User: marcosgue, Location: Tampa
Asked on: Friday, February 14, 2025 at 8:00 pm EST
Answered on: Thursday, March 6, 2025 at 8:41 am EST
Question: Is clear the two conditions in 517.13 that in Patient Cares Spaces, including OR, the use of wiring method shall be qualify as equipment grounding conductor and beside that every circuit from the isolated panel shall be run with green wire type equipment grounding conductor which is connected to grounding terminals of receptacles, metal boxes, device boxes.The fact is the PM assistant was doing grounding test and mandate to disconnect the ground pigtail saying that specifically in OR is no allow to bond the metal box with the equipment grounding conductor running with the circuits originated in the Iso Panel.I believe he's wrong and violate 517.13b.My question is why to bond the metal boxes to provide an effective ground fault current path if there's no neutral in the Isolate power system and is not allow the operation of overcurrent device.Any input and clarification is appreciated.Thanks in advance
You are correct. The PM assistant's assertion that metal boxes in an OR should NOT be bonded to the equipment grounding conductor (EGC) originating from the isolated power panel is almost certainly incorrect and likely a violation of NEC 517.13(B).Here's a breakdown of why and addressing your specific question
Understanding the Requirements - 517.13(B) and Beyond
517.13(A) & (B): General Requirements
These sections of the NEC, including in operating rooms and critical care areas,
mandate a reliable equipment grounding system. Acceptable Wiring Methods
The wiring methods must qualify as an equipment grounding conductor, AND...
Supplemental Grounding Wire
Each branch circuit supplying patient care equipment must include an insulated copper equipment grounding conductor (green or green with yellow stripe). This EGC is connected to the grounding terminals of receptacles, metal boxes, and device enclosures.
Why 517.13(B) Exists
The purpose of a supplemental EGC is to provide a low-impedance path for fault current. This is critical for personnel safety.
Important: Isolated Power Systems are NOT a Waiver
The presence of an isolated power system does not negate the requirement for a properly installed and bonded equipment grounding system. The isolated power system adds a layer of safety, but it doesn't replace the fundamental grounding requirements.
517.19 Isolated Power Systems (Further Clarification)
This section describes the operation of the Isolated Power System
Addressing Your Specific Question: Why Bond Metal Boxes in an Isolated Power System?
Even though an isolated power system is designed to limit the initial fault current and prevent the immediate operation of overcurrent devices, there are several crucial reasons why bonding metal boxes is still essential:1. First Fault Scenario
An isolated power system doesn't eliminate ground faults. It limits the current of the first ground fault. Without a properly bonded grounding system, the enclosure of a device with a first fault will be elevated to a voltage level. This scenario poses a significant shock hazard to anyone who touches the faulty enclosure and a grounded surface (like the operating table).2.
Second Fault = BOLT OF LIGHTNING
While a single fault in an isolated power system won't trip a breaker, a second fault on a different conductor will result in a very large current. The grounding system is vital to provide a low-impedance path for this second fault current, ensuring the overcurrent protection device will operate quickly. Without proper bonding, the high fault current can flow through unintended and potentially dangerous paths.3.
Electrostatic Discharge (ESD)
Properly bonding metal boxes helps to minimize the build-up of static electricity. ESD can be a concern in operating rooms, especially with sensitive electronic equipment.4.
Code Compliance is Mandatory
NEC 517.13(B) doesn't provide exceptions for isolated power systems. You must follow the code.
Why the PM Assistant is (Almost Certainly) Wrong
Disconnecting the EGC pigtails from the metal boxes is a dangerous practice and almost certainly violates NEC 517.13(B). This creates a situation where the metal boxes are not properly grounded, increasing the risk of electrical shock and creating an unreliable fault current path. His reasoning is flawed, and it's crucial to correct this misunderstanding immediately.
What You Should Do1. Document Everything
Document the PM assistant's instructions in writing and the potential safety concerns.2.
Escalate
Escalate this issue to someone with the authority to overrule the PM assistant – a senior engineer, the facility's electrical safety officer, or the hospital's administration. Explain the NEC requirements and the potential safety hazards.3.
Consult with a Qualified Electrical Engineer
If there's any doubt, consult with a qualified electrical engineer experienced in healthcare facilities. They can provide a definitive interpretation of the code and ensure the grounding system is compliant and safe.4.
Insist on Corrective Action
Insist that the metal boxes be properly bonded to the EGC. This may involve re-terminating the ground pigtails.5.
Formal Inspection: Request a formal electrical inspection and evaluation from an independent, qualified authority.In conclusion, you are correct in your assessment. The PM assistant's instruction to disconnect the EGC pigtails from metal boxes in the OR is likely a violation of the NEC and creates a dangerous situation. Immediate corrective action is required. Flag for review