Question: Can I install a 125 amp panel-board with 125 amp main CB to underground #1/0 aluminum service conductors?
No, you generally cannot install a 125 amp panelboard with a 125 amp main circuit breaker using #1/0 aluminum service conductors in most residential applications. Here's why: NEC Ampacity Rules
The National Electrical Code (NEC) dictates the ampacity (current-carrying capacity) of conductors. #1/0 Aluminum conductors typically have an ampacity of 100 amps (based on the 75°C column of NEC Table 310.16, which is commonly used for residential services). While some tables allow a higher ampacity under specific conditions, those often don't apply to residential services.
Overcurrent Protection
The overcurrent protection (the main circuit breaker) must be sized to protect the conductors. You can't have a 125 amp breaker protecting a wire that's only rated for 100 amps. It's a safety hazard.
Service Entrance Conductor Sizing
The service entrance conductors must be sized to carry the calculated load of the dwelling, but in no case shall the conductors have an ampacity less than the rating of the main breaker.
Larger Conductor Required
To use a 125 amp breaker, you need a larger conductor. Generally, you would need #2/0 Aluminum. It's very important to check the NEC and local codes for your specific installation.
Important Considerations
Local Codes
Local building codes might have additional or more restrictive requirements. Always check with your local electrical inspector.
Calculated Load
The calculated load of your dwelling is critical. It's possible your dwelling's load is less than 125 amps, but you still can't use a 125 amp breaker with #1/0 aluminum. You might be able to use a smaller breaker if your calculated load permits it, but you are still required to use the appropriate sized conductor for the breaker.*
Voltage Drop
Consider voltage drop over long conductor runs. Larger conductors minimize voltage drop.
In summary, to use a 125 amp main breaker, you will need to upgrade the conductor to a size suitable for a 125 amp rated service. Consult with a qualified electrician for proper sizing based on your specific situation and local code requirements. Flag for review