User: MisterMoSparky, Location: WV
Asked on: Saturday, February 8, 2025 at 9:50 pm EST
Answered on: Thursday, March 6, 2025 at 8:26 am EST
Question: I had two customers in one day call me bc lightning directly struck their house.First customer lost:- Gas Furnace- Gas Stove- Plug in Security Camera (WiFi)- Electric Blanket- 3-Lightbulbs (incandescent) in the same bathroom Vanity- Flat Screen TV connected to CoaxSecond customer lost only their gas stove.I’ve previously installed surge protectors on their meter combo outside with x2 ground rods when replacing their service.My boss theorized that bc it was connected to the gas lines that the gas itself might not have been bonded to system ground. The same with the TV connected to the coax line.I can’t explain the rest for customer one bc the type 1 SPD I installed has green light indicator and in their manufacture specs it says if the light is still on then the max voltage rating for the surge was not met so the SPD is still operational.I never advertise that these SPD will be able to handle a direct lightning strike but my first customer was pretty disappointed having to make an insurance claim for ~$15k and I don’t blame her.Any thoughts
This is a tough situation, and your customers' disappointment is understandable. While a Type 1 SPD at the service entrance provides a good first line of defense, it's crucial to understand its limitations, especially against direct lightning strikes. Here's a breakdown of what might have happened and some considerations
Understanding the Limits of Surge Protection
Direct Strikes are Devastating
A direct lightning strike carries an enormous amount of energy. While a Type 1 SPD can divert a significant portion of a surge, it's
unlikely to completely eliminate the voltage spike from a direct hit. Think of it like trying to stop a tsunami with a seawall – it can help, but it won't always prevent all damage. Energy Capacity
SPDs have a limited energy absorption capacity. A direct lightning strike can exceed this capacity, even if the indicator light suggests it's still "operational." The green light usually indicates that the MOV (Metal Oxide Varistor) components haven't catastrophically failed (shorted), but it doesn't guarantee they diverted the entire surge.
Lightning Follow-Through
Sometimes, after the initial surge, lightning can cause follow-through currents, especially in gas lines or other conductive paths. These follow-throughs are not the initial lightning bolt but a result of the ionized path created by the strike.
Possible Explanations for the Damage
Grounding and Bonding Issues
Your boss is on the right track. Improper grounding and bonding is a major factor in lightning damage.
Gas Line Bonding
The gas line must be properly bonded to the grounding electrode system. If it's not, the gas line can act as a path for the lightning surge, potentially damaging anything connected to it (like the stove and furnace). It's not just the gas itself being conductive, but the metal pipes creating a conductive pathway.
Coax Bonding
The coax cable should also be properly bonded to the grounding system before it enters the house. This helps to divert surges that travel along the cable.
Ground Rod Resistance
While you installed ground rods, it's important to test the resistance to ground. High resistance makes it harder for surges to dissipate into the earth.
"Cascading" Surges
The initial surge from the lightning strike can create smaller, "secondary" surges within the home's electrical system. These smaller surges can damage sensitive electronics even if the main SPD is functioning.
Ground Loops
Improper grounding can create ground loops, which can amplify the effects of a surge and make damage more widespread.
Inductive Coupling
Lightning strikes can induce surges in nearby wiring even if there's no direct connection. This can happen in parallel runs of wire (e.g., electrical wiring running near coax cable).
SPD Failure Mode
Although the indicator light may be on, SPDs can degrade over time with repeated surges. It's possible the SPD's performance had diminished, reducing its ability to handle a large strike.
Lack of Point-of-Use Protection
While the Type 1 SPD provides whole-house protection, it's often recommended to also use point-of-use surge protectors (e.g., power strips with surge protection) for sensitive electronics like TVs and computers. This provides an extra layer of defense.
Specific to the Customers' Losses
Customer 1
Gas Furnace & Stove
Likely related to gas line grounding/bonding issues.
Security Camera (WiFi)
Surge could have entered through the power line or the data line (WiFi, even though wireless still uses electricity).
Electric Blanket
Direct surge through the electrical system.
Lightbulbs (Vanity)
A strong surge could easily burn out incandescent bulbs.
Flat Screen TV (Coax)
Surge entered through the coax line.
Customer 2
Gas Stove
Almost certainly a gas line grounding/bonding issue.
What to Do Now
Inspect Grounding and Bonding
This is the most critical step.
Gas Line Bonding
Ensure the gas line is properly bonded to the main grounding electrode system with a listed bonding clamp. Check for corrosion at the connection points.
Coax Bonding
Verify the coax is bonded to the grounding system where it enters the house.
Ground Rod Resistance
Measure the resistance to ground of your ground rod system. Ideally, it should be 25 ohms or less. If it's higher, consider adding additional ground rods or improving soil conductivity.
Bonding at the Meter Combo
Ensure that the neutral and ground are properly bonded at the service entrance.2.
Review Installation Practices
Double-check your work to ensure you followed all applicable electrical codes and manufacturer's instructions.3.
Consider Additional Protection
Point-of-Use Surge Protectors
Recommend point-of-use surge protectors for sensitive electronics.
Whole-House Coax/Data Line Surge Protectors
These protect devices connected to coax or data lines.
Lightning Rod System
For homes in areas prone to frequent lightning strikes, a lightning rod system is the best way to provide effective protection.4.
Educate Customers
Limitations of SPDs
Clearly explain that SPDs are not a guarantee against all lightning damage, especially direct strikes.
Layered Protection
Emphasize the importance of a layered approach to surge protection, including whole-house and point-of-use devices.
Regular Inspection
Advise customers to have their electrical system inspected periodically, including the grounding and bonding system.
Addressing Customer Disappointment
Empathy
Acknowledge their frustration and disappointment. Let them know you understand their situation.
Explanation
Explain the limitations of surge protection and the likely causes of the damage.
Solutions
Offer to inspect and correct any grounding and bonding issues to improve their protection.
Transparency
Be honest about what the SPD can and cannot do.
Important Notes
Consult with a Lightning Protection Specialist
For complex situations or in areas with high lightning frequency, consider consulting with a certified lightning protection specialist.
Electrical Code
Always adhere to the latest edition of the National Electrical Code (NEC) and local codes regarding grounding and bonding.*
Documentation: Keep thorough records of your grounding and bonding installations, including ground resistance measurements.By thoroughly investigating the grounding and bonding system, recommending additional protection, and clearly communicating with your customers, you can help minimize the risk of lightning damage and manage their expectations effectively. Flag for review