User: Malywr, Location: New Jersey USA
Asked on: Friday, March 7, 2025 at 11:09 am EST
Answered on: Saturday, March 8, 2025 at 12:10 am EST
Question: Hi everyone I need help how to wire makeup air dumper to range hood over 400cfm When hood is ON make up dumper must open. Or I should temper with range hood and install same size wire as power supply to hood and run it to dumper? or use current transformer next to electrical panel that will detect when hood is energized currently transformer will energize dumper I font want to over complicate something what suppose to be simple
You're on the right track thinking about different ways to detect when the hood is on and then activate the damper. Here's a breakdown of the options, their pros/cons, and my recommended approach, keeping in mind you want to keep it simple and safe
Option 1: Direct Tap into Range Hood Wiring (Generally Not Recommended)
Description
Tapping into the power wires that feed the range hood to power the damper directly.
Pros
Simple in theory.
Cons
Safety Issues
You're potentially modifying a UL-listed appliance, which could void its warranty and create a fire hazard if not done properly. You're messing with high voltage.
Code Violations
This could violate electrical codes, especially if the damper's power requirements overload the hood's circuit.
Hood Functionality
You could interfere with the hood's internal electronics or motor.
Difficult to do Correctly
You would need to know the exact type of power that the makeup air damper needs, if its 120V or 24V
Option 2: Current Transformer (CT) at Electrical Panel Description
A current transformer clamps around the wire feeding the range hood circuit breaker. When the hood draws current, the CT induces a small current in its secondary winding, which then triggers a relay to open the damper.
Pros
Non-Invasive
You don't modify the range hood itself.
Safe
The CT is isolated from the main power wires.
Cons
More Complex
Requires understanding of current transformers, relays, and low-voltage wiring.
More Expensive
CTs and relays add to the cost.
Calibration
May require some adjustment to ensure the CT triggers reliably at the hood's operating current.
Option 3: Dedicated Interlock Relay Description
This is what you want to do. The range hood will need to have a standard outlet that plugs into the wall. You can get a smart outlet that has two outlets. When the outlet detects power draw from the hood outlet, it will then enable the second outlet to power on. This is a clean, safe, non-evasive method.
Pros
Simplest Installation
Safest and easiest method Low Cost Cons
More expensive than direct tapping into the range hood wiring.Recommendation: Option 3 - Dedicated Interlock Relay
Option 3 is the cleanest, safest, and easiest option to install. If you want to go ahead and do option 1, then it is highly recommend that you get a certified electrician. They can assess the situation and do all the wiring for you. If you do not know what you are doing you can get seriously injured, or even killed.
Important Considerations
Local Codes
Always check your local building and electrical codes. Makeup air requirements vary greatly by location.
Professional Installation
If you're not comfortable working with electrical wiring, hire a qualified electrician. It's always better to be safe than sorry.
Damper Compatibility
Ensure the damper you choose is compatible with the control method you select (voltage, current, etc.).
Before you start ANY electrical work
Turn OFF the breaker that supplies power to the range hood circuit.* Test with a non-contact voltage tester to ensure the circuit is de-energized.Good luck with your project! Let me know if you have any more questions. Flag for review