User: kjroller, Location: Dawson Mn
Asked on: Monday, March 3, 2025 at 1:50 pm EST
Answered on: Thursday, March 6, 2025 at 9:18 am EST
Question: (C) ContinuousExcept as provided in 250.30(A)(5) and (A)(6), 250.30(B)(1), and 250.68(C), grounding electrode conductor(s) shall be installed in one continuous length without a splice or joint. If necessary, splices or connections shall be made as permitted in the following:Splicing of the wire-type grounding electrode conductor shall be permitted only by irreversible compression-type connectors listed as grounding and bonding equipment or by the exothermic welding process.( I was gonna splice with irreversible crimp which is one of the ways permitted) however am I allowed to do so. Or does it have to meet one of the exceptions. For me to splice? Or can I splice anytime with irreversible crimp
You are interpreting the code correctly. Here's a breakdown: General Rule
Grounding electrode conductors (GECs) should be a
continuous length without splices or joints. Exceptions
There are some exceptions to the general rule that allow for splicing under specific circumstances, (as listed in 250.30(A)(5) and (A)(6), 250.30(B)(1), and 250.68(C).)
Permitted Splicing Methods
When splicing is permitted (either because of an exception or because the AHJ allows it in specific situations), the only acceptable methods are: Irreversible compression-type connectors
listed as grounding and bonding equipment Exothermic welding.
In your situation
You can only splice with an irreversible crimp connector
if and only if one of the following applies:1. One of the Exceptions in 250.30(A)(5) and (A)(6), 250.30(B)(1), and 250.68(C). applies. Important Considerations
Listed Connectors
The irreversible compression connector must be
listed for grounding and bonding purposes. This means it has been tested and certified for this specific application. Authority Having Jurisdiction (AHJ)
Always consult with your local electrical inspector (AHJ). They have the final say in interpreting and enforcing the code. They might have local amendments or interpretations that affect your situation.
In summary, splicing a grounding electrode conductor is generally not allowed unless an exception applies. If splicing is permitted (due to an exception or AHJ approval), you must use an irreversible compression connector listed for grounding and bonding or exothermic welding. Flag for review