Topic: Waterless Toilet GFCI Protection

User: session88, Location: USA

Asked on: Friday, March 7, 2025 at 11:56 am EST
Answered on: Tuesday, March 11, 2025 at 9:32 pm EDT

Question: Installing multiple Waterless Toilets at Remote Facilities. The small buildings have a small room that I will make into a Toilet Only Rest Room.The entire building does not have running water at all. Zero plumbing in the building. There is nothing else inside the Rest Room with the Incinolet Waterless Toilet. The toilet is essentially a large stainless steel can with a large heating element and blower fan - See link below.I will be installing a dedicated 120VAC 20Amp Circuit to the outlet as per the manufacture's requirement.The toilet has a cord with a 20 Amp Plug. Will not be Hard-Wiring the toilet.Does the 20 Amp outlet for this Incinolet Toilet need to be GFCI Protected ?

Let's break down the requirements for GFCI protection based on the NEC (National Electrical Code), since that's the governing standard in the US (and widely adopted elsewhere).

NEC Considerations (and why it likely NEEDS GFCI) NEC 210.8(A) Dwelling Units

This section doesn't apply since it's not a dwelling.


NEC 210.8(B) Other Than Dwelling Units

This is where it gets relevant. It requires GFCI protection for 125-volt through 250-volt receptacles supplied by single-phase branch circuits rated 150 volts or less to ground, 50 amps or less in specific locations. The relevant one here is usually:

(6) Toilet Rooms

GFCI protection is generally required for receptacles in toilet rooms in commercial, industrial, and institutional occupancies.

Why GFCI is Almost Certainly Required


Even though it's not a "wet" location in the sense of a shower or sink being present, the presence of a toilet means this will probably be considered a toilet room. Therefore, unless there is a VERY specific and highly unlikely exception, the 20A, 120V receptacle for the Incinolet
will need GFCI protection.

Important Considerations & Recommendations1. Local Codes and AHJ (Authority Having Jurisdiction)

This is the
most important point. The NEC is a model code. Your local building codes may be stricter or have specific amendments. Always consult with your local building department or electrical inspector (AHJ) for a definitive answer. They have the final say. Tell them exactly what you're planning to do (waterless toilet, no other plumbing, etc.) and ask if a GFCI is required.2.

Manufacturer's Recommendations

While the Incinolet documentation may not explicitly
require GFCI, it is generally good practice to follow any safety recommendations they make. You could also contact them directly to ask about GFCI.3.

Best Practice

Even if not strictly required by code (which is
unlikely), GFCI protection adds a layer of safety. Given the potential for moisture (even from cleaning, spills, or humidity) and the fact that you're dealing with electrical equipment, it's a prudent safety measure.4.

Type of GFCI

Install a GFCI receptacle (the type that's built into the outlet) at the location where the Incinolet will be plugged in. A GFCI breaker at the panel would also work, but the receptacle is generally more convenient for testing and resetting.

In Conclusion


Given the NEC requirements for toilet rooms, it is nearly certain that the 20A receptacle for the Incinolet will need GFCI protection. However, you
must* confirm this with your local building department or electrical inspector (AHJ) to ensure compliance with local codes. Installing GFCI is a good safety practice regardless. Flag for review