Question: Can you use a 20 amp gfci dead front on a 15 amp circuit? I have one in the truck, and I wasn’t sure if you could use it on a 15 amp circuit fed with #14 nm.

No, you should not use a 20-amp GFCI dead front on a 15-amp circuit wired with 14 AWG NM cable. Here's why: Overcurrent Protection

The circuit breaker (or fuse) is designed to protect the wiring. If you have a 15-amp breaker and 14 AWG wire, the breaker will trip if more than 15 amps is drawn through the wire. This prevents overheating and potential fire. While the GFCI can interrupt a circuit under certain conditions, it does not provide the same overcurrent protection as a breaker. If a fault caused, say, 18 amps to flow through the 14 AWG wire, the 20A rated GFCI would not trip. The #14 AWG wire would overheat and could cause a fire.


Code Compliance

Electrical codes (like the NEC) specify the maximum size overcurrent protection allowed for different wire sizes. Using a 20-amp GFCI on a 15-amp circuit violates these codes.*

Confusion

It can be confusing for future electricians or homeowners who might assume the circuit is rated for 20 amps if they see a 20-amp device.

In summary, stick with a 15-amp GFCI for a 15-amp circuit.