Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Emergency Power source for High Rise building

User: AM59, Location: Boston, MA

Asked on: Thursday, March 6, 2025 at 10:45 am EST
Answered on: Thursday, March 6, 2025 at 6:34 pm EST

Question: I'm working on a retrofit project in a high-rise building in Massachusetts. I'm aware of building code and NEC requirements that require Standby power and Emergency power in high rises for the elevator systems and fire pump, as well as other accessory systems (fire command center lighting and power, Fire Alarm, etc.). This building currently uses either lighting inverters or wall-mounted battery emergency lights for emergency egress lighting (similarly for exit signs; self-contained batteries); there is no dedicated life safety/Emergency/Article 700 ATS or distribution aside from the fire pump ATS and controller.For some reason, I was under the impression that the IBC 2021 and Massachusetts amendments thereof had some sort of a requirement that emergency power be provided by a generator. I spoke with a former colleague of mine about this and he said there is, in Article 400 of the IBC. I looked in the IBC and can find no proscription on the type of emergency power source, only that there be one.Is it ok to use normal dual-light emergency battery units for egress lighting in a high rise in Massachusetts, or does this violate some other code that I'm missing (or am I misinterpreting the code)?

You've done well to question your initial assumption. You're right, there isn't a blanket requirement in the IBC (or Massachusetts amendments, generally) that emergency power for egress lighting in a high-rise must be a generator. Your colleague is mistaken about Article 400.Here's a breakdown of the relevant considerations and why battery units can be acceptable, but also why you need to be very careful

Key Considerations:

1. IBC Chapter 10 (Means of Egress) and Massachusetts Amendments (780 CMR Chapter 10)

This is your primary reference for egress lighting requirements. While it mandates the presence of emergency lighting, it doesn't typically dictate the power source. Look for sections like:

1006 (Illumination)

Specifies the required illumination levels.


1006.3 (Emergency Power)

This is where it gets specific about what must be powered by emergency power. It generally requires emergency power for the means of egress lighting.

Review Massachusetts amendments carefully.
These may have local modifications or stricter interpretations.2. IBC Section 403 (High-Rise Buildings) and Massachusetts Amendments (780 CMR Chapter 4)

This section
does specify systems that require standby or emergency power in high-rise buildings. These typically include:

Fire Pumps

Always requires a reliable source of emergency power. Usually, this is generator-backed.

Elevators

Often require standby or emergency power, depending on the building's configuration.


Fire Alarm System

Must have a secondary power source (usually batteries, but generator-backed standby is sometimes required depending on the system's design and the local AHJ).

Smoke Control Systems

If present, these
typically require standby power.

Fire Command Center

Lighting, communications, and other critical systems in the fire command center must have emergency power.3.

NFPA 101 (Life Safety Code) and NFPA 70 (National Electrical Code)

These are often referenced by the IBC and local amendments, and can influence requirements:

NFPA 101 (Life Safety Code)

Specifies the required duration of emergency power. For high-rise buildings, it's typically

at least 90 minutes
. This is a critical consideration for battery units.

NFPA 70 (National Electrical Code - specifically Article 700, Emergency Systems, and Article 701, Legally Required Standby Systems)

These articles define emergency and standby systems. You must comply with the testing and maintenance requirements of these articles for any emergency lighting system, regardless of power source.4.

AHJ Interpretation

Ultimately, the Authority Having Jurisdiction (AHJ) – the local building inspector or fire marshal – has the final say. Their interpretation of the codes is what matters.

Why Battery Units Can Be Acceptable (But with Caveats)



Code Compliance

If the self-contained battery emergency lights and exit signs

meet the illumination levels required by IBC Chapter 10 (and MA amendments), AND can provide at least 90 minutes of power, then
technically, they can be code-compliant. However, there are potential complications



Load Calculation

You need to be sure you're correctly calculating the required illumination levels for egress. It might be more difficult to achieve sufficient illumination in some areas with individual battery units compared to a central generator-backed system with strategically placed luminaires.

Maintenance and Testing

Individual battery units require diligent maintenance and testing (as per NFPA 101 and NFPA 70 requirements). This can be a significant operational burden.


Reliability

Individual units are more prone to failure than a well-maintained generator system. Battery failures, vandalism, and other issues can compromise the system's effectiveness.

Coordination

It is hard to coordinate so that an emergency egress event has proper illumination throughout the building and is not dependent on someone testing the lights every 30 days.


Monitoring

A centralized generator system can be monitored to ensure that it is ready to provide the required service when the mains power goes out.

Why a Generator-Backed System is Often Preferred (and Sometimes Required in Practice)



Reliability

Generators, when properly maintained and fueled, are generally more reliable than relying on hundreds of individual battery units.


Centralized Monitoring

A generator system can be monitored to ensure it's functioning correctly.

Automatic Transfer

An Automatic Transfer Switch (ATS) automatically switches to generator power when normal power fails.


Duration

Generators can provide power for extended periods, limited only by fuel supply.

Scalability

You can easily add more lighting fixtures to a generator-backed system.


Other Systems

As you mentioned, fire pumps require emergency power, and elevators often do. A single generator can serve multiple critical systems.

AHJ Preference

Many AHJs
prefer generator-backed systems for high-rises due to their superior reliability and maintainability. They may scrutinize battery-only solutions more carefully.

Overall Building Strategy

Generators are better aligned with a comprehensive life safety strategy.

Recommendations


Consult with the AHJ Early

Before investing any time or money, meet with the local building and fire officials. Present your proposed approach and get their feedback. They may have specific requirements or preferences.2.

Perform a Thorough Code Review

Go through the IBC, Massachusetts amendments, NFPA 101, and NFPA 70 line-by-line to ensure you understand all the requirements. Pay close attention to the sections on emergency lighting duration, illumination levels, and testing/maintenance.3.

Develop a Detailed Design

If you propose using battery units, create a detailed plan showing the location of each unit, the illumination levels they will provide, and the maintenance schedule.4.

Consider the Life Cycle Cost

While battery units may have a lower initial cost, the ongoing maintenance and replacement costs can be significant. Compare the total life cycle cost of battery units vs. a generator system.5.

Weigh the Risks

Consider the potential consequences of a failure in the emergency lighting system. In a high-rise, a reliable emergency lighting system is crucial for safe evacuation.6.

Consider a Hybrid Approach

A hybrid approach involves providing a generator for the Fire pump, elevators, and Fire Command Center. You can then include battery powered egress lights for the stairwell that are more cost effective.

In conclusion, while battery units can be code-compliant for egress lighting in a Massachusetts high-rise, it's crucial to thoroughly review the codes, consult with the AHJ, and carefully weigh the risks and benefits. A generator-backed system is often the more reliable and practical solution, especially when considering the other life safety systems in the building.
Flag for review

Previous Question Next Question