User: alixenos, Location: Florida

Asked on: Thursday, February 6, 2025 at 3:05 pm EST
Answered on: Thursday, March 6, 2025 at 8:21 am EST

Question: Hi,4.13.1.1 of NFPA 780:"Each down conductor shall terminate to one of thefollowing:(1)A grounding electrode dedicated to the lightning protection system(2)A grounding electrode system of a building, structure, orfacility that has multiple grounding electrodes bondedtogether with a ground ring electrode meeting therequirements of 4.13.4"what determines the choice of selecting where the down conductors will terminate?thanks

The choice of terminating down conductors to either a dedicated grounding electrode or the building's grounding electrode system (with a ground ring) depends on several factors, and a qualified lightning protection installer will consider all of them. Here's a breakdown of the key considerations

1. Existing Grounding System of the Building/Structure:
Presence and Quality

Is there already a robust, interconnected grounding system in place for the building, meeting relevant electrical codes and with documented resistance to ground? If the existing system is inadequate (high resistance, poorly connected, not meeting modern standards), a dedicated system is often preferable.


Multiple Electrodes and Ground Ring

The NFPA 780 specifically allows connection to the building's system only if it has multiple grounding electrodes bonded together with a ground ring meeting the requirements of 4.13.
4. This ensures low impedance and effective current dissipation. If the building's system doesn't have this, you essentially have to use a dedicated system.


Potential Ground Loops

Connecting to the building's system can, in some cases, introduce ground loops if not done carefully. This can create unwanted currents and interference with sensitive electronic equipment. A dedicated system can avoid this issue.

2. Soil Resistivity



Low Resistivity is Key

Soil resistivity is a crucial factor. Lower resistivity allows for quicker dissipation of lightning energy into the ground. If the soil has high resistivity, a more extensive and potentially dedicated grounding system may be necessary to achieve the required low resistance to ground.

Site-Specific Testing

Soil resistivity testing is almost always required. The results of this testing inform the design and extent of the grounding system, regardless of whether it's dedicated or connected to the building's system.

3. Size and Complexity of the Structure



Large or Complex Structures

Larger or more complex structures may require multiple down conductors and grounding points. In these cases, integrating with the building's existing system (if compliant) can be more practical and cost-effective, provided the ground ring and multiple electrodes exist.

Smaller, Simpler Structures

For smaller, simpler structures, a dedicated grounding electrode system may be perfectly adequate and simpler to install.

4. Sensitivity of Equipment Inside the Building



Sensitive Electronics

If the building houses highly sensitive electronic equipment, a dedicated lightning protection system grounding system can provide better isolation from ground currents generated by a lightning strike. This helps protect the equipment from damage. The more sensitive the electronics, the more attractive the dedicated system becomes.

5. Local Codes and Regulations



Compliance is Mandatory

Local building codes and regulations may have specific requirements or preferences regarding lightning protection grounding systems. These codes must be followed.

6. Cost



Installation and Maintenance

Cost is always a consideration. Dedicated systems can sometimes be more expensive to install, but they might offer long-term benefits in terms of protection and reduced risk of damage. Connecting to an existing system can be cheaper, if the existing system is fully compliant and requires no upgrades. Upgrading an existing system to make it compliant could easily outweigh the cost of a dedicated system.

7. Accessibility for Maintenance and Testing



Ease of Access

The grounding electrodes and connections should be accessible for periodic inspection and testing.

In summary, there's no one-size-fits-all answer. The best approach is to


Have a qualified lightning protection system designer/installer assess the site and the existing grounding system.
2. Perform soil resistivity testing.3. Evaluate the building's construction, size, complexity, and the sensitivity of equipment inside.4. Consider local codes and regulations.5. Weigh the cost of both options (dedicated vs. connection to building's system).

The installer will then be able to make an informed recommendation that best meets the specific needs of the building and provides adequate lightning protection. Remember to prioritize safety and compliance with applicable standards. Flag for review