Question: Some years back I recall incidents where LED's tripped the circuit breaker if there were "too many" on a circuit.Is this still true?Low many LED's can we really put on a circuit?Is there any "standard", rule of thumb, or any way of knowing?I know that supposedly LED have a big "inrush".In the "old" days we could load up a circuit with fluorescent fixtures to 75% without any issues.How much can we "safely" load up a circuit with LED fixtures? I would like to take advantage of loading up several circuits instead of having to spread them out over many circuits.ThanksRC
Yes, you're right, LED tripping breakers was a known issue, and while significantly better than early LEDs, it's still a factor to consider, especially when maximizing circuit loading. Here's a breakdown
Why LEDs Trip Breakers (The Inrush Current Issue):
Inrush Current (Also Called Inrush or Surge Current)
This is the peak current drawn by an LED driver momentarily when it's first energized. It's MUCH higher than the steady-state running current. Think of it like a water balloon suddenly hitting a wall – a lot of force for a tiny period. This brief surge can trick the breaker into thinking there's a short circuit, causing it to trip. Incandescent and fluorescent fixtures have a lower inrush current.
Capacitive Load
LED drivers (the power supply inside the LED fixture) use capacitors to smooth out the AC voltage. These capacitors act like a momentary short circuit when they first charge up.
Breaker Tolerance
Circuit breakers aren't perfectly precise. They have a tolerance band. Some breakers might trip slightly below their rated amperage, especially as they age.
Is it Still a Problem? Yes, but less so than early LEDs. LED driver technology has improved. Better drivers incorporate inrush current limiting circuitry. However, it's still a consideration. The quality of the LED fixture is a big factor. Cheaper fixtures often have poorer inrush current control. Higher Quality Matters
High-quality LEDs, especially those from reputable brands, are designed with better inrush current limiting.
Larger Installations are More Susceptible
The more LED fixtures on a single circuit, the greater the chance of the accumulated inrush current exceeding the breaker's trip threshold.
How Many LEDs Can You Put on a Circuit? (The Math and Considerations)
This is not a simple "one-size-fits-all" answer. You need to do some calculations, and the steps are as follows:1.
Determine Circuit Amperage
Most residential circuits are either 15 amps or 20 amps. Look at the breaker.2.
Determine Allowable Continuous Load
Important Rule
The National Electrical Code (NEC) generally limits continuous loads (loads that operate for 3 hours or more) to
80% of the circuit breaker's rating. This is a safety factor to prevent overheating. 15 Amp Circuit
15 amps 0.80 = 12 amps maximum continuous load.
20 Amp Circuit
20 amps 0.80 = 16 amps maximum continuous load.
3.
Find the LED Fixture's Wattage and Voltage
Look at the label on each LED fixture. It will state the wattage (e.g., 10W, 15W, etc.) and voltage (usually 120V in North America).4.
Calculate the Running Amperage of EACH Fixture
Use the formula:
Amps = Watts / Volts Example: A 10W LED fixture on a 120V circuit draws 10W / 120V = 0.083 amps (approximately).
5. Calculate the Inrush Current of EACH Fixture (This is the Tricky Part)
Ideally, the manufacturer's specifications will list the inrush current for the fixture. Look for this on the product data sheet, in the installation manual, or on the fixture itself. It might be expressed as "inrush amps," "surge current," or similar. It will also have a duration (usually a fraction of a millisecond). If you cannot find the inrush current specification, this is where you need to make assumptions. A common assumption is that the inrush current can be anywhere from 10x to 100x the running current. A 10x assumption is fairly conservative, while a 100x assumption is a very poor quality driver. A good quality driver should have a small multiple for inrush current.Example Calculations
Let's assume you have 10-watt LED fixtures operating at 120 volts on a 20-amp circuit, and the inrush current is assumed to be 10x the running current. Running Amps per fixture: 10 W / 120 V = 0.083 A Inrush Amps per fixture: 0.083 A x 10 = 0.83AAssuming the inrush current on all lamps occurs simultaneously, which is highly improbable, then we must sum up the inrush amps of the lights to be on the same circuit.Now let's find the number of lights we can put on a single circuit.Since this example circuit is a 20-amp circuit, let's find the number of fixtures that will generate a load of 80% of the maximum amperage, or 16 amps.This is the formula we can use to find the maximum number of fixtures, where N is the number of fixtures:
.083 = 16Then the maximum number of fixtures is:N
N = 16/.083N = 192.771Therefore, you can theoretically put 192 fixtures on a single circuit if it were strictly running amperage being calculated.Next, we must do the same with the inrush amperage, and make sure this circuit can withstand the amperage from the inrush current from each lamp.N .83 = 16N = 16/.83N = 19.277Therefore, the absolute maximum number of fixtures, even with a good driver and inrush current, is 19.However, you must remember that this calculation assumes that all inrush currents will occur at the same time, which is highly improbable.