User: miko868, Location: New York
Asked on: Tuesday, March 4, 2025 at 10:10 am EST
Answered on: Thursday, March 6, 2025 at 9:20 am EST
Question: I am finishing up a FA design for a school that someone else had started. Upon my site visit I noticed in each of the longer corridors there was skylights (48"x48"x48"). Normal ceiling height elsewhere is 108". Would smoke detectors need to be installed within the skylight itself? I have coverage in the corridor already. NFPA 72 isn't too clear with this. I would assume you would treat this similar to a beam pocket location, but was curious what others think.
You're right, NFPA 72 doesn't specifically address skylights in the way you're describing. However, your analogy to beam pockets is a good starting point. Here's a breakdown of how to approach this, combining code understanding with practical considerations
Understanding the Issue:
Purpose of Smoke Detectors
To detect smoke early and provide a timely alarm.
Smoke Stratification
Smoke rises but can be trapped in certain areas, such as beam pockets, skylight wells, or other recessed spaces. This can delay detection if detectors are only located on the main ceiling.
Obstructions
The skylight well itself could obstruct the free flow of smoke to the corridor's main ceiling-mounted detectors.
NFPA 72 Guidance and Considerations
NFPA 72, Section 17.7.
3.2.5 (and similar sections for other detector types) regarding Beam Construction
This section (and similar sections for other detector types) are frequently interpreted to include similar obstructions. It generally states that detectors need to be placed in each bay formed by beams running the longer direction, if the beam depth exceeds a specific percentage of the ceiling height (typically 4").
Engineering Judgement (Performance-Based Design)
If you believe your corridor detectors adequately cover the area and detect smoke quickly enough, you might be able to argue against detectors in the skylight wells. This would require a strong justification and may need approval from the AHJ. Consider factors like air currents, anticipated fire scenarios, and building materials.
AHJ (Authority Having Jurisdiction)
Ultimately, the AHJ has the final say. It's wise to contact them early in the process to discuss your design and get their perspective on the skylight issue. They may have local interpretations or specific requirements.
Applying it to Your Situation
Treat the Skylight as an Obstruction
Given the dimensions of the skylights (48"x48"x48") and the ceiling height (108"), the skylight depth is a significant portion of the ceiling height (48" / 108" = ~44%). This strongly suggests treating it like a beam pocket for detector placement.2.
Detector Placement within the Skylight
Recommended
The safest and most code-compliant approach is to install a smoke detector within each skylight well. Mount it as high as possible within the well, near the top, without obstructing the skylight itself.
Consideration
The detector location should be accessible for testing and maintenance.
Type of Detector
Use a compatible detector type, likely the same as the ones you're using in the corridor.3.
Alternative: Engineering Judgement and AHJ Approval (More Difficult)
Demonstrate Adequate Coverage
You'd need to prove that the corridor detectors will detect smoke within a reasonable timeframe, even with the skylights obstructing airflow.
Consider CFD (Computational Fluid Dynamics) Modeling
For complex situations, CFD modeling can simulate smoke spread and demonstrate detector effectiveness. This is a more expensive approach.
Early Consultation
Crucially, discuss this approach with the AHJ
before finalizing your design. Get their agreement in principle.
Recommendations
Go with the safe approach
Install smoke detectors in the skylight wells. This is the most defensible approach from a code perspective and provides the best protection.
Document everything
Keep detailed records of your design decisions, including calculations, assumptions, and any consultations with the AHJ.
Consult with the AHJ
This is the most important* step. Get their feedback and approval on your design.
In summary, the most prudent approach is to treat the skylight wells as obstructions similar to beam pockets and install smoke detectors within each well. This ensures better smoke detection and minimizes potential code compliance issues. Flag for review