User: ako, Location: Los angeles, CA
Asked on: Thursday, February 13, 2025 at 3:07 pm EST
Answered on: Thursday, March 6, 2025 at 8:37 am EST
Question: Hi,How are you? I hope you can help me clarify the requirement from NEC if there is any.The job site is in California. Currently, the owner is building a two-story unit at the back of the property. Back side is an alley for parking access. The "main" structure in the front is a triplex with 3 meters.The power line (Service Feed) is from the back to this triplex. Because the new structure is at the back and it is 2-story tall, it will block the existing overhead Service Feed to the triplex in the front.The final plan is to install a 400-amp panel with 5 meters at the back. The overhead Service Feed will be connect at the back, and then install an underground line with PVC conduit, to feed the front.The issue here is What do we in the mean time (temperory). The existing Service Feed need to move to one side of a 200 amp temperoary pol/box, away from the building foot print, so the general contractor/framer can build the new unit. After moving the SF to the temp. pole, How do I reconnect the power back to the main unit? Can I run a new overhead wire from this temp power pole back to the old weatherhead location? Or I need to DO it underground even if it is temperory?Well, obivously, this new line will be a branch circuit from this temp. power panel, meaning I will run it AFTER the meter.I guess, there are a few issues that I am not sure. Given this case scenrio, there are a few questions.1.) Can a branch circuit run on overhead, WITH the same pole of the service Feed? So, there will be 2 different weatherhead on the same pole, but will be on different drection.2.) If so, what is the minimum distance from this Service Feed wire to this branch circuit wires feed ? yes... We will use outdoor rated SER wiresl3.) Can I use PVC conduit on this temp branch circuit? Will it be strong strong enough to support the "pull-strength" from the wires?Please let me know what you think.Thanks in advance
Okay, this is a common situation, and you're right to be concerned about complying with the NEC (National Electrical Code) and local requirements in California. Let's break down the scenario and address your questions.
General Considerations
NEC is a Minimum Standard
The NEC provides minimum safety requirements. Local jurisdictions (city, county) always have the authority to amend or add to the NEC. You must check with your local building department or electrical inspector. California also has its own specific amendments to the NEC.
Permitting is Essential
This temporary and permanent work requires a permit and inspection. Doing otherwise is inviting trouble (fines, delays, potential safety hazards). The inspector is the final authority on interpretations.
Coordination
Communicate clearly with the utility company (PG&E, Southern California Edison, etc.) and your local inspector throughout this process. They will have specific requirements for service drops, meter locations, and grounding.
Licensed Electrician
You stated "I will run it after the meter" indicating the likelihood of you doing the electrical work. As you know, most electrical work requires to be done by licensed contractors.
Addressing Your Specific Questions
Can a branch circuit run overhead on the same pole as the service feed? Potentially, but HIGHLY unlikely without special considerations/requirements. NEC Article 230 (Services) and Article 225 (Outside Branch Circuits and Feeders) cover this. The major concern is clearance and separation. You can't simply run a branch circuit alongside a service drop without maintaining proper clearances. The NEC requires separation between service conductors and other conductors, especially branch circuits. Think about the possibility of a fault on either the service or the branch circuit. The main concern is safety.2. If so, what is the minimum distance from this service feed wire to this branch circuit wires feed? This is where it gets very specific and depends on voltage, conductor type, and location. Consult NEC Articles 230 and 225. Table 230.51(C) and the notes accompanying it are relevant. Also refer to 225.26 and 225.
27. In general, you're looking at several feet of separation, and possibly even requiring a physical barrier between the service and branch circuit conductors. Think several feet, not inches. In reality, the clearances are often so stringent that it's simply impractical to run the branch circuit on the same pole as the service. That is why there are requirements for "service mast" and "meter pole" to protect the service conductors.3. Can I use PVC conduit on this temp branch circuit? Will it be strong enough to support the "pull-strength" from the wires? Yes, you can use PVC conduit for the temporary branch circuit, but you MUST support it properly. PVC conduit can be used overhead, but it requires very careful support to prevent sagging or breakage. Use appropriate support straps/clamps at regular intervals (check the NEC and manufacturer's instructions for spacing requirements). These intervals will be considerably shorter than for rigid metal conduit. The pulling strength of the wires is not a primary concern if you are pulling the wires through the conduit according to code. Consider using a stronger conduit type like rigid metal (RMC) or intermediate metal (IMC) for overhead runs, especially in temporary situations. This will give you a more robust and less sag-prone installation.
Recommended Approach (Temporary Setup)
Consult with the Utility Company
The utility must be involved in disconnecting and reconnecting the service drop. They will have specific requirements for the temporary pole and its location.2.
Temporary Service Pole (Properly Installed)
The temporary pole must be properly sized and installed to meet the load requirements of the triplex. It needs to be firmly grounded. Use a weatherproof disconnect at the pole.3.
Underground is Safest (and Often Required)
The safest and most code-compliant approach is to run an underground temporary feeder from the temporary service pole to the existing triplex. This eliminates clearance issues.4.
If Overhead is Absolutely Required
If underground is not possible, and the inspector approves an overhead temporary feeder: Use a separate pole for the temporary feeder from the temporary service disconnect to the triplex. Do not try to share the same pole as the service drop. Maintain all required clearances from buildings, ground, and other conductors. Use appropriately sized and rated conductors and conduit (RMC or IMC is recommended). Support the conduit at very frequent intervals to prevent sagging.5.
Grounding
Ensure proper grounding at both the temporary service pole and the triplex.
Important Considerations
California Amendments
Research California-specific amendments to the NEC related to services, feeders, and temporary wiring.
Working Space
Provide adequate working space around the temporary service disconnect and meter.
Accessibility
Make sure the meter and disconnect are readily accessible.
Weatherproof
All temporary wiring and equipment must be weatherproof.
Temporary Wiring Time Limits
The NEC limits the duration of temporary wiring installations (see Article 590). Plan the permanent installation as quickly as possible.
In summary: Running a branch circuit on the same pole as the service drop is highly problematic from a code compliance and safety perspective. Underground is almost always the better option for temporary feeders. Contact the utility company and get a permit before starting any work. Coordinate closely with the electrical inspector to ensure your temporary and permanent installations meet all requirements. Flag for review