Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Nec 220.61 B 2, a 70 % neutral & harmonic currents

User: Jpflex, Location: Victorville

Asked on: Tuesday, March 4, 2025 at 4:29 pm EST
Answered on: Thursday, March 6, 2025 at 9:20 am EST

Question: I askwd a similar question a while back but i wanted to ecxpandFirst, in 220.61 (C) point 2, makes no sence when NEC mentions NON LINEAR LOADS on a Y neutral system as being a determining factor to dissallow a 70% neutral reduction because point 1 already said ALL 3 phase Y systems with a neutral cannot have its neutral reducedSecond, the 2023 handbook explains that the neutral is considered as a current carrying conductor if the load of the electric discharge lighting, data process lighting or similar equipment on the neutral consist of more than half the total load.I used to think nec did not allow a 70% reduction of neutral feeder to the anount in excess of 200 amperes, if NON LINEAR LOADS were served or to the portion of non linear loads.It seems we can apply a 70% reduction to the neutral service or feeder wire in excess of 200 amperes regardless if non linear loads were served and as long as the transformer is not from a 3 phase Y system with ground. Is this correct?

Okay, let's break down NEC 220.61(C) and the neutral conductor sizing rules, focusing on your specific questions and the interaction with non-linear loads. It's a tricky area, and the understanding has evolved over the years.

Understanding 220.61(C) - Neutral Conductor Load

This section deals specifically with calculating the neutral conductor load for the service or feeder. It's about how much current you need to plan for in your neutral, not necessarily the minimum size of the wire (which has other code-driven requirements).Here's the breakdown of 220.61(C) with the 2023 NEC in mind: General Principle

The neutral conductor load is generally the
maximum unbalanced load. Think of it as the worst-case scenario where one phase is loaded heavily, and the other phases are lightly loaded.

(C)(1) Y Connected Systems

This is a key point of confusion. This section states, "On a 3-wire dc or single-phase ac, or 4-wire, 3-phase, wye-connected ac systems, a neutral conductor shall be permitted to be sized at 100% of the unbalanced load." This effectively eliminates any reduction based on load type on 3-phase, 4-wire wye systems when calculating the unbalanced load.

(C)(2) Feeder or Service Conductor Size

Where the maximum unbalanced load is over 200 amperes, a 70% demand factor shall be permitted for that portion of the unbalanced load in excess of 200 amperes.


(C)(3) Nonlinear Loads

On a 3-wire dc or single-phase ac, or 4-wire, 3-phase, wye-connected ac systems, a neutral conductor shall be considered a current-carrying conductor when the major portion of the load consists of nonlinear loads. The neutral conductor shall be sized to carry the calculated neutral load.

Addressing Your Questions
1. The Apparent Redundancy of (C)(1) and (C)(3) Regarding Non-Linear Loads on 3-Phase Wye Systems

You're right, the wording can be confusing. In 220.61(C)(1), the code already stated that all 3-phase Y systems with a neutral must have a neutral that can carry 100% of the unballanced load. (C)(3) simply further reinforced that point when non linear loads are involved.
2.


Non-Linear Loads and the 70% Reduction

This is where the understanding gets nuanced. The 70% reduction can be applied on 3 phase systems with a neutral to that portion of the calculated unbalanced load exceeding 200 amps. The exception is that you can never reduce the neutral load below the amount caused by non-linear loads. This is the practical effect of the handbook's explanation about electric discharge lighting, data processing equipment, etc.

Here's a simplified way to think about it


Calculate the Unbalanced Load

Determine the maximum difference between the load on any one phase and the load on the other phases.2.

Consider Non-Linear Loads

If a significant portion (more than half) of the total load is from non-linear sources, the neutral must be sized to carry the calculated load from those non-linear sources (which can be as high as the phase current). If the non-linear load is smaller than the unbalanced load, the unbalanced load is the determining factor.3.

Apply the 70% Reduction (If Applicable)

If the unbalanced load (or the non-linear load calculated as the determining factor) exceeds 200 amps, you can apply the 70% demand factor to the portion above 200 amps to get a neutral load.4.

Determine Wire Size

Finally, you use the calculated neutral load to choose the appropriate wire size from Table 310.16 or other applicable ampacity tables. Remember that the chosen wire must be able to carry at least the calculated neutral load.

Important Considerations



Total Harmonic Distortion (THD)

Non-linear loads create harmonic currents, primarily third harmonics, which add arithmetically in the neutral of a wye-connected system. This is why the code is so cautious about neutral reduction when non-linear loads are present.


3-Phase Delta Systems

The neutral rules are different for 3-phase Delta systems with a midpoint neutral tap (high-leg delta). In those cases, you wouldn't have the same harmonic concerns, and the neutral current would be primarily due to single-phase loads.

Over-Sizing for Future Growth

It's often wise to over-size the neutral slightly, especially in commercial and industrial settings, to accommodate future load growth and potential increases in non-linear loads.


Local Amendments

Always check for any local amendments to the NEC. Some jurisdictions may have stricter rules regarding neutral sizing.

In Summary, Regarding Your Final Question:


No, it's not quite correct to say you can always apply the 70% reduction regardless of non-linear loads as long as it isn't a 3-phase Y. The exception is that you can never reduce the neutral load below the amount caused by non-linear loads on a 3 phase Y system with a neutral or a single phase system.The key is to carefully calculate the unbalanced load, determine the extent of non-linear loading, and then apply the 70% demand factor (if applicable) while ensuring that the neutral can still carry the calculated load, including the contribution from non-linear harmonics. When calculating the neutral load required for a 3-phase system, you would need to calculate a neutral current to ensure that the reduction would result in a neutral that is capable of handling the unbalnced load. The same is true for single phase loads. The only thing that this section says about neutral loads is that its permitted to do so.Always consult with a qualified electrical engineer or inspector if you have any doubts about neutral conductor sizing, especially in complex installations with significant non-linear loads. Flag for review

Previous Question Next Question