User: alyoshak24, Location: Chicago
Asked on: Sunday, February 23, 2025 at 6:07 pm EST
Answered on: Thursday, March 6, 2025 at 8:58 am EST
Question: Hello Fellow Wizards,I have a couple of troubleshooting related questions in a paramedical environment.PROLOGUE: Client called due to hearing a "Buzzing Sound," during normal operational hours, from a utility room that houses all the load centers, electrical enclosures, disco's and pull-boxes.While this "Buzzing Sound" occurred, client noted that it did NOT have any negative impact to their medical tools, dedicated medical equipment, lighting, outlets or phone systems.When i arrived to inspect and troubleshoot noise, the manager on shift stated that the "Buzzing Sound" had randomly stopped (however, we all know that these type of problems rarely if ever resolve on their own, especially when they create a "Buzzing Sound" from any electrical enclosure). So the next thing i did was the following:A. Took note of all medical equipment in continuous use during normal work hoursB. Panel these circuits and breakers are on are labeled as follows: [ Siemens P1 Panel ][ 250A Max ] | [208/120V 3Phase] installed on May 2022. Breakers are of SiemensType HBL / IAC Rating 65KA / HACR Type SWD, 40'CB1. Total of (4x 20A SP and x1 DP 20A, all #12AWG5 stationary medical appliances/equipment that were used for 3 or more hours which are listed below:Boilers (x3) plugged into 20A gfi on dedicated circuit | 3.5-4.5 hours of continuousVacuum System DP20A on dedicated circuit and has its own disco next to it with step down transformer | 8 - 9.5 hours of continuous useDuplicator SP 20A plugged into 20A gfi on dedicated circuit | 24/7 hours of continuousThe nameplates for all the equipment calculated at 125% per NEC for continous use arrive at 18A or lower so they are sized correctly.B2. Next step was to open panel that housed all medical equipment and appliances. After inspection i noticed that 6 circuits had conductors AND breakers that were noticeably warmer than normal, like hot hot to the touch (unfortunately did not have my therm-cam) with a DP breaker (2 out of the 6) was substantially hotter than the other 4 breakers.////QUESTION(S): My question is as follows:A. Is it safe to say that "Buzzing Sound" was not a short or a ground fault, but the actual breaker(s) malfunctioning due to the continuous use of the medical equipment described above ?B. If (A) assertion is erroneous, then what else could cause the "Buzzing Sound" ? (which was made from Utility Room that housed panels, discos and pillboxes)C. if (A) assertion is agreed upon by majority consensus of wizards. then can i upsize these specific 6 circuits from 20A -> 30A and #12 - > #10AWG ?Thank you for taking the time to read my question(s), i appreciate all your help and wisdom oh great council of Sages, Priests and Wizards.
Okay, let's break down this buzzing electrical mystery and the potential solutions.
Analysis of the Situation
You've presented a classic electrical troubleshooting scenario. The "buzzing" sound is a critical clue, as is the heat on specific breakers. Here's a more detailed breakdown of each element: The Buzzing Sound
Electrical buzzing typically indicates a loose connection, vibration of components due to current flow, or arcing. While it can be related to a short or ground fault, it's less likely if the system isn't tripping breakers or experiencing a significant voltage drop.
The Heat
This is a major red flag. Breakers and conductors getting hot to the touch under normal load is a sign of resistance. Resistance generates heat. Possible causes include:
Overloading
Even though your nameplate calculations seem to indicate compliance, there might be issues with the actual load draw or how it's being applied.
Loose Connections
Anywhere along the circuit, including at the breaker, in the junction boxes, at the receptacles, and within the equipment itself. Loose connections create resistance.
Corrosion
If there's any corrosion on the conductors, terminals, or breaker contacts, that will increase resistance.
Faulty Breaker
The breaker itself could be failing internally, creating excessive resistance.
Undersized Conductors (Unlikely but possible)
Although you specified #12AWG, verifying its existence is necessary, especially if it's getting hot.
Addressing Your Questions
Let's tackle your specific questions one by one
A. Is it safe to say that "Buzzing Sound" was not a short or a ground fault, but the actual breaker(s) malfunctioning due to the continuous use of the medical equipment described above?
Not entirely safe to say. While the buzzing could be related to a failing breaker or the conductors, the fact that the breakers are noticeably warm suggests something is wrong with the load, the breakers, or the circuit wiring. It could very well be related to a high Neutral current due to harmonic distortion. The continuous use is contributing, but it's likely exacerbating an underlying issue. You can confirm this by checking the neutral conductor on each breaker and see if there's any current flowing through the conductor.
B. If (A) assertion is erroneous, then what else could cause the "Buzzing Sound" ? (which was made from Utility Room that housed panels, discos and pullboxes) Loose connections
This is the most common cause. Go through every connection in the affected circuits – breaker terminals, receptacle terminals, wire nuts in junction boxes, terminals in the equipment – and ensure they are tight and clean. (Make sure to de-energize circuits).
Arcing
This is a serious hazard. Arcing occurs when electricity jumps a gap, often due to a loose connection or damaged insulation. It produces heat, light, and a buzzing or crackling sound.
Transformer Vibration (if applicable)
The step-down transformer for the vacuum system could be vibrating due to loose mounting hardware or an internal problem.
Loose Conduit/Enclosure Components
Vibration from equipment can loosen screws or other fasteners on the electrical enclosures or conduit, creating a buzzing sound.
Harmonic Distortion
Modern electronic equipment (like some medical devices) can introduce harmonic currents into the electrical system. These harmonics can cause transformers and other equipment to vibrate and hum. If you can get your hands on a good harmonics meter, verify the system for distortion.
Neutral Current
Sometimes a circuit breaker will get warm to the touch if the Neutral is carrying excessive current, but the breakers don't trip.
C. if (A) assertion is agreed upon by majority consensus of wizards. then can i upsize these specific 6 circuits from 20A -> 30A and #12 - > #10AWG ? Absolutely NOT without a thorough investigation! Code Violation
You cannot simply upsize a breaker without ensuring the entire circuit is rated for the new amperage. This includes the wiring, receptacles (must be rated for 30A), and all associated components.
Underlying Problem
Upsizing a breaker without addressing the root cause of the overheating is a recipe for disaster. You're just masking the symptom and creating a fire hazard.
The wires are overheating for a reason; fixing that reason is critical, not just bumping up the amperage. Medical Equipment Approval
Altering circuits that supply medical equipment might require approvals from regulatory bodies or the equipment manufacturers to ensure continued safety and compliance.
Receptacle Limitations
If the receptacle that the devices are plugging into is rated at 20A, then this is a violation because these receptacles are not intended to handle 30 amps.
Recommended Troubleshooting Steps (The Wizard's Approach)1. Safety First
De-energize the affected circuits before doing any work. Use proper lockout/tagout procedures.2.
Visual Inspection
Carefully inspect all components of the affected circuits:
Breakers
Look for signs of discoloration, melting, or damage. Sniff the breakers - a burnt smell is a bad sign.
Wiring
Check for signs of damage, fraying, or overheating.
Connections
Check for loose connections at the breaker, receptacles, and junction boxes.
Equipment
Inspect the equipment for any signs of damage, overheating, or loose connections.3.
Tighten Connections
Systematically tighten all connections in the affected circuits. Use a torque screwdriver to ensure proper torque (check manufacturer specifications).4.
Measure Voltage and Current
Voltage Drop
Measure the voltage at the receptacle while the equipment is running. Excessive voltage drop indicates a problem with the circuit.
Current Draw
Use a clamp meter to measure the current draw of each piece of equipment under normal operating conditions. Compare this to the equipment's nameplate rating.
Crucially, measure the neutral current. High neutral current can be a result of non-linear loads creating harmonics.5. Breaker Testing (If Possible)
If you suspect a faulty breaker, replace it with a new breaker of the same type and rating. Observe if the new breaker also gets hot.6.
Infrared Thermography (Ideal)
If you can get access to a thermal camera, use it to scan the panels, breakers, and wiring while the equipment is running. This will quickly identify hot spots that indicate problems.7.
Neutral-Ground Voltage
Measure the voltage between the neutral and ground conductors. A reading of more than a few volts can indicate a problem with the grounding system.8.
Address Harmonic Distortion
If you suspect harmonic distortion, consider installing harmonic filters to reduce the harmonic currents in the system. If the system isn't properly grounded, you could be in trouble with medical tools.9.
Consult a Qualified Electrician
If you're not comfortable performing these tasks, or if you're unable to identify the source of the problem, consult a qualified electrician. Electrical work can be dangerous, and it's important to have it done by someone who is experienced and knowledgeable.10.
Document Everything
Keep detailed records of your troubleshooting steps, measurements, and any repairs you make.
Important Considerations for Medical Environments Safety
Patient safety is paramount. Any electrical issues in a medical facility must be addressed promptly and effectively.
Code Compliance
Ensure that all electrical work complies with the National Electrical Code (NEC) and any applicable local codes.
Grounding
Proper grounding is critical in medical facilities to minimize the risk of electrical shock and interference with sensitive equipment.
Emergency Power
Ensure that the emergency power system is functioning properly.
Regular Maintenance
Implement a regular electrical maintenance program to prevent future problems.
In summary: The buzzing sound and hot breakers indicate a problem that needs to be addressed immediately. Do NOT upsize the breakers. Instead, systematically troubleshoot the circuits to identify the root cause of the overheating and fix it. And if unsure, call a qualified electrician experienced in medical facility electrical systems. Flag for review