Topic: Change of Plans, failed inspection

User: Greg1707, Location: Alexandria, VA

Asked on: Wednesday, March 5, 2025 at 4:08 pm EST
Answered on: Thursday, March 6, 2025 at 9:23 am EST

Question: I have a small residential basement remodeling project that includes 12 receptacles and four recessed lights. The plans specify a receptacle at 5' above floor for a wall mounted TV. The home owner decided to eliminate the TV, so no receptacle.I failed rough in inspection because the plans specified the receptalce and of course there was no receptacle.Does this happen often? I was suprised the inspector even took the time took look at the plans.

Yes, it does happen. Here's a breakdown of why and some potential solutions

Why the Failure?
Code Compliance Through Approved Plans

When you obtain a permit and submit plans, you are agreeing to build according to those plans and all applicable codes (NEC - National Electric Code). The inspector's job is to verify that your work matches the approved plans.


Enforcement of Minimum Standards

Inspectors enforce code to ensure safety and prevent future issues. While a receptacle at 5' might seem unnecessary now, the plans might have taken into account other code issues.

Clarity and Documentation

Approved plans establish a clear baseline for construction. Changes should be documented and approved.


Misunderstanding of the Inspection Process

It's common for homeowners to change their mind after plans are approved, but it can complicate the inspection process.

Why the Inspector Looked Closely
Thoroughness

A good inspector will review plans to get a general idea of the scope of the project and specific requirements.


Standard Practice

Checking against plans is a fundamental part of the inspection process for many jurisdictions.

High-Visibility Element

A receptacle at 5' is a highly visible element. Inspectors may look for these type elements to verify the installation is proceeding in a manner that would be approved.


Specifics Triggered Attention

The location of the receptacle in the plans, could have been a clue to the inspector to look at the specifics of this installation.

What to Do Now (Solutions)
1. Talk to the Inspector ASAP

This is the most crucial step. Explain the homeowner's change of plans. Ask if there are any other reasons for the failure besides the missing receptacle. Discuss potential solutions.2.

Options for Resolution



Install the Receptacle

This is the easiest way to pass, even if the homeowner doesn't use it. You can cap it off and put a blank plate on it.

Submit Revised Plans

If the inspector is amenable, and depending on the local process, you might be able to submit a revised plan showing the elimination of the receptacle. This may require a formal amendment to the permit. This is the most correct path, but could take time. The inspector will still have to approve the plan.


Request a Field Adjustment

Some jurisdictions allow minor field adjustments to the plans with inspector approval. This may require a written note on the plans, signed by the inspector.

Key Takeaways to Avoid This in the Future
Communication is King

Before starting any work, confirm with the homeowner that the plans are
exactly what they want.

Change Orders/Written Documentation

If there are changes after plans are approved, document them in writing (a change order, even a simple email).

Communicate with the Inspector

Before making any changes, discuss them with the inspector. They can advise on the proper procedure for approval.


Plan Review

If you think you need to deviate from the plans, speak to the inspector for guidance.

In Summary


It's not uncommon for small plan deviations to cause inspection failures. The key is communication, documentation, and a willingness to work with the inspector to find a solution that meets code requirements. I recommend calling the inspector as soon as you can to discuss the situation. The inspector will have the final say regarding code compliance. Good luck. Flag for review