User: Canton, Location: Virginia
Asked on: Monday, February 24, 2025 at 1:49 pm EST
Answered on: Thursday, March 6, 2025 at 9:01 am EST
Question: I have a couple of installations with meter stacks that have a 2000 and 1600 amp Main breaker, but than have feeder bussing with 1200 amp bussing/meter branches and 800 amp amp bussing/meter branchesRegardless of what the manufacturer says are permissible configurations, and these being feeder busing/busways with branch taps/OCPDS to go to apartments, how does the feeder busway ampacity comply with 368.17 when it has an OCPD larger (2000 or 1600 amp) than the busway ampacity 1200 amp/800 amp?Even looking at TAP rules, it appears to be tapping a tap.Any thoughts from the brain bank?Thanks
You've hit a common and legitimate point of confusion with meter stacks and feeder busway installations, especially when dealing with large service sizes and multiple downstream branches. Here's a breakdown of the potential code compliance issues and possible explanations
The Problem:
368.17 Overcurrent Protection
This section generally requires the busway to be protected against overcurrent in accordance with its ampacity rating. Having a 2000A breaker feeding a 1200A busway clearly violates this on the surface.
Tap Rules (240.21)
You're right. Trying to apply tap rules here is problematic. The tap rules generally deal with conductors, and even then, your scenario appears to be tapping a tap, which is usually not allowed.
Possible Explanations & Considerations
Engineering Supervision and Calculated Load
This is the most common reason why these installations are allowed.
Detailed Load Calculations
A qualified engineer MUST perform very detailed load calculations for each apartment unit served by each meter, taking into account diversity factors and expected usage patterns.
Demand Factors
These calculations demonstrate that the actual maximum load on any 1200A or 800A section of busway will never exceed its ampacity, even under the worst-case scenario.
Supervision and Restriction
These are typically for larger multi-family installations that are under the supervision of qualified persons for proper maintenance and operation
Documentation
This detailed load study is crucial and MUST be submitted to the AHJ (Authority Having Jurisdiction) for approval. The manufacturer's "permissible configurations" are typically based on this type of engineering analysis.2.
Specific Busway Design and Listing
Listing
The busway assembly as a whole, including the main disconnect and the branch taps, might be specifically listed and labeled for this type of configuration. Look for markings that explicitly state the permissible configurations and the conditions under which they are allowed. The listing could incorporate specific OCPD requirements.
Manufacturer's Instructions
The busway manufacturer's instructions are critical. They may contain specific requirements for OCPD sizes and installation methods that are part of the product's listing.
High Fault Current Withstand
The busway sections are often designed and tested to withstand very high fault currents, even if the overcurrent protection doesn't trip immediately at 1200A or 800A. This withstand capability allows for selective coordination with downstream breakers.3.
Feeder Protection as a System (Selective Coordination)
Selective Coordination Study
A selective coordination study might be performed to demonstrate that downstream breakers will clear faults before the main breaker trips, thus protecting the smaller busway sections from prolonged overcurrents.
Purpose of Main OCPD
The main breaker's primary function in this case might be to protect the entire service entrance conductors and the main busing upstream of the feeder busways, rather than the individual feeder busway sections themselves.4.
AHJ Acceptance
Local Amendments
Your AHJ might have specific local amendments to the NEC that address meter stacks and feeder busways in multi-family dwellings.
Alternative Methods
The AHJ might accept an "alternative method" of compliance if you can demonstrate that the proposed installation is safe and meets the intent of the NEC. This requires detailed documentation and justification.
Important Considerations
"Per Manufacturer's Instructions" is Not a Blank Check
Simply saying "it's per the manufacturer's instructions" isn't enough. You need to understand what those instructions are based on (load calculations, listing requirements, etc.) and demonstrate compliance.
Load Growth
Consider potential future load growth in the apartments. Over-optimistic load calculations can lead to problems down the road.
Enforcement
AHJs have different levels of scrutiny. Some might simply accept the manufacturer's instructions without further investigation, while others will require detailed load studies and justification.
Action Steps
Obtain Detailed Manufacturer's Documentation
Get the complete installation instructions, listing information, and any engineering reports related to the busway assembly.2.
Perform (or Review) Load Calculations
Critically review the load calculations for each apartment unit. Ensure they are accurate, conservative, and account for diversity factors.3.
Consult with the Engineer
If you're not the engineer of record, discuss the design with them to understand the rationale behind the OCPD sizes.4.
Consult with the AHJ: Present your documentation to the AHJ before installation to get their feedback and approval. Be prepared to answer questions and provide additional information.In conclusion, while the scenario appears to violate 368.17 at first glance, it can be code-compliant if supported by detailed load calculations, specific busway listing and design, selective coordination studies, and AHJ approval. The key is to thoroughly understand the basis for the design and demonstrate that the installation is safe and meets the intent of the NEC. Flag for review