Question: [TLDR] For Intrinsically Safe systems, when putting together a DSD, what Entity Parameters are you supposed to use? It seems like each Table of parameters I've seen is missing some important information that would tell me why I need to use one over the other.I have been struggling to design an intrinsically safe circuit, so I'm hoping that I can get some clarification on a few things in Pepperl+Fuchs literature:I plan on using NCN3-F25-N4-V1 inductive sensors for a Class I, Zone 1/2 (NEC – USA) application. There will be ten (10) of these sensors mounted to the individual pneumatic actuators for our solution. My intention was to run these back to a 4-channel Switch Amplifier (KFD2-SRA-Ex4). From my understanding, I need to install these in accordance with the Control Drawings, which is fine.My intention would be to run two (2) different sensors, both the open and closed signals, to one (1) switch amplifier, which would make up the four (4) channels of the amplifier. When I look at the Control Drawing (116-0145E) of the Switch Amplifier, it allows me to connect to either a Simple Apparatus, which a proximity sensor is NOT, or an approved device with appropriate Entity Concept parameters Voc < Vi and Isc < Ii and Po < Pi (??) and Lo > Lcable + Li and Co > Ccable + Ci. Not sure why Po is missing from the equation…For the KFD2-SRA-Ex4: Voc = 10.6V, Isc = 19.5mA, Po = ??, Co (IIC) = 1.273uF, Lo (IIC) = 84.88mH.When I look at the Control Drawing (116-0456) for the proximity sensor, Table 1 has three sets of values, without any reference to what Type 1, 2 or 3 is referring to, so I’m unsure if I can wire these four (4) sensor circuits to the amplifier based on that Table alone. Is Type 1, 2 and 3 ATEX specific? I don’t see any mention of it in NFPA or UL 698A.I guess beyond the question that I mentioned above, is Po not a factor in determining suitability for this Switching Amplifier since it’s not listed on the Control Drawing? I would just need to make sure Voc, Isc, Lo and Co are appropriate? And if that’s the case, is it safe to conclude that I am able to use these sensors in tandem with the amplifier, as Voc = 10.6V < Vi =15V and Isc = 19.5mA < Ii = 25mA and Co and Lo are going to be pretty negligible, as the cable run will be less than 10 meters.
Okay, you've identified a common area of confusion when designing intrinsically safe circuits. Let's break down the issues you're encountering with the Entity Concept and those Pepperl+Fuchs control drawings.
Understanding the Entity Concept and Intrinsic Safety Parameters
The Entity Concept is a simplified method for interconnecting intrinsically safe apparatus. The core idea is ensuring the output parameters of the non-hazardous area device (like your KFD2-SRA-Ex4 switch amplifier) are always less than the input parameters of the hazardous area device (your NCN3-F25-N4-V1 sensor) with appropriate safety factors built-in.The parameters you are concerned about (Voc, Isc, Po, Co, Lo, Vi, Ii, Ci, Li) represent the maximum levels of voltage, current, power, capacitance, and inductance, respectively. Voc (Voltage open circuit)
The maximum open-circuit voltage the non-hazardous area device can produce under worst-case fault conditions.
Isc (Current short circuit)
The maximum short-circuit current the non-hazardous area device can produce under worst-case fault conditions.
Po (Power output)
The maximum power the non-hazardous area device can deliver to the hazardous area device under worst-case fault conditions.
Co (Capacitance output)
The maximum allowed total capacitance the non-hazardous area device can drive, including cable capacitance.
Lo (Inductance output)
The maximum allowed total inductance the non-hazardous area device can drive, including cable inductance.
Vi (Voltage input)
The maximum voltage the hazardous area device can withstand without becoming a source of ignition.
Ii (Current input)
The maximum current the hazardous area device can withstand without becoming a source of ignition.
Ci (Capacitance input)
The internal capacitance of the hazardous area device.
Li (Inductance input)
The internal inductance of the hazardous area device.
Why is `Po` Sometimes Missing?
You are correct to question the omission of `Po` on some control drawings. Here's why it might be missing, and why you should proceed with caution:1. Fault Calculation Based on Voc/Isc
Sometimes, `Po` isn't explicitly stated because the entity standards assume that it can be derived from Voc and Isc. Specifically, `Po` = (Voc Isc) / 4. This is a simplified calculation based on the maximum power transfer theorem.
2.
Standard Requirements The different standards will treat `Po` differently. You will need to check with the applicable standard that is relevant to your system.3. Oversight
While unlikely from a reputable manufacturer like Pepperl+Fuchs, there's a small chance it's an omission.
Therefore, DO NOT assume `Po` is unimportant, even if not explicitly stated. In absence of the parameter on the control drawing, you should calculate the output power and verify the device's documentation to ensure compliance.
Analyzing the Control Drawings KFD2-SRA-Ex4 (Switch Amplifier)
You've correctly identified the Voc, Isc, Co, and Lo values. You must calculate `Po`. Use the formula: Po = (Voc Isc) / 4 = (10.6V 0.0195A) / 4 = ~0.0516W or 51.6mW. These parameters represent the maximum output capabilities of the switch amplifier under fault conditions.
NCN3-F25-N4-V1 (Proximity Sensor)
This is where your biggest problem lies. You need to understand what "Type 1, 2, and 3" refer to. Do not proceed without clarification from the manufacturer or distributor!
Possible Interpretations of Type 1, 2, and 3 (Without Clarification, These are Just Educated Guesses)
ATEX Category
Could refer to different ATEX equipment categories (e.g., different levels of protection for Zone 0, Zone 1, or Zone 2). But you mentioned NEC in USA, and it is very unlikely this would be the case
Internal Resistors
Might be tied to how the sensor is internally protected or configured to meet intrinsic safety requirements, and is not being expressed clearly.
Fault Conditions Assumed During Testing
Could be tested under different fault conditions.
Crucially
Each "Type" will have a different set of Vi, Ii, Pi, Ci, and Li values. You must know which set of parameters applies to your specific application.
Recommendation
Contact Pepperl+Fuchs technical support and explicitly ask what "Type 1, 2, and 3" represent in the context of US/NEC Class I, Zone 1/2 certification. Get the full set of Vi, Ii, Pi, Ci, and Li values for the "Type" appropriate for your installation.
Is it Safe to Conclude You Can Use These Sensors with the Amplifier?
The answer is: NOT YET!You can only determine safety after you know the Vi, Ii, Pi, Ci, and Li values for the correct "Type" of sensor configuration and properly calculate the output power on the switch amplifier control drawing:1.
Calculate Po
You did this correctly: Po = (Voc Isc) / 4 (for the switch amplifier). Ensure this aligns with the control drawing.2.
Compare Parameters
Only after you know the sensor parameters can you check: Voc < Vi Isc < Ii Po < Pi Co > Ccable + Ci Lo > Lcable + Li3.
Cable Parameters
You are correct that for short cable runs, Ccable and Lcable are often negligible. However, document your assumption. If the cable run is longer, you must factor in the cable's capacitance and inductance per unit length. Consult the cable manufacturer's data sheet.
Addressing Your Specific Scenario (Wiring Two Sensors to One Amplifier)Wiring two sensors into one amplifier channel might be possible, but requires VERY careful analysis and likely isn't advisable. Here's why:
Combined Parameters
You'd need to determine the combined Ci and Li values of both sensors connected in parallel. The calculations depend on whether they're truly in parallel or if internal resistors within the sensors influence the equivalent inductance and capacitance.
Fault Propagation
Consider what happens if one sensor fails in a specific way (e.g., a short circuit). Could that failure propagate to the other sensor or the amplifier channel and compromise intrinsic safety?
Certification Implications
This configuration might invalidate the original certifications of the devices. It's crucial to confirm that wiring sensors in this way is explicitly supported by the manufacturers of both the sensor and the switch amplifier, and that the entire circuit retains its intrinsic safety rating.
In summary, while it might be appealing to reduce the number of amplifier channels, combining sensor signals on one channel adds significant complexity and risk and is typically avoided in IS design.
Recommendations1.
Contact Pepperl+Fuchs
Get clarification on the "Type 1, 2, and 3" designations for the sensor and obtain the full set of Vi, Ii, Pi, Ci, and Li values for the appropriate "Type" applicable to your installation conditions.2.
Calculate Output Power
Perform a precise calculation of `Po` from the switch amplifier parameters, ensuring it agrees with the control drawing.3.
Verify Entity Parameters
Compare Voc, Isc, Po, Co, and Lo from the switch amplifier to the Vi, Ii, Pi, Ci, and Li values of the sensor (after you have the correct values).4.
Avoid Combining Sensor Signals
Seriously reconsider wiring two sensors into one amplifier channel unless it is explicitly permitted and supported by the manufacturers. The potential risks and complexity outweigh the benefits.5.
Document Everything
Thoroughly document all your assumptions, calculations, and the reasoning behind your design decisions. This is essential for safety reviews and future maintenance.6.
Consult with an Intrinsic Safety Expert
If you are not highly experienced in designing intrinsically safe circuits, it is strongly recommended to consult with a qualified expert to review your design. Intrinsic safety is complex, and errors can have serious consequences.
Disclaimer: This information is for educational purposes only and should not be considered a substitute for professional engineering advice. Always consult with qualified professionals and refer to the relevant standards and regulations for your specific application. Flag for review