Topic: Transfer switch grounding/bonding

User: BoMaFl, Location: Pittsburgh

Asked on: Wednesday, February 19, 2025 at 6:17 pm EST
Answered on: Thursday, March 6, 2025 at 8:51 am EST

Question: Existing setup is 120/208, 4 500mcm conductors in 3" pvc from meter ~100ft to mdp. Meter is grounded to building steel. Mdp has ground rod. We are looking to install a transfer switch next to the meter and run the service through the transfer switch.Since the transfer switch will become the first means of disconnect, the ground and neutral will be bonded there, and the mdp will need to have grounds/neutrals unbonded.1. For the transfer switch, will a ground rod be needed, or can building steel be used?2. For the mdp, can the existing ground rod be used, or will a new grounding conductor need to be ran from the transfer switch? If so, can it be ran outside the pvc?

Okay, let's break down the grounding and bonding requirements for this service change. This is a common scenario when adding a transfer switch, and it's important to get it right for safety and code compliance.

Understanding the Requirements

The National Electrical Code (NEC) dictates how to properly ground and bond electrical systems. The key principles here are: Service Equipment Bonding

The neutral conductor
must be bonded to the grounding electrode system at the service equipment. This is the only place where this bond should occur in the system (unless dealing with separately derived systems further downstream).

Grounding Electrode System

The grounding electrode system (GES) must be connected to the service equipment and must consist of specific electrodes outlined in the NEC.

Equipment Grounding Conductor

Equipment grounding conductors (EGCs) are run with the circuit conductors to provide a low-impedance fault path back to the source (the transformer supplying the service). This allows overcurrent devices (breakers or fuses) to operate quickly and clear a fault.

Your Specific Situation
1. Transfer Switch Grounding



Building Steel is Acceptable

You can use the existing building steel as your grounding electrode at the transfer switch (assuming it meets the requirements of the NEC as a qualified grounding electrode – see below). You do not need a ground rod at the transfer switch if the building steel is properly connected and qualifies as a grounding electrode.

Important Considerations for Building Steel



Continuous to Earth

The building steel must be effectively grounded (connected to earth). This usually means it's physically connected to the earth or has a low-impedance path to earth.

NEC Requirements

Refer to NEC Article 250 (specifically 250.52) for the specific requirements for building steel to qualify as a grounding electrode. It generally needs to be a substantial steel frame, in direct contact with the earth for a certain distance, or connected to concrete encased electrode.


If Building Steel Does NOT Qualify

If the building steel does not meet the NEC requirements for a grounding electrode, you will need to install another type of grounding electrode. This could be:

Ground Rods

At least two ground rods, spaced at least 6 feet apart.


Concrete-Encased Electrode (Ufer Ground)

If available, often the most effective option.

Ground Ring

A bare copper conductor encircling the building in direct contact with the earth.2.

Main Distribution Panel (MDP)



Neutral-Ground Separation

As you stated, absolutely do not bond the neutral and ground at the MDP once the transfer switch becomes the service equipment. The neutral and ground conductors must be kept separate.

Existing Ground Rod

The existing ground rod at the MDP
can be used, but it must be connected back to the grounding electrode system at the transfer switch. You cannot just leave it disconnected.

Grounding Electrode Conductor

A grounding electrode conductor (GEC) must be run from the MDP back to the transfer switch to connect the ground rod to the grounding electrode system.

Running the GEC



NEC Preferred Method

The NEC prefers that the grounding electrode conductor be installed inside the same raceway (conduit) as the circuit conductors whenever practical. However, it is permitted to run the GEC separately from the circuit conductors.

If Running Outside the PVC

If you run the GEC outside the PVC, it
must be:

Protected from Physical Damage

NEC requires the grounding electrode conductor to be securely fastened to the surface on which it is carried.

Continuous

No splices are allowed in the GEC unless they are made by irreversible compression-type connectors listed for the purpose or by the exothermic welding process.


Sized Correctly

Refer to NEC Table 250.66 to determine the proper size of the grounding electrode conductor based on the size of the service entrance conductors (your 500 kcmil conductors). For 500 kcmil copper service conductors, your copper GEC to the ground rod would generally need to be at least #6 AWG copper.

Summary of actions
1. Install Transfer switch next to meter2. Move existing service entrance conductors to transfer switch3. Bond neutral to ground at transfer switch4. Verify building steel meets NEC requirements, if not install 2 ground rods5. Run new conductors from transfer switch to MDP with grounds and neutrals isolated.
6. Run #6 or better grounding electrode conductor from transfer switch to ground rod at MDP.

Important Considerations and Recommendations Local AHJ (Authority Having Jurisdiction)

Always consult with and get approval from your local electrical inspector before making any changes to your electrical service. They have the final say on what is compliant in your area.


Licensed Electrician

It is highly recommended that you hire a qualified, licensed electrician to perform this work. Working on service equipment is dangerous and requires specialized knowledge.

NEC 250

Thoroughly review NEC Article 250 for all the details on grounding and bonding.


Disconnect Before Work

Ensure the power is completely disconnected from the service before beginning any work.*

Overcurrent Protection

Be mindful of overcurrent protection requirements for the generator connection to the transfer switch.

Disclaimer:
This information is for general guidance only and should not be considered a substitute for professional electrical advice or adherence to local codes and regulations. Flag for review