User: SENTHIL M, Location: AL KHOBAR
Asked on: Tuesday, February 11, 2025 at 8:33 am EST
Answered on: Thursday, March 6, 2025 at 8:30 am EST
Question: Dear engrsIn Saudi Arabia, 132/33kV substations utilize FSCT (Free Standing Current Transformers) for OHL feeder protection when connecting to 132kV GIS over a short distance of 200 meters for cable tail protection. However, the same cable tail protection feature is not applied to the 132/33kV transformer protection requirements when the connection is made from 132kV GIS to a Grid Transformer (GT).I understand that GT transformers use cable sealing ends; is this the reason for the difference?Can anyone explain?
You're right to question this. The setup you describe is common in Saudi Arabia and other regions, but the discrepancy you point out requires careful consideration. Here's a breakdown of why the FSCTs might be used on the OHL feeder but not for the transformer, and what factors influence that decision
Possible Reasons for Using FSCTs for OHL Feeders but Not the Transformer:
1. Focus on External Faults on the OHL
OHL Feeders are more exposed to external faults
Overhead lines are inherently more susceptible to faults caused by lightning strikes, tree contact, animal interference, and other external factors. The FSCTs provide fast and sensitive protection specifically for these faults on the OHL itself.
Distance to fault
Because OHLs are longer than the short 200m cable tail connection, the FSCTs need to detect faults happening along the entire OHL cable.2.
Transformer Protection Philosophy
Internal Fault Emphasis
Transformer protection schemes (differential, REF, etc.) are primarily designed to detect internal faults within the transformer itself. These schemes often rely on CTs located inside the transformer bushings or very close to the transformer terminals, providing highly localized fault detection.
Backup Protection for Cable Tails
While dedicated cable tail protection isn't always implemented with FSCTs for the transformer, the overall transformer protection scheme (differential, overcurrent, restricted earth fault) inherently provides some level of backup protection for the cable tail connection to the GIS. The sensitivity and speed might not be as high as with dedicated FSCTs, but it's still present.3.
Cost and Complexity
FSCTs add cost and complexity
Installing additional FSCTs just for a short cable tail protection for the transformer adds extra equipment, wiring, and commissioning effort. If the existing transformer protection is deemed adequate for the cable tail, this additional cost might be considered unnecessary.
Coordination Challenges
Adding more protection elements (like FSCTs) requires careful coordination to ensure proper tripping and avoid nuisance tripping.4.
Assumptions about Cable Tail Faults
Lower Probability of Cable Tail Faults
The assumption might be that the probability of a fault within the short cable tail connection to the transformer is relatively low, especially if high-quality cable and sealing ends are used and installation practices are rigorous. A cable fault, if it occurs, may likely be a phase to phase or ground fault that the transformer differential protection will detect.
Manufacturing Quality
Cable sealing ends are designed to withstand high voltages and currents. It's assumed that these sealing ends are manufactured to a high quality, thereby minimizing the risk of failure.5.
Reliance on Existing Protection Schemes
Differential Protection Dominance
Differential protection is typically the primary protection for power transformers. It detects faults by comparing current entering and leaving the transformer. While it primarily focuses on internal faults, it will detect faults in the cable tail connection if they are significant enough.
REF Protection
Restricted Earth Fault (REF) protection is highly sensitive to earth faults within the transformer winding. It might also offer some limited protection for earth faults in the cable tail close to the transformer.6.
Cable Sealing Ends
Yes, the use of cable sealing ends contributes to the decision. These sealing ends are designed to provide reliable insulation and protection at the cable termination points. They are typically tested to withstand high voltages and currents, minimizing the risk of flashover or breakdown in normal operating conditions. These sealing ends also provide a barrier against environmental factors such as moisture, dust, and pollution, which can degrade the insulation and lead to faults over time.
Why the Assumption Might Need Re-Evaluating
While the above reasons provide a rationale, the difference in approach should be critically assessed based on:
Cable Type and Quality
If the cable tails are of a type that's known to be less reliable or more prone to failure, dedicated protection should be considered.
Conduit Protection
If cable tails are not installed in protected conduits, but are subject to physical damage, a dedicated protection scheme is recommended.
Operating Experience
If the substation has experienced cable tail faults in the past, adding FSCTs for the transformer connection is justified.
Importance of the Transformer
For critical transformers, the added protection might be worth the cost and complexity, regardless of the perceived risk.*
Grid Codes and Standards
Local grid codes and standards might have specific requirements regarding cable tail protection. Ensure the installation complies with these regulations.
In conclusion:
The decision to use FSCTs on the OHL feeder but not the transformer cable tail likely stems from a combination of factors, including the greater exposure of OHLs to external faults, the primary focus on internal fault detection for transformers, and cost considerations. The robustness of the transformer protection scheme (differential, REF, overcurrent) also plays a role, along with assumptions about the reliability of the cable tail installation and sealing ends.However, it's essential to re-evaluate this approach based on the specific conditions, operating history, and criticality of the transformer. A risk assessment, considering the likelihood and consequences of cable tail faults, should be conducted to determine if additional protection is warranted. It is also important to consider local grid codes and standards to ensure the installation complies with these regulations. Flag for review