Question: Got called on a service call The customer has a building management system panel, as of right now there’s a 120 V circuit running to the panel connected to a terminal block input and the wire is on the output of the terminal block are capped off instead of being landed on the 120 to 24 V transformer. Instead, they have a battery back up plugged into a receptacle, and the output of it is ran to the panel and landed on the transformer input terminal essentially providing normal power to the panel instead of the feed from the electrical panel. It’s done this way so if the building loses power Since the battery back up is connected to the building management system panel, it won’t lose power.question, obviously how do I provide normal power from the electrical panel to the building management system panel but also still intertwine the battery back up to the panel in case of the power outage that will stay on do I need a special set of contacts to route the circuit through as well as the output of the battery back up and then feed the building management system panel from that?
Okay, this is a fairly common scenario and you're on the right track. You want to provide normal power and seamless battery backup. Here's how to approach this, breaking down the methods and the considerations
The Problem:
Directly wiring the battery backup output to the transformer input, as it's currently done, is a hack and likely not ideal, potentially unsafe, and may not be providing conditioned power.
Solution 1: Using a UPS (Uninterruptible Power Supply) - RECOMMENDED
This is the simplest, safest, and most reliable approach. It provides conditioned power and automatic switchover. Replace the existing battery backup with a proper UPS. Sizing
Determine the VA (Volt-Amps) or Wattage requirement of the BMS panel. Check the panel's documentation. Oversize the UPS slightly (20-30% is a good rule) to account for potential future additions.
Voltage and Output
Choose a UPS with a 120V input and 120V output. Ensure the UPS output waveform is compatible with the BMS panel's transformer. Sine wave output is generally preferred, but consult the panel's documentation.
Runtime
Select a UPS with sufficient battery runtime to keep the BMS panel operational for the required duration during a power outage. Consider the BMS's critical functions and how long they need to run on battery.
Wiring
1. Connect the 120V feed from the electrical panel to the UPS input.
2. Connect the UPS output to the 120V input terminal block on the BMS panel (where the original 120V feed was supposed to connect).3. Remove the existing battery backup and its wiring completely.
Advantages
Clean Power
UPS units typically provide filtered and regulated power, protecting the BMS panel from voltage spikes and sags.
Automatic Switchover
Seamless transition to battery power during outages. The BMS panel won't even notice the power loss.
Battery Management
The UPS manages the battery charging and health, extending its lifespan.
Safety
Properly designed and certified UPS units provide better safety compared to a DIY approach.
Monitoring
Many UPS units offer monitoring features, allowing you to track battery status, load, and power events.
Disadvantages
Cost
UPS units can be more expensive than a simple battery backup.
Solution 2: Using a Contactor and a Separate Battery Backup (More Complex)If you absolutely cannot use a UPS, this is a more complex solution that requires careful implementation. It involves using a contactor to switch between the normal power feed and the battery backup output.
Components
Contactor
A normally closed (NC) contactor with a 120V coil. The contactor needs to be rated for the voltage and current of the circuit. Crucially, the contactor must be rated for inductive loads if the transformer is an inductive load.
Separate Battery Backup
(The existing one, presumably) Double check voltage is 120V
Enclosure
A suitable enclosure to house the contactor and any wiring.
Wiring Supplies
Appropriate wire, connectors, etc.
Wiring
Normal Power
Connect the 120V feed from the electrical panel to the normally closed (NC) terminal of the contactor. Connect the other side of the NC contact to the 120V input terminal block on the BMS panel's transformer.2.
Battery Backup
Connect the output of the battery backup to the normally open (NO) terminal of the contactor.3.
Contactor Coil
Connect the 120V feed from the electrical panel (the same feed that powers the NC contact) to the contactor coil.
Operation
Normal Operation
When the power is on, the contactor coil is energized. This opens the NC contact, disconnecting the normal power feed. The BMS panel is powered by the battery back up, but since it is plugged in and is the source of power to the Contactor’s coil it is also constantly being charged.
Power Outage
When the power goes out, the contactor coil is de-energized. The NC contact closes, connecting the normal power feed to the BMS panel.
Advantages
Potentially lower cost than a UPS (depending on the cost of the contactor).
Disadvantages
Switchover Time
There will be a brief interruption of power to the BMS panel during the switchover. This may or may not be acceptable depending on the panel's sensitivity.
Complexity
More complex to wire and troubleshoot than a UPS.
Safety
Requires careful wiring and adherence to electrical codes to ensure safety. Proper grounding is essential.
Battery Management
Requires a separate battery charger for the backup battery.
No Power Conditioning
Does not provide any power filtering or regulation.
Important Considerations for Both Solutions
Local Electrical Codes
All wiring must comply with local electrical codes. You may need a permit for this type of work.
Grounding
Ensure proper grounding of all components.
Overcurrent Protection
Verify that the circuit feeding the BMS panel has appropriate overcurrent protection (circuit breaker or fuse). The UPS or contactor setup should not compromise this protection.
Labeling
Clearly label all wiring and components for easy identification.
Testing
Thoroughly test the system after installation to ensure it functions correctly. Simulate a power outage to verify the switchover to battery backup.
Documentation
Provide the customer with documentation of the wiring and operation of the system.
BMS Panel Documentation
Absolutely essential! Consult the BMS panel's documentation for specific power requirements and recommendations. Some panels might have specific requirements for backup power systems. This is especially important regarding the type of AC power (sine wave, modified sine wave, etc.) that the panel can accept.
Recommendation:
Using a UPS is the strongly recommended* solution. It's safer, more reliable, and provides better power quality. While it may be slightly more expensive upfront, the long-term benefits and peace of mind are worth it.Before you start any work, DISCONNECT THE POWER and verify that the circuit is de-energized. Consult with a qualified electrician if you are not comfortable performing this work yourself. Flag for review