User: skorpioskorpio, Location: Georgia
Asked on: Friday, February 21, 2025 at 2:40 pm EST
Answered on: Thursday, March 6, 2025 at 8:55 am EST
Question: I had my Generac generator installed by a generator company, and something seems very wrong with their installation. It is using a 16 space/24 circuit sub-panel layout fed from a 100 amp breaker from the main panel (not a whole house switch). I noticed that there is only a single neutral/ground bar in the switch panel, which they have connected both neutrals and grounds to. Why would this be? Shouldn't there be separate ground and neutral buses? The panel uses Siemens guts and there is a place to snap in a 2nd bus rail, but it isn't there, just the one. There is also no place for a can mounted bar, just the snap in spot where on a regular Siemens panel would have a secondary neutral bar. Does this switch not follow the rules of a sub panel where ground and neutral should be unbonded?The generator itself has a feed breaker, and the switch has no manual disconnect (it is fused though), I don't see anyway, or any scenario where this switch could be viewed as the first point of disconnect where neutral/ground bonding would be appropriate. It just seems very wrong. Seems like there should be a 2nd bar to separate the grounds from the neutrals and that the ground bar should then be bonded to the can, right?
You're absolutely right to be concerned. What you're describing sounds like a code violation and potentially dangerous. Here's a breakdown of why it's wrong and what you should do
Why Your Concerns are Valid
Neutral-Ground Bonding in a Subpanel
The fundamental principle you're questioning is correct. In a subpanel (fed from a main panel), the neutral and ground should
not be bonded. Here's why: Parallel Neutral Paths
When neutral and ground are bonded in the subpanel, you create a parallel path for neutral current to flow through the ground wire. This can cause:
Stray Voltage
Voltage on the ground wires, which can be a shock hazard.
Nuisance Tripping
GFCI breakers may trip randomly because they detect current imbalance.
Overheating
Ground wires are typically smaller than neutral wires and not designed to carry significant current. They could overheat under sustained neutral load.
The Only Acceptable Bond
The only place where the neutral and ground should be bonded is at the service entrance (usually the main panel). This ensures a single point for fault current to return to the source (the transformer).
Single Neutral/Ground Bar
The fact that the subpanel only has one bar and both neutrals and grounds are connected to it is a clear indication of improper wiring.
No Disconnect
Your description of the fused switch without a disconnect is unusual and potentially non-compliant. While a fused switch can provide overcurrent protection, it doesn't provide a readily accessible disconnect to safely isolate the subpanel for maintenance or emergencies. A manual disconnect is almost always required for a subpanel fed from a generator.
Generator Doesn't Change the Rule
Having a feed breaker on the generator itself does not change the fact that neutral and ground need to be isolated in a subpanel. The generator breaker is for overcurrent protection, not for establishing a ground-neutral bond for the entire system.
Why It's Done Wrong (Possible Reasons, Not Excuses) Ignorance/Incompetence
Sadly, some installers may not fully understand electrical code requirements.
Laziness/Cutting Corners
Installing a second bus bar and properly separating grounds and neutrals takes extra time and effort.
Misunderstanding Generator Requirements
Sometimes installers misunderstand the difference between a permanently installed generator system and a portable generator setup (where bonding is sometimes different).
What You MUST Do
IMMEDIATE ACTION: Turn off the breaker feeding the subpanel in the main panel to avoid any potential safety hazards. Do not use the generator.2. Contact the Generator Company Immediately
Call the company that installed the generator and demand that they rectify the situation immediately. Explain that the neutral and ground are improperly bonded in the subpanel and that this is a code violation and safety hazard.3.
Document Everything
Keep detailed records of all communications with the company, including dates, times, names of people you spoke with, and what was discussed. Take photographs and videos of the existing wiring.4.
Independent Inspection
If the company is unwilling to fix the problem promptly and correctly, contact a licensed and reputable electrician unaffiliated with the original company to inspect the installation. Get a written report detailing all the code violations and required corrections.5.
Code Enforcement
Report the issue to your local electrical inspector. They have the authority to enforce electrical codes and can order the company to correct the violations.6.
Replacement of parts and wiring. The existing panel must be fully disassembled. All wiring must be inspected for damage and re-terminated onto the proper new ground and neutral bars. Check for any screw holes that shouldn't be there.
What Needs to Be Done (The Correct Solution)1. Separate Neutral and Ground Buses
Install a Dedicated Ground Bar
The subpanel needs a separate ground bar, typically mounted to the metal enclosure.
Install a Dedicated Neutral Bar
The subpanel needs a separate neutral bar, typically isolated from the metal enclosure with insulators.2.
Wiring Corrections
Neutral Wires
Disconnect all neutral wires from the existing bar and move them to the new neutral bar.
Ground Wires
Disconnect all ground wires from the existing bar and move them to the new ground bar.
Enclosure Grounding
Connect the ground bar to the metal enclosure of the subpanel using a grounding screw or lug.
Grounding Electrode Conductor (GEC)
Run an appropriately sized grounding electrode conductor (usually copper wire) from the ground bar to the grounding electrode system (e.g., ground rods, water pipe). The size of this wire depends on the size of the service entrance conductors.3.
Disconnect Improvement (Likely Required)
Have the electrician evaluate the fused switch situation and determine if it meets code requirements for a disconnect. It may be necessary to install a separate, clearly labeled disconnect switch.
Important Considerations
Permits and Inspections
Make sure all work is done under a valid electrical permit and is inspected by a qualified electrical inspector.
Licensed Electrician
Only a licensed and experienced electrician should perform this work.
Safety First
Never attempt to work on electrical wiring unless you are fully qualified and understand the risks.
In summary, the installation you describe is not correct and potentially dangerous. Do not use the generator until the problems are corrected by a qualified electrician and inspected by a code official. Flag for review