kVA / (208 * sqrt(3))Is there service equipment sized to handle >200 kA? Or is the better path to install equipment rated 200 kA and inform the Owner of the decision. I've found Class L fuses rated up to 300 kA but am unable to find enclosures to put them in.

You're right to be concerned about these high fault current values. Let's break down the problem and discuss potential solutions.

Understanding the Issue High Fault Current

A potential fault current of over 200kA at 208V is exceptionally high. This means that in the event of a short circuit, a tremendous amount of current could flow through the equipment. This can cause significant damage, fires, and potential injury.


NEC Compliance

The National Electrical Code (NEC) requires all electrical equipment to have a Short-Circuit Current Rating (SCCR) sufficient to withstand the available fault current at its terminals (NEC 110.9).

Equipment SCCR

You need to ensure that all your service equipment, including the main disconnect, switchboards, panelboards, and branch circuit protective devices, have SCCRs that meet or exceed the calculated available fault current.


Utility Contribution

The utility's contribution to the fault current is a significant factor. The increasing fault current in the future due to utility system upgrades compounds the issue.

Solutions and Strategies
1. Accurate Fault Current Calculation is Key Verify Utility Data

While your calculations are close, it's vital to confirm the utility's fault current data (magnitude and X/R ratio) directly with them. Small variations in X/R can significantly impact the calculated peak let-through current. Request a detailed fault study report from the utility if possible.


Detailed System Modeling

Use a software program like SKM PowerTools, ETAP, EasyPower, or similar to perform a thorough short-circuit study of your entire system. These programs will accurately calculate fault currents at each point in your distribution system, taking into account transformer impedances, cable impedances, and the utility contribution. Don't just rely on hand calculations. Software is crucial for accuracy.

Calculate Ipeak

The asymmetrical peak current (Ipeak) is crucial for selecting equipment. Calculate Ipeak = Fault Current
Symmetrical Factor (SF) = Fault Current (1.6 + (X/R ratio / sqrt(3)))2.

Equipment Selection and Coordination
High SCCR Equipment



Service Entrance Equipment

Finding a single piece of equipment (main switchboard or switchgear) rated for >200kA SCCR at 208V can be challenging and expensive. Consult with manufacturers like Square D/Schneider Electric, Eaton, Siemens, ABB, or GE. They may have engineered solutions for very high fault current applications. Look into switchgear-type assemblies, which tend to have higher ratings.


Fuses

You're correct about Class L fuses having high interrupting ratings. However, finding suitable enclosures is the issue.

Current Limiting Devices



Current-Limiting Fuses

Using current-limiting fuses upstream of lower-rated equipment is a common strategy. The current-limiting action of the fuse reduces the let-through current seen by the downstream equipment. Carefully coordinate the fuse characteristics with the downstream equipment's SCCR.

Current Limiting Circuit Breakers

These are a thing, though less common. They act to limit the current like a fuse.


Series Ratings

Series ratings are a big maybe and needs to be done by a qualified person with the appropriate knowledge of the equipment being used.

Transformers

You could use "fault impedance" transformers. These are specially designed transformers with impedance high enough to reduce the available fault current to a manageable level. They are more costly and can impact voltage regulation.


Impedance

Adding impedance between the utility and service entrance can limit the fault current. Reactors are sometimes used for this purpose, but they introduce voltage drop and losses.3.

Coordination and Selective Coordination
Selective Coordination

Design your system so that the protective device closest to the fault clears it
without causing upstream devices to trip. This minimizes the impact of a fault and ensures that only the affected area is de-energized. This is crucial for reliability.

Coordination Study

A professional coordination study is essential. This study analyzes the time-current characteristics (TCC) curves of all protective devices (fuses and circuit breakers) to ensure proper coordination and selectivity.4.

Documentation and Communication
Detailed Documentation

Maintain thorough documentation of all fault current calculations, equipment SCCRs, coordination studies, and any deviations from standard practices.


Owner Notification

You are right to inform the owner of the situation and your proposed solutions. Clearly explain the risks associated with the high fault current and the rationale behind your design choices. This should be done in writing.

Labeling

Label all equipment with the available fault current at its terminals.5.

Consider these things when deciding



Cost

Each solution has its own cost. High SCCR equipment is the most expensive, while current limiting devices are the most cost effective.

Space

You are very limited on space with an indoor service.


Voltage Drop

Adding impedance, even a few feet of cable between a CT cabinet and the main disconnect can cause a voltage drop.

Specific Actions to Take
1. Contact the Utility

Discuss the provided fault current data, the X/R ratio, and the possibility of future increases. Request a detailed fault study report.2.

Engage a Qualified Electrical Engineer

This is not a DIY situation. You need a professional engineer experienced in power system studies and protective device coordination.3.

Perform a Detailed Short-Circuit Study

Using software, model the entire system, including the utility contribution, transformers, cables, and all protective devices.4.

Evaluate Equipment Options

Research high SCCR equipment, current-limiting devices, and other solutions. Get quotes from multiple manufacturers.5.

Develop a Coordination Study

Ensure selective coordination between all protective devices.6.

Document Everything

Keep detailed records of all calculations, studies, and design decisions.

Important Considerations
Safety

High fault current presents a serious safety hazard. Prioritize safety in all design and installation activities.


Maintenance

Ensure that the system is properly maintained and that protective devices are tested regularly.*

Future Changes

Be aware of potential future changes to the utility system that could increase fault current.

In summary, dealing with extremely high fault current requires a comprehensive approach involving accurate calculations, careful equipment selection, expert engineering analysis, and clear communication with the owner. Don't cut corners on safety or rely on assumptions. Engage qualified professionals to ensure a safe and reliable installation.
Flag for review

Previous Question Next Question