Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Unusual Panel Modification

User: J2H, Location: Wisconsin

Asked on: Saturday, March 8, 2025 at 11:02 am EST
Answered on: Saturday, March 8, 2025 at 11:12 am EST

Question: I saw this unusual setup at transmitter site, I was recently at. Seems questionable at best but other than the double lugged wires, and the design consideration of the top breaker spaces being blocked I can't find think of a definitive code violation. That said, the length of the studs looks a little short and there are possible not enough threads engaged. Curious on the forum's thoughts on this, and if it is something that should be corrected.

Okay, let's break down what we're seeing in that picture and address your concerns. You're right; it's a less-than-ideal installation, and while it might not be a slam-dunk code violation that you can immediately point to, there are several potential issues and questionable practices.

Here's a breakdown of the concerns


Double-Lugged Neutrals (Most Serious)

This is almost certainly a code violation.

The Problem

Neutral conductors
generally require a dedicated terminal. Putting two neutrals under one lug is extremely dangerous. In a multi-wire branch circuit, removing one neutral can cause overvoltage on the other leg, potentially damaging equipment and creating a fire hazard.

Relevant Codes



NEC 408.41 (B)

"Terminals for neutral conductors and grounding conductors shall be identified and shall be of a type that prevents accidental disconnection of the conductor." The intent is for
individual terminations.

Manufacturer's Instructions

Breakers and panels are Listed by manufacturers, and their instructions always specify the number and type of conductors permitted per terminal. Double-lugging would almost certainly violate the listing.

Why it Matters

This is not just about code compliance; it's about safety. Neutrals carry return current, and overloading a termination can lead to overheating, arcing, and fire. Also, the current sharing between the two conductors under the same lug will not be equal, and one conductor may have a significantly higher current draw than the other.2.

Blocked Top Breaker Spaces (Design Deficiency/Possible Violation)



The Problem

While technically not against code to block the top breaker spaces if the panel rating isn't exceeded by the remaining breakers installed, it's poor practice. This limits future expansion.

Relevant Codes



NEC 110.3(B)

Equipment shall be installed and used in accordance with any instructions included in the listing or labeling. If the design of the panel requires that it be fully populated to maintain the buss bar ratings, then this install would be in violation of NEC 110.3(B).

Why it Matters

It restricts future usability and makes the installation less flexible. Plus, it looks unprofessional and suggests a lack of planning.3.

Short Stud Length/Insufficient Thread Engagement



The Problem

This is where it gets tricky without precise measurements. Fasteners have minimum thread engagement requirements to achieve their rated holding strength. If the studs are too short and not enough threads are engaged in the mounting nuts/washers, the entire panelboard could be structurally compromised.

Relevant Codes

This falls more under general engineering principles than a specific NEC section. However:


NEC 110.3(B)

(Again) This becomes relevant because the manufacturer of the panelboard specifies the mounting hardware and procedures. Using inadequate studs could violate the listing and invalidate the warranty.

How to Assess

You'd need to measure the stud length, the thickness of the panelboard enclosure, the thickness of any washers, and the depth of the nut. Compare this to fastener engineering guidelines (which are beyond the scope of this discussion, but easily searchable). A general rule of thumb is a minimum of 1 diameter thread engagement.4.

General Workmanship



The Problem

The overall appearance is not great. While not a code violation in itself, sloppy wiring and haphazard placement of components often indicate other underlying problems.

Why it Matters

Professional installations are easier to maintain, troubleshoot, and are more reliable.5.

Wire Bending Radius
The Problem

The wire bending radius on some of the conductors looks to be to tight.

Relevant Codes



NEC 312.6(A)

Wire bending space at terminals.

How to Assess

Compare the wire bending radius with the requirements in NEC 312.6(A).

What to Do


Document Everything

Take clear, high-resolution photos from multiple angles.2.

Contact the Site Owner/Manager

Explain your concerns
calmly and professionally. Emphasize the safety implications, especially the double-lugged neutrals. Mention the limited expansion capability and the potential for structural issues with the mounting.3.

Suggest a Qualified Electrical Contractor Evaluation

Recommend that a licensed electrician inspect the installation and provide a written report with recommendations for correction.4.

If Necessary, Contact the Authority Having Jurisdiction (AHJ)

If the site owner is unresponsive or dismissive, and you genuinely believe there's an immediate safety hazard, you may need to contact the local electrical inspector. This should be a last resort.

In Summary:


This installation has several red flags. The double-lugged neutrals are the most concerning and require immediate attention. The other issues, while perhaps not as critical, contribute to a substandard and potentially unsafe installation. It
definitely* needs a thorough evaluation by a qualified electrician. Flag for review

Previous Question Next Question