User: Isaiah, Location: Baton Rouge
Asked on: Thursday, February 6, 2025 at 10:19 pm EST
Answered on: Thursday, March 6, 2025 at 8:22 am EST
Question: I was asked if I had performed a short circuit calculation for a feeder to HVAC unit. I sized the feeder based on the MCA of the unit. Why would it be necessary to do a short circuit calculation on something this simple?
You're right, it might seem unnecessary for a simple HVAC feeder. However, here's why a short circuit calculation is still important, even in this situation: Overcurrent Protective Device (OCPD) Selection
The short circuit calculation verifies that the overcurrent protective device (breaker or fuses) you've chosen can interrupt the maximum available fault current at the HVAC unit. If the fault current exceeds the interrupting rating of the OCPD, the OCPD could fail catastrophically during a fault, leading to fire, explosion, and severe damage.
Equipment Withstand Rating
The HVAC equipment itself has a short circuit withstand rating. This is the maximum fault current the equipment can safely withstand for a short duration without damage. The short circuit calculation ensures the available fault current at the HVAC unit doesn't exceed this withstand rating.
Arc Flash Hazard
A short circuit calculation is a fundamental step in performing an arc flash risk assessment. Even in a small HVAC unit, an arc flash can be deadly. By knowing the available fault current, you can determine the incident energy and appropriate personal protective equipment (PPE) required for working on the equipment.
Code Requirements
The NEC (National Electrical Code) generally requires that electrical systems be designed to withstand the effects of fault currents. While the NEC doesn't explicitly mandate a formal short circuit study for every single circuit, it's implied that you need to verify the interrupting rating of the OCPD and the withstand rating of the equipment. Many jurisdictions and employers have specific policies requiring short circuit studies.
Why it matters even if it seems small
Long Feeder Runs
A long feeder run, even if sized correctly for the MCA, can still have a significant impact on the available fault current. Longer runs introduce impedance, which reduces the fault current. However, you need to calculate the actual fault current to ensure it's within the limits.
Upstream System
The strength of the upstream power source (transformer size, utility impedance) significantly impacts the available fault current. Even if the HVAC unit is small, a strong upstream source could result in high fault currents.*
Coordination
A short circuit study helps to verify that the OCPDs in the system are coordinated. This means that the OCPD closest to the fault will trip first, minimizing the impact on the rest of the system.
In summary: While it might seem overkill for a small HVAC feeder, a short circuit calculation is a crucial step in ensuring safety and compliance. It verifies the OCPD interrupting rating, equipment withstand rating, informs arc flash risk assessment, and helps coordinate the protective devices in your electrical system.Many software packages exist that can easily perform a short circuit study. It's a worthwhile investment to protect yourself, your company, and the people who will work on the equipment. Even simple online calculators can give you a rough estimate. Flag for review