Question: Greetings,I am currently working on a surgery center where we are required to achieve the alternate power source requirements under 700.3. My problem is the lead time of getting a docking station built vs. to the project's completion schedule.Does anyone have any ideas of other possible methods that can be used to achieve the 700.3 requirement using items such as an MTS w/ aux contacts??
Okay, let's break down the situation and explore alternative solutions to meet the emergency power requirements of NEC 700.3 in your surgery center project, given the long lead time for a docking station.
Understanding the Requirements
NEC 700.3 generally mandates an alternate source of power for emergency systems. This could be a generator, battery system, or other approved source. The key is that it must be reliable and available when the normal power source fails.
The Docking Station Issue
Docking stations, presumably for mobile generators or other portable backup power units, are sometimes used as a more flexible and scalable solution. However, as you pointed out, they can have long lead times, which are not feasible for your project.
Alternative Solutions Using MTS with Auxiliary Contacts (and Other Considerations)
The core of your idea is solid: using a Manual Transfer Switch (MTS) with auxiliary contacts is a viable approach, but you need to ensure it meets the stringent requirements of Article 700. Here's a detailed breakdown:1. Manual Transfer Switch (MTS) with Auxiliary Contacts
Functionality
The MTS allows you to manually switch the emergency loads between the normal power source and a portable generator (or other alternate power source you select).
Auxiliary Contacts
The auxiliary contacts are critical. These contacts provide a signal indicating the position of the switch (normal or emergency). This signal can be used to: Disable the normal power source breaker feeding the MTS to prevent back-feeding power into the utility grid when on generator power. Activate visual and audible alarms (required by code) indicating the system is operating on emergency power. Communicate the switch status to a Building Management System (BMS), if applicable.
Key Considerations
Listing and Suitability
The MTS must be listed for emergency system use (UL 1008 is the standard). Look for a transfer switch specifically designed for emergency systems.
Current Rating
Size the MTS appropriately for the anticipated emergency load. Overestimate slightly to accommodate future growth.
Voltage Rating
Match the voltage requirements of your system.
Number of Poles
Ensure the switch has the correct number of poles (usually 3-pole for a 3-phase system, plus a neutral pole).
Break-Before-Make
Essential for transfer switches. It ensures that the normal power source is completely disconnected before the alternate source is connected.
Location
Locate the MTS in an accessible location, clearly labeled.
Single Point Connection
Ensure that the MTS is designed to connect to the alternate power source at a single point. This simplifies the connection process and reduces the risk of wiring errors.2.
Portable Generator (or Other Alternate Source)
Sizing
Calculate the total emergency load (in kVA or kW) that needs to be supplied. Consider the inrush current of motors and other inductive loads. Size the generator accordingly. Consult with a qualified electrical engineer for load calculations.
Voltage and Phase
Match the voltage and phase of the generator to the electrical system.
Fuel Source
Consider fuel availability and storage for a generator. Propane or natural gas may be preferable to gasoline or diesel due to storage and shelf-life issues.
Automatic Start vs. Manual Start
While the MTS is manual, the generator can be automatic start. This is not always necessary for surgery centers but can be beneficial.
Exhaust
If using a generator, properly vent exhaust fumes to the outside, away from building intakes. Comply with all local regulations regarding generator placement and exhaust.
Safety
Ensure the area where the generator is placed is well-ventilated and secure.3.
Wiring and Connections
Qualified Electrician
All wiring must be done by a qualified and licensed electrician and comply with the NEC.
Conduit and Wiring Type
Use appropriate conduit and wiring types for the application (e.g., EMT, THHN).
Grounding
Properly ground the generator and the MTS.
Labeling
Clearly label all circuits, the MTS, and the generator connection point.4.
Alarms and Indicators
Audible Alarm
An audible alarm is required to alert personnel that the system is operating on emergency power.
Visual Indicator
A visual indicator (e.g., a light) is also required.
Placement
Place alarms and indicators in locations where they will be readily noticed by staff.5.
Documentation and Training
Written Procedures
Develop and maintain written procedures for manually starting the generator and operating the MTS. Include step-by-step instructions, safety precautions, and troubleshooting information.
Training
Train key personnel on the operation of the emergency power system. Conduct regular drills to ensure proficiency.
Maintenance Schedule
Establish a regular maintenance schedule for the generator and MTS, including periodic testing. Keep records of all maintenance activities.
Important Considerations Specific to Surgery Centers
Essential Electrical Systems (EES)
Surgery centers are typically required to have a Type 1 Essential Electrical System (EES) per NFPA 99 (Health Care Facilities Code). This dictates which loads must be powered by the emergency system. Common loads include: Operating room lighting and receptacles. Anesthesia equipment. Life support equipment. Critical monitoring equipment. Nurse call systems. Fire alarm systems. Egress lighting.
Risk Assessment
Conduct a risk assessment to determine the critical loads that must be powered during an outage. This will help you size the generator and determine the appropriate level of redundancy.
Coordination with Authorities
Work closely with the Authority Having Jurisdiction (AHJ, usually the building inspector or fire marshal) throughout the design and installation process. Get their approval on the proposed solution before proceeding with the installation.
Load Shedding
Consider load shedding strategies to minimize the size of the generator. This involves automatically disconnecting non-essential loads when the system is operating on emergency power.
Steps to Take Now
Load Calculation
Accurately determine the emergency load requirements. Engage a qualified electrical engineer to perform this calculation if you are unsure.2.
MTS Selection
Select a UL 1008 listed manual transfer switch with auxiliary contacts that is appropriately sized for the load.3.
Generator Sizing
Based on the load calculation, determine the appropriate size (kVA or kW) and type of generator.4.
Detailed Design
Develop a detailed electrical design, including single-line diagrams, wiring diagrams, and equipment specifications.5.
AHJ Approval
Submit the design to the AHJ for review and approval.6.
Installation
Have a qualified and licensed electrician install the MTS, generator connection point, wiring, and alarms in accordance with the NEC and all applicable codes.7.
Testing
Thoroughly test the system to ensure that it operates as intended. Document all test results.8.
Training
Train key personnel on the operation of the system.
Advantages of an MTS-Based System (over waiting for a docking station)
Faster Implementation
You can likely procure an MTS and a generator more quickly than waiting for a custom-built docking station.
Potentially Lower Cost
Depending on the complexity of the docking station, an MTS-based system might be more cost-effective.
Simpler Design
An MTS is a relatively straightforward component, making the design and installation process simpler.
Disadvantages (compared to an automated system)
Manual Operation
Someone must physically start the generator and operate the MTS. This requires trained personnel and a timely response.
Potential for Human Error
Manual operation increases the risk of errors.
Important Disclaimer: This information is for general guidance only. You must consult with qualified and licensed professionals (electrical engineers, electricians, AHJs) to ensure that your emergency power system meets all applicable codes and safety requirements.* Flag for review