Topic: UL508A VFD fuse rounding

User: JovialBulge, Location: New England

Asked on: Monday, February 17, 2025 at 10:42 am EST
Answered on: Thursday, March 6, 2025 at 8:45 am EST

Question: If I have a VFD that is rated HP=25.0, Output Amps=37.0, Max Input Amps=33.7, 480VAC and I am getting just a bit fuzzy on the Class J fuse sizing for the line side of the drive. The 25HP motor that the drive is controlling has a nameplate FLA of 29.50A @ 480VAC, using table 50.1 in the UL document that motor has an FLA of 34A. It's my understanding that I need to use the values within table 50.1 when doing any FLA calculations for the main incoming disconnect for the panel overall, however does that rule apply here as well?In this case the manufacturers table shows a Min and Max fuse rating for non-UL applications, 45A and 70A respectively. Then they give a MAX rating for a fuse in a UL application of 70A. With my max input amps to the drive being 33.7, should I be using 33.7 x 1.25 = 42.125A and then rounding down to 42A and choosing the next common size of 45A on the fuse? Should I be using 33.7 x 1.50 = 50.55A and rounding up to 51A and then choosing the next common size of 60A on the fuse?I know that the minimum ampacity of the wires feeding VFD is 125% of the rated input current of the drive as per 430.122(A).First I read...5.2 in the UL508A doc "For calculations involving amperes, calculations resulting in a fraction of less than 0.5 shall be rounded down to the next whole number. Calculations resulting in a fraction of 0.5 or more shall be rounded up to the next whole number."Then I read...31.3.2 The branch circuit protection for a single-motor circuit provided with a variable-speed drive shall be of the type and size specified by the manufacturer's instructions provided with the drive. Lower sizes, of the same type, can be used. When the instructions do not specify the type and size, a branch-circuit fuse or inverse-time circuit breaker shall be used and shall be sized in accordance with 31.3.1(a) based upon the full-load motor output current rating of the drive.

Okay, let's break down the VFD fuse sizing and clarify the code requirements. You're right to be careful; proper overcurrent protection is critical.

Understanding the Conflicting Information

The situation is tricky because you have multiple sources of information: NEC (National Electrical Code)

The NEC is the governing code, but it relies on UL standards for product listings.


UL 508A (Standard for Industrial Control Panels)

This standard provides construction and safety guidelines for control panels, including fuse sizing.

VFD Manufacturer's Instructions

These instructions are paramount, as they are based on the specific design and testing of the VFD.


Motor Nameplate & UL 50.1

You've pointed out that for overall panel calculations, UL 50.1 dictates using the listed FLA for motor sizing, and it may be different from the motor nameplate.

Here's the recommended approach


Prioritize the VFD Manufacturer's Instructions

NEC 430.52(C)(1) generally allows sizing overcurrent protective devices (OCPDs) according to the manufacturer's instructions. Also, UL 508A section 31.
3.2 you mentioned emphasizes this. Therefore, start with the manufacturer's recommendations. In your case, the manufacturer provides a MAX fuse rating for UL applications of 70A. They also provide a range for non-UL applications.2.


Confirm the Listing

You're using the VFD in a UL-listed assembly (presumably an industrial control panel). This means you

must
adhere to the limitations of the UL listing and cannot exceed the manufacturer's maximum fuse rating for UL applications.3. Verify Adequate Protection

Even if the manufacturer's instructions allow for a larger fuse, it's crucial to ensure the fuse size still provides adequate protection for the VFD's components and wiring. This is where your calculations come in.4.

Calculate Based on VFD Input Current

Use the VFD's
maximum input current (33.7A) as the basis for your calculation, not the motor's nameplate FLA or the UL 50.1 table value. NEC 430.122(A) requires the conductors feeding the VFD to have an ampacity of at least 125% of the rated input current of the drive. This indirectly informs the fuse sizing. Calculate 125% of 33.7A: 33.7A 1.25 = 42.125A5.

Account for Starting and Overload

VFDs typically handle motor starting in a controlled manner, so the high inrush currents associated with across-the-line motor starting are mitigated. However, you still need to consider potential overload conditions. The 125% factor already provides some allowance for this.6.

Choose the Fuse

Your calculation of 42.125A suggests a fuse close to that value. Since you must meet the manufacturers listing of a

MAX 70A fuse
, and the calculated value is close to a common 45A fuse that would be the first one to select. HOWEVER, considering the FLA on the motor which is very close to the Output Amp Rating of the drive, selecting the 45A fuse may cause nuisance tripping. It may be best to select the next common fuse size of 50A or 60A.

Therefore, the most likely scenario is the following

You can use a Class J fuse up to a maximum of 70A, as recommended by the manufacturer. Given your calculated value of 42.125A, a fuse in the 45A-60A range would provide adequate protection, and it is acceptable to use a fuse smaller than 70A based on your discretion. A good solution here would be a 50A or 60A fuse.

Addressing Your Specific Questions



UL 50.1 vs. VFD Input Current

UL 50.1 is primarily for sizing the overall panel's main disconnect and conductors feeding
multiple loads, including motors. When dealing specifically with the VFD input circuit, use the VFD's input current rating for protection.

125% vs. 150%

The 125% factor comes from NEC 430.122(A) for conductor sizing related to the VFD. The 150% factor is for general motor branch-circuit short-circuit and ground-fault protection (NEC 430.52), but it's typically not the primary consideration when you have manufacturer's instructions for the VFD.

Rounding

While UL 508A 5.2 addresses rounding in general calculations, the overriding factor is staying within the manufacturer's listed limits.

Important Considerations



Class J Fuses

You've correctly identified Class J fuses. They are a common and suitable choice for VFD protection due to their high interrupting rating and current-limiting characteristics.

Short-Circuit Current Rating (SCCR)

Ensure that the VFD's SCCR is sufficient for the available fault current at its installation location. The fuse contributes to the overall SCCR of the VFD system.


Upstream Protection

Consider the coordination of the VFD's fuse with any upstream overcurrent devices (e.g., a main panel breaker).

Documentation

Always document your fuse selection rationale, including the manufacturer's instructions, your calculations, and the specific code sections you followed.


Coordination Study

In critical applications or where you have complex distribution systems, a formal coordination study may be necessary to ensure optimal protection and minimize nuisance tripping.

Disclaimer:
Always consult with a qualified electrical engineer to ensure compliance with all applicable codes and regulations. The information provided here is for educational purposes only. Flag for review