Question: Our facility is installing new out door MV switchgear consisting of several sections joined together. The last switch gear section contains the batteries, battery charger, an AC load panel and a DC bus distribution panel. The enclosure is large enough to walk into. The enclosure opens from both sides. The batteries, installed on a 3 tier rack, consist of 92 wet cell NiCad cells in series that creates a 130V, 175Ah bus to power the protective relays, the trip and close motors and all the associated controls. Several issue have come up about this system and the enclosure.1. Since the enclosure can be entered and the front of the battery rack is accessible while inside, does the working space requirements of 110.26 apply? Currently there is only 18" of clearance between the battery bank and the side wall of the enclosure. From one side of the enclosure with a door open, there is plenty of clearance if the perspective is from the outside of the enclosure. It is when the perspective is from a worker standing inside the enclosure that the working space is obstructed between the battery bank the the enclosure side wall. A majority of the battery maintenance would need to be performed in the area with the 18" of clearance. Is this in violation of the working space requirements?2. Should we be concerned about hydrogen accumulation? A simple vent exists near the top, on one side of the enclosure opposite the battery bank. The batteries are not below this vent. Any hydrogen would accumulate in the ceiling pockets and can also migrate to the adjoined medium voltage sections. I understand that under normal conditions, the hydrogen emission is somewhat low. However, I am concerned about the abnormal conditions such as thermal runaway, and charger malfunction. There is no hydrogen detection sensor or powered ventilation.3. Should we be concerned with high temperatures? There are no environmental controls on this outdoor enclosure, in direct sun, and summer time temperatures can reach +110F. The maximum battery temperature rating is 124F. I would expect the inside of this enclosure to greatly exceed this maximum.
Okay, let's break down these issues related to your MV switchgear enclosure and associated battery system. It's good you're addressing these concerns proactively.1. Working Space Requirements (NEC 110.26) Yes, NEC 110.26 likely applies. The key phrase in 110.26 is "examination, adjustment, servicing, and maintenance." You've already identified that battery maintenance will need to be performed in the 18" space. Why it's likely a violation
110.26 (A)(1) states: "Sufficient access and working space shall be provided about all electrical equipment to permit ready and safe operation and maintenance of such equipment." While the nominal voltage might be 130V DC, the actual voltage from the battery bank to ground could be higher (especially if the battery bank has a center tap or other grounded connection). The NEC would consider this an insulated voltage. Even though the DC voltage is low, 110.26 applies. The 18" clearance is highly unlikely to meet the requirements of Table 110.26(A)(1). You need to determine the specific voltage and the conditions (exposed live parts on one or both sides of the working space, or grounded parts). The relevant columns in the table are then selected to see the required distance. Regardless of the voltage of the battery bank, the DC power distribution panel and AC distribution panel will have voltage levels that easily invoke the table for required clearance.
Considerations
"Dedicated Equipment Space" (NEC 110.26(E)) While often applied to indoor equipment, the intent is to prevent obstructions above or below the equipment. The limited space here could be argued to impede the dedicated electrical space needed for safe work. AHJ (Authority Having Jurisdiction)
Ultimately, the local inspector or AHJ makes the final determination. Be prepared to discuss your rationale and potential solutions.
Manufacturer's Recommendations
Consult the switchgear and battery rack manufacturer's documentation. They may have specific clearance requirements that exceed NEC minimums.
Solutions
Relocate the battery rack
Moving it further away from the side wall is the ideal solution, if possible.
Modify the enclosure
Expanding the enclosure to provide adequate working space would address the issue.
Rearrange equipment
Can the battery charger, DC panel, or AC panel be relocated within the enclosure to improve the battery rack working space?
Restricted Access (Last Resort)
Implement procedures and physical barriers to prevent personnel from entering the area with inadequate clearance while the batteries are energized. This is a difficult solution to enforce and doesn't eliminate the problem, but might be a temporary measure while other solutions are implemented.
2. Hydrogen Accumulation Concern is Valid
NiCad batteries do produce hydrogen during charging and especially during overcharging or fault conditions. Hydrogen is lighter than air and highly flammable/explosive.
The Vent Alone is Likely Insufficient
Passive Ventilation Problems
A single vent near the top may not provide adequate air exchange, especially in a sealed enclosure. Stagnant air pockets can still form.
Location
The vent's location on the side opposite the batteries is a concern. Hydrogen will tend to accumulate at the highest point above the batteries before it diffuses to the vent.
Air Flow
Natural convection alone may not be enough, particularly on hot, still days.
Potential Hazards
Explosion
A buildup of hydrogen could lead to an explosion if ignited by a spark from the switchgear, charger, or even static electricity.
Corrosion
Hydrogen can contribute to corrosion of electrical components.
Migration
Hydrogen can migrate to adjacent switchgear sections through conduit openings, seams, or other gaps, increasing the risk of an explosion there.
Recommendations
Forced Ventilation
Install a properly sized exhaust fan system with ducting to draw air from the highest point above the batteries and vent it safely to the outside. The fan should be rated for hazardous locations if there's a possibility of explosive atmospheres (check with an electrical engineer knowledgeable in hazardous locations). Interlock the fan with the battery charger so it operates whenever the charger is on.
Hydrogen Detection
Consider a hydrogen detector with an alarm and automatic shutdown of the battery charger in the event of high hydrogen concentration. This is especially important if you can't guarantee adequate ventilation.
Sealing
Seal any openings between the battery compartment and adjacent switchgear sections to prevent hydrogen migration.
Explosion-Proof Considerations
Depending on the risk assessment and potential hydrogen accumulation, you might need to consider explosion-proof (Class 1, Division 2) components and wiring methods within the battery compartment. Consult a qualified electrical engineer experienced in hazardous locations.
Check with Battery Manufacturer
The battery manufacturer should provide specific ventilation recommendations based on the battery type, size, and charging characteristics.
Hazardous Area Classification
It's worth considering whether a hazardous area classification (NEC Article 500-505) applies to the battery enclosure. An assessment by a qualified person is recommended.
3. High Temperatures Valid Concern
Exceeding the battery's maximum temperature will significantly reduce its lifespan and performance and can lead to thermal runaway.
Consequences
Reduced Battery Life
Elevated temperatures accelerate the degradation of battery components.
Reduced Capacity
The available capacity of the battery will decrease at high temperatures.
Thermal Runaway
In extreme cases, high temperatures can trigger thermal runaway, a dangerous condition where the battery overheats and can catch fire or explode.
Recommendations
Temperature Monitoring
Install a temperature sensor inside the enclosure, near the batteries, to monitor the temperature. Connect this to an alarm system.
Shading
Provide shading for the enclosure to reduce direct sunlight exposure. A simple roof or awning can make a big difference.
Ventilation
Improved ventilation can help to reduce the temperature inside the enclosure. Forced ventilation (with an exhaust fan) is the most effective. Ensure the incoming air is cooler than the air inside the enclosure.
Thermal Management System
If temperatures are consistently too high, consider a dedicated cooling system (air conditioner or thermoelectric cooler) designed for outdoor enclosures. Choose a system rated for the expected ambient temperatures.
Battery Type
If possible, consider switching to a battery technology with a higher operating temperature range (though this may not be feasible given your existing system).
Derating
Consult the battery manufacturer about derating the battery's charging and discharging parameters at high temperatures. This can help to extend battery life, but it will also reduce the available capacity.
Important Considerations (General)
Consult Qualified Professionals
This is a complex situation involving electrical safety, hazardous materials, and environmental factors. Engage a qualified electrical engineer, a hazardous location specialist, and battery system experts to perform a thorough assessment and develop a comprehensive solution.
Documentation
Keep detailed records of your assessments, modifications, and maintenance procedures.*
Training: Ensure personnel who work on the battery system are properly trained in safe operating procedures, emergency response, and the hazards associated with NiCad batteries.By addressing these issues proactively, you can significantly improve the safety and reliability of your MV switchgear and battery system. Flag for review