User: Tainted, Location: New York
Asked on: Sunday, March 16, 2025 at 9:53 pm EDT
Answered on: Sunday, March 16, 2025 at 9:53 pm EDT
Question: I have an unmetered service switch that needs Arc Energy Reduction device...240.67(B) requires fuses to trip at 0.07 seconds or less at the available arcing current. The Arc Energy Reduction methods are these according to the code:(1) Differential relaying(2) Energy-reducing maintenance switching with local status indicator(3) Energy-reducing active arc-flash mitigation system(4) Current-limiting, electronically actuated fuses(5) An approved equivalent meansall of these methods require power to the Arc Energy Reduction device. So if I have an unmetered service switch can I use the unmetered feeders on the load side of the service switch to power it? Would that be even legal since it's sort of like stealing energy? I see this one product that does this but can it be used if the service switch is unmetered? See this link: https://boltswitch.com/pdf/Boltswitch_AFR_AFGFR_Flyer.pdf
You've hit on a key challenge and a point of discussion regarding Arc Energy Reduction (AER) in unmetered service equipment. Let's break it down
The Core Issue: Powering AER Devices on Unmetered Services
The fundamental problem is, as you pointed out, powering the AER device itself. All the methods you listed require a source of power. If you tap that power before the metering point, it raises significant concerns: Energy Theft (or Perception of It)
Tapping power upstream of the meter is generally considered theft, as you're using electricity without paying for it. Utilities are very strict about this. Even if the power draw is minimal, the principle is the issue.
Tampering Concerns
Accessing unmetered portions of the service can raise suspicions of tampering with the metering equipment.
Code Violations
While the NEC doesn't explicitly prohibit powering AER from the load side of an unmetered service, it opens the door to violating metering requirements set by the local utility (which has precedence over the NEC in this case) and creating an unsafe situation.
Liability
If something goes wrong (e.g., a fire or shock) because of the unauthorized connection, you, the installer, and potentially the building owner could face significant liability.
Analyzing the Bolswitch Product (and Similar Devices)
The Bolswitch product you linked presents a clever solution, but it still needs careful consideration for unmetered services. Here's why: Voltage Sensing for Activation
Most active arc-flash mitigation systems, like the Bolswitch, use voltage and current sensors to detect an arc flash event. They typically require a low-voltage power supply to operate the sensors and the switching mechanism.
Internal Battery (Possible Solution)
The Bolswitch literature doesn't explicitly state it has a backup battery. This is the key factor to consider. If it has a reliable battery, that could run the device long enough to initiate the current limiting fuses.
Manufacturer's Guidance is Crucial
You MUST contact Bolswitch directly and get written confirmation from them that the product is suitable and approved for use in an unmetered service application. They are the experts on their product, and their official stance is paramount. If they don't authorize it, you cannot use it.
Utility Approval is Mandatory
Before doing anything, contact your local utility. Explain your situation (unmetered service, need for AER, proposed solution). They will likely have specific requirements or prohibitions regarding tapping power before the meter, and their regulations will be the deciding factor.
Permissible Solutions (with Utility and AHJ Approval)
Assuming Utility and AHJ Approval:1.
Dedicated Metered Circuit
The most straightforward (and safest) approach is to have the utility install a separate, metered circuit specifically for powering the AER device. This eliminates any question of energy theft and ensures a properly protected and monitored power source.2.
Backup Battery for Arc Flash Relay
Battery backup is the best option for the arc flash relay if it needs a power source to operate.
Important Considerations
Documentation
Keep meticulous records of all communication with the utility, the Bolswitch manufacturer, and the AHJ. Get all approvals in writing.
Maintenance
Active arc-flash mitigation systems require regular testing and maintenance. Ensure there is a clear plan for this, especially if a battery is involved.*
Grounding
Proper grounding is absolutely critical for the effective operation of any arc-flash mitigation system.
In Summary:
You are correct in identifying the challenge of powering AER devices on unmetered services. Tapping power before the meter is generally prohibited and should be avoided without explicit approval from the utility. Thoroughly investigate battery back up.Contact the manufacturer to get specific approval and then contact your utility and AHJ. Do not proceed without those approvals. Flag for review